Customer Question
Hi, my Rheem Classic...

Hi, my Rheem Classic 90 plus furnace keeps turning off (after ~15 minutes)

Contractor's Assistant: Did you check the furnace's filters?

Yes replaced last week

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Nope It has an ecobee thermometer

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
12/26/2017
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,407
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation. I need the actual model number of your unit? It's on the BTU rating tag inside the burner compartment. Do you get an LED flash code on the control board when it shuts down?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
The model number is: RGRA-07EMAES
Customer reply replied 6 months ago
I'm not sure about the flash code with the LED
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

How old is the unit? If you don't know then give me the serial number.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
was put in 2007
serial is: EH5D702F310004947
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Ok, this model has a green LED on the control board inside the blower compartment. I need to know what that green LED is doing when it shuts down (prematurely?). If it's flashing I need the flash sequence. How many times does it flash before it pauses and repeats

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Hi, I'm holding the button right now (it is not turning on yet, just humming). I have been holding for several minutes. The "OK" green LED is flashing twice at the moment every 2 seconds.
Customer reply replied 6 months ago
Will have to wait for the furnace to turn on and shut down to let you know what the LED is doing when it shuts down.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Ok, a 2 flash is an open pressure switch error. Given that it takes 15 minutes to d=shut down you need to check all the hoses for water and all the condensate drains to be sure they are open and flowing.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It was 2 flash waiting to turn on; it just turned on. I will let you know what happens when it shuts down early.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

ok

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Thanks, ***** ***** still going it is taking longer than usual to fail
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

ok

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It got all the way up to the temperature without failing today.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Given your description the most likely cause for a failure like you describe is water in the draft pressure switch or the condensate tubing. The fix I described earlier is the most likely solution. I'd suggest you do it anyway.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,407
24,407 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My dad passed away this summer and I'm trying to help my mom
My dad passed away this summer and I'm trying to help my mom turn the heat on. She has a Rheem Classic 90 Plus furnace. I see a valve on the outside of the left panel. They also have a propane tank. W… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My name is ***** ***** I have a 21 year old Day and Night
Hi My name is ***** ***** I have a 21 year old Day and Night Plus 90 furnace that goes on and off frequently rather than stay on to bring up to temp. Same problem 4 years ago fixed with new circuit bo… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hvac question. I have a rheem classic 90 plus furnace with
Hvac question. I have a rheem classic 90 plus furnace with a/c. The board was replaced last fall but there is a wire going to a/c that is not hooked up. It is a 2 conductor wire red and white. My ques… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem Classic 90 Plus furnace. I would like a little
I have a Rheem Classic 90 Plus furnace. I would like a little cooler air in the heating cycle. I have bumped up the airflow 15% via the dip switches. Is there anything else I can do to reduce the hot … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
my rheem classic 90 plus furnace is have issues, it works for
my rheem classic 90 plus furnace is have issues, it works for some five minutes and just shuts off suddenly and when i go to the power box to turn it back on the switch is hot comparing to all of the … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hi, I have a Rheem 90 Classic Plus furnace. I am not seeing
Hi, I have a Rheem 90 Classic Plus furnace. I am not seeing any ignition, partial or temporary, when I turn on heat. Blower turns on, and at times will remain on for an extended period of time blowing… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi, I have a Rheem classic 90 Plus furnace which is not turning
Hi, I have a Rheem classic 90 Plus furnace which is not turning on to blow air and has 2 red indicator lights #6 and #8 blinking. What may I do about the problem since we would like to use our AC. Kat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rheem Classic 90 Plus Furnace Blower kicks on. Burner is
Rheem Classic 90 Plus Furnace Blower kicks on. Burner is ignited. Runs for a minute then kicks off. Blower kicks back on but flame on burner is no longer appearing. Turn it off then on again. I have a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my rheem classic 90 plus led light code blinks once every two
my rheem classic 90 plus led light code blinks once every two seconds, the other light stays on continuously. the furnace only starts if i turn the power off then back on. the code on the furnace stat… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Classic 90 PLus RCBA Rheem Gas furnace..it has been
I have a Classic 90 PLus RCBA Rheem Gas furnace..it has been squealing everytime is shuts down. We recently bought this house and it was already in it..it also comes on alot!!… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem classic 90 plus model number RGRA 09EZAJS, igniter
I have a Rheem classic 90 plus model number RGRA 09EZAJS, igniter isnt lighting and the OK led blinks 3 times, whats going on?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rheem Furnace with conventional Honeywell thermostat runs 10-15
Rheem Furnace with conventional Honeywell thermostat runs 10-15 minutes and cycles off. If you turn off the switch and turn it back on, furnace will restart and run another 10-15 minutes, etc. Why… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a classic 90 plus rheem furnace, will not light main
I have a classic 90 plus rheem furnace, will not light main burner. The igniter fires but nothing else… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I am purchasing a rheem propane furnace/AC unit 2.5 tons. RHEEM
I am purchasing a rheem propane furnace/AC unit 2.5 tons. RHEEM RGRA-06EMAES 90% FP - Conversion Kit RCFL-HM3617AC Cased Coil 1B410A-2.5 Ton RANL-0315AZ Condenser 2.5 ton w/R410A Rangers SEER I can't … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am in Colorado, 20 deg outside. Furnace is apparently not
I am in Colorado, 20 deg outside. Furnace is apparently not working. I have turned it off now, and before I call repair people, I want to check the filter. Can I just open the filter access door, and … read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Good Evening, I have a Rheem Classic 90 Plus furnace that is
Good Evening, I have a Rheem Classic 90 Plus furnace that is 10 years old. It started shutting off today however will turn back on when turned off and then restarted. It will remain on for approximate… read more
Mario
Mario
Owner Of At Your Service Plumbing & Heat
High School or GED
672 satisfied customers
We have a rheem classic 90 Plus furnace which is only 2 years
We have a rheem classic 90 Plus furnace which is only 2 years old. In the past month it has become a noisy machine. It appears to have difficulty starting a motor or something when it starts and than … read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
I have a rheem classic 90. set a code 2 and stopped running.
I have a rheem classic 90. set a code 2 and stopped running. It would run after turn power off for a few seconds. It would be about 45 minutes and set code again. I noticed this last time it set a cod… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.