I have a lennox furnace that is not working the furnace

Customer Question
Hello i have a...

Hello i have a lennox furnace that is not working the furnace lights and the burners come on breifly then shut off i have a flash code of 8 flashes

Contractor's Assistant: Did you check the furnace's filters?

Yes they are clean do you know what the 8 flash code is?

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

It is a lennox ML193UH furnace

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
12/25/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,713
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

That is normally an open limit code, but if it lights up then goes out right away then repeats this process you need to remove and clean the flame sensor rod off on the unit. The flame sensor rod is what detects the flame after lighting and tells the board to keep sending power to the gas valve to keep the flame going. Over time these get corroded and even go bad failing to send the correct Milliamp signal to the board. Normally a good cleaning with some sand paper will clean them right up and they will work fine again and in other instances they need to be replaced. The part is on the burner manifold and typically will only have 1 wire attached to it and will either be a straight metal rod with a porcelain base or a bent metal rod with a porcelain base. Get that out and clean it off then try it and see what happens. Here is an image of what you would be looking for to take out and clean off with sand paper. If that does not solve it let me know.

CLICK HERE

Merry Christmas....All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 6 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,713
18,713 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Lennox Model G24M3-75A2. The unit turns on, the
I have a Lennox Model G24M3-75A2. The unit turns on, the evac runs for 30-40 seconds, the gas turns on, the igniter kicks on. Sometimes the burners light and run fine. Sometimes they light for 5-8 sec… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Power went out. When it came back on, the furnace kicked on
Power went out. When it came back on, the furnace kicked on for 2 seconds then shut off. Now furnace doesn't work. … read more
Rick
Rick
Supervisor
24,242 satisfied customers
I have a Lennox ML193uh. It turns on for a few min blows
I have a Lennox ML193uh. It turns on for a few min blows cold air then shuts right off. The red indicator ligt is off and the green is flashing slowly. I tried cleaning the flame sensor that didn't wo… read more
Rick
Rick
Supervisor
24,242 satisfied customers
I HAVE A LENNOX G26 PUT IN 1997 BURNERS KICK ON RUNS FOR
I HAVE A LENNOX G26 PUT IN 1997 BURNERS KICK ON RUNS WHILE SHUTS DOWN NO BLOWER COMES ON REPLACED MOTOR LAST YEAR REPLACED FLAME SENSOR WITH GENARIC ONE… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hello, I have a Lennox Merit Series Model # ***** Furnace
Hello, I have a Lennox Merit Series Model # ***** Furnace will come on, but burners will not light. Then the furnace shuts down. I pulled the filter out, to make sure the air wasnt being blocked. Is t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Lennox ML193UH and this morning woke up to a cold
I have a Lennox ML193UH and this morning woke up to a cold house! The furnace is trying to start but at first gave an LED code of 3 blinks (pressure switch open with combustion air inducer energized) … read more
type2technician
type2technician
253 satisfied customers
Hi, I have a York Diamond 80 heater. It won't heat past 62
Hi, I have a York Diamond 80 heater. It won't heat past 62 degrees. The burners go for several minutes and shutoff and turn back on. The fan also constantly runs. I tried cleaning the flame sensor and… read more
type2technician
type2technician
253 satisfied customers
Hi Bill . I've got a Lennox furnace about a year old not firing
Hi Bill . I've got a Lennox furnace about a year old not firing up . Throwing diagnostic code no1 off no2 flashing .(green light flashing ) any suggestions ?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Lennox 80UGH furnace is about 12 years old now. Never any
My Lennox 80UGH furnace is about 12 years old now. Never any issues. Annual inspection/cleaning by local gas company, etc. Recently the gas company switched gas meters and this morning the furnace isn… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a g26q3 lennox elite furnace. Was working fine but
I have a g26q3 lennox elite furnace. Was working fine but now even after unplugging and re-powering unit, it sounds like the fan or motor powers up and then shuts down. It will do this repeatedly ever… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i just installed a new furnace and having a problem with it.
i just installed a new furnace and having a problem with it. The furnace lights properly it will run for about 15mins then it shuts down one it shuts down it drains Alot of water out of the condisatio… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Lennox model 90UGFA3-75-6 that is not firing properly. burners
Lennox model 90UGFA3-75-6 that is not firing properly. burners ignite but only for a few seconds. left diagnostic light flashes slow, right flashes fast while lighting signaling "Low Flame Sensor" wil… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a gas furnace with electronic ignition. The blower starts
I have a gas furnace with electronic ignition. The blower starts up and the burners start and about 10 seconds after the burners start they shut off. The fan continues to run for a while then shuts do… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My home furnace Lennox model G60UH-48C-110-5 tries to start
My home furnace Lennox model G60UH-48C-110-5 tries to start and then shuts down. It shows Alternating Slow flash code and Burner lost fire five times. This is not and old furnace. Is this something th… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
i noticed that my lennox furnace was not running. i went to
i noticed that my lennox furnace was not running. i went to look at it and the green led lights on the bottom section were not blinking simultaniously they were alternating. when i flipped the breaker… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Lennox C33 25A 2F 2 gas furnace. When I turn it on,
I have a Lennox C33 25A 2F 2 gas furnace. When I turn it on, it ignites, the blue flames come on then it shuts off after about 3 seconds. The blower stays on and the lights blink as if it's working pr… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My lennox Elite Series furnace Manufactory # G24M2-45A-12 serial#6399E
My lennox Elite Series furnace Manufactory # XXXXX serial#6399E 00881 is not working correctly. The thermostat is telling the furnace to turn on, but the furnace is not responding. If I flip the break… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
furnace comes on for 1 minute and shuts off a new thermostat
furnace comes on for 1 minute and shuts off a new thermostat has been installed still same problem.… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.