Billy I hope all is well. We chatted back in late November…

Customer Question
Billy I hope all is...
Billy I hope all is well. We chatted back in late November about our Carrier furnace. Based upon the code that was flashing (24) you ssaid I needed to replace the fuse. I did that. I used existing fuses I had and then I purchased new fuses. Both fuses blew within 3 days of our discussion. I travel a lot so I didn't get a chance to contact you again PLUS our weather has been very mild and we haven't needed the furnace.But now temps are dropping and hopefully you can help.I am still getting the blinking 24 code. I do have extra fuses.
Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
12/21/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,155
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Sorry for the ongoing issues...

At the circuit board...check all wires and make sure none are touching each other,,,make sure where wire goes through side of furnace there is no scrapes.

Pretty much follow the wire that connects the thermostat to the furnace looking for any damage...does this have ac also?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
No this is a furnace only.
Customer reply replied 8 months ago
going to check wires now.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

Great...can you trace the thermostat wire from the thermostat all the way to where it connects in furnace looking for any damage at all?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok I will look.
Customer reply replied 8 months ago
I have jiggled every wire and removed the blown fuse. I can put in a new fuse. No wires are touching. None of the wires are bare. They are all covered.
Customer reply replied 8 months ago
If I put in the fuse, it will appear fixed but will blow a day or so later.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

Correct...that is why we want to see if the wire is pinched, scraped etc...

I eliminate this sometimes by running new thermostat wire....if it still blows I know it is on furnace

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I got it. What should I do now?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

Depends on how easy it would be to run new wire or check the existing....if it is a fairly short run....I would just replace the wire since it is pretty cheap...and plus there are only 2 connections at each end.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok. Can I make two wires using alligator clips?
Customer reply replied 8 months ago
Could it be the thermostat that's on the wall?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

If you want to by pass the thermostat wire....you would connect R on the circuit board to W.

This would bypass wire and thermostat...only problem is it will not shut off