No power to tstat, I've flipped breakers off / on at power…

Customer Question
No power to tstat...

No power to tstat, I've flipped breakers off / on at power box, at air handler and pulled and placed back the shut off outside at compressor. Checked fuse inside air handler, still no power on R on thermostat. Carrier a/c system Air handler model FY4ANF048T00

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

digital thermostat, no power no nothing

Contractor's Assistant: Do you plan on doing the work yourself?

Yes if its minor

Contractor's Assistant: Anything else we should know to help you best?

Thats it

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
12/23/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,122
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello, my name is Billy,

What function have you been using recently?..heating or cooling?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
cooling, I live in FL
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

thank you.

There is a safety switch on most units that turn off power to the thermostat if the drain gets plugged. Is your air handler in the attic?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
In the garage. pan completely dry. I don't think the float switch has ever been activated. I push it up and it came back freely
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

Are you willing to remove the cover over the wiring area of the air handler to see if there is a control fuse present?

was thermostat recently changed?

any recent yard work around the outdoor unit?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
i have the cover off. pulled out atc fuse and it looks ok. I haven't changed anything on the system. tstat is 24 volt wired to air handler. put volt meter on R pin and C and got 0 volts on tstat
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

do you have 24 volts at R and C in the air handler?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

Or even back up...do you have 220v to the transformer

Ask Your Own HVAC Question
Customer reply replied 6 months ago
can you get me a parts breakdown to help me identify. I got 230 in and out of the breaker inside the air handler. Then I got 230 to the rectifier control. It goes to what I believe is the 24 volt transformer. On the bottom I have 230 terminal and common. I got 0 between those terminals. I get 230 if I go from the 230 terminal to the ground wires at the breaker. I have a red and brown wire that comes out at the top. I think this is the power for the thermostat. I got 0 between these terminals.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

Ok this shows a bad transformer.

230 input to transformer an d zero out = bad 24v transformer. The transformer is known as a generic part as any 230 to 24v transformer will work. Just google the number on side of the transformer to obtain parts availability

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I'm not sure. I got 230 when grounding to the incoming ground wire at the breaker. I got 0 between the 230 and Common terminal on the bottom. Is this the ground going in to the transformer? I might not be testing properly. The only way I get 230 is when I ground to the incoming wire at the breaker?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

ok, take a pic and post of the wiring area and I will draw test points for you.

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

put meter leads as shown HERE and tell me what value

Ask Your Own HVAC Question
Customer reply replied 6 months ago
0
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

ok now can you show me the contact point where the 2 power wires come into unit?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

we are missing one leg at the transformer...that is why we need to back track right now

Ask Your Own HVAC Question
Customer reply replied 6 months ago
OK, but I do get 230 if I ground that terminal to the incoming nuetral wire in the last photo its the white wire with red tape on it
IMG_6134.JPGIMG_6134.JPGIMG_6138 (1).JPGIMG_613...JPGIMG_6137.JPGIMG_6137.JPGIMG_6135 (1).JPGIMG_613...JPG
Customer reply replied 6 months ago
Billy, I'm no expert but I believe that is the transformer. I don't think the C is for common. I got 120 volts on the yellow wire terminal grounded to case and 120 volts on the black wire when grounded to case. I got nothing on what I believe is the 24 volt terminals at the top, jumping the red and brown wires.
Customer reply replied 6 months ago
it looks like both heating elements have the black and yellow wires going to each of them. I can ground them and I get 120volts out of each of them.
Customer reply replied 6 months ago
the incoming power goes through a breaker. If I jump between the 2 incoming wires I get 240 volts. If I jump between the 2 out going wires I get nothing. I can ground the out going wires and get 120 volts on each. Could I possibly have a bad breaker?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

you are correct...it appears to be a bad connection or breaker....the 120v you are reading is the same 120v everyplace...we are missing the other 120v.

That is why we have 230 at incoming breaker and not leaving

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Rick, I am having issues with a similar question you already
Hi Rick, I am having issues with a similar question you already answered in reference to installing a wifi Honeywell thermostat. This model is RTH6580WF, connecting to a gas fired heating boiler with … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I installed a rheem rhll air handler condenser shuts off
I installed a rheem rhll air handler condenser shuts off when tstat is satisfied in heat but fan continues to run. I have replaced board I pulled off the electric heat so it is not a sequencer. I have… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I was trying to install my new Ecobee3 thermostat last night
i was trying to install my new Ecobee3 thermostat last night took okk the old Honeywell thermostat … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I have a Lennox 21j7101 tstat. I am replacing with a Pro1
I have a Lennox 21j7101 tstat. I am replacing with a Pro1 IAQ T715. Need wiring directions… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,122 satisfied customers
Carrier AC blowing hot on cool cycle. Happened suddenly. Had
Carrier AC blowing hot on cool cycle. Happened suddenly. Had problem with fan running and then cut off. Tech had said low voltage wire was shorting in the outside unit. could this be my problem?… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
I have a VisionPRO TH8000 series thermostat. Yesterday it
I have a VisionPRO TH8000 series thermostat. Yesterday it seemed to be cool in the house and so I checked the termostat and it said LO BATTERY so I changed the batteries as they were... I still do not… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
We have a Goodman model # XXXXX serial number XXXXXXXXXX
We have a Goodman model # XXXXX serial number XXXXXXXXXX . We were without power for three days when we came back into the building this morning the unit was not working. we have a blank screen on the… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a TRANE system Model 4TWB3036A1000BB Serial 10135NML4F What
I have a TRANE system Model 4TWB3036A1000BB Serial 10135NML4F What fuse amp does it take? WHERE IS THE FUSE BOX? I can't find it outside I have 30 amp fuses. will they work?… read more
SWFLHVAC
SWFLHVAC
67 satisfied customers
changed thermostat from digital to digital with internet functions;
changed thermostat from digital to digital with internet functions; didn't shut off power; wires touched an got a spark; new thermostat not working; replace old thermostat and its not working; flipped… read more
spivco
spivco
153 satisfied customers
Lennox ac system fuse blows when system starts. Why?
I have Lennox ac system and the fuse #3 amp in blue wire keeps blowing. If jumped system would start and function fine. Now even a 5 amp fuse blows when system starts. Model #CB29M-41-2P AIR HANDLER.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a 14 yr old horizontal Bryant A/C / Forced hot air furnace
I have a 14 yr old horizontal Bryant A/C / Forced hot air furnace in an attic. The A/C stopped working a few days ago. The thermostat is calling, I hear the click when it is turned on, but nothing hap… read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
am installing a rth7600d honeywell thermostat and have a picture
am installing a rth7600d honeywell thermostat and have a picture of the wiring to the original thermostat that I would like you to look at and tell me where each wire goes. Note the Yellow wire attach… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
Hi, my heat pump stopped. There is no power to the thermostat.
Hi, my heat pump stopped. There is no power to the thermostat. I've thrown the circuit breakers off and on again, and the fuses are undamaged. The thermostat trouble shooting guide says to the power s… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,122 satisfied customers
my thermidistat has a blank screen with no display and my hvac
my thermidistat has a blank screen with no display and my hvac unit is not comming on. I've checked that all breakers are on. I opened the thermidistats and looked behind at the wiring and when I clos… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have an American Standard thermostat (ASYSTST570) on my heatpump
I have an American Standard thermostat (ASYSTST570) on my heatpump A/C system. The display is gone and nothing works. What do I check next? The breakers are OK, there is power at the outdoor unit.… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
our heat pump (18 months old) stopped working yesterday. The
our heat pump (18 months old) stopped working yesterday. The thermostat (batteries replaced this morning) says "cooling on". Interior temperature is 79, cooling is set to come on at 75. But the heat p… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
breaker flipped insider air handler. Reset breaker, outside
breaker flipped insider air handler. Reset breaker, outside heat pump and fan will not start. happened one year ago. then when I flipped breaker unit started… read more
Robert
Robert
Associate Degree
161 satisfied customers
I have a Carrier air handle that seems to power down for no
I have a Carrier air handle that seems to power down for no apparent reason. Have checked power to the unit and is ok. Usually, turning breaker off and back on brings it back to life. This appears to … read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x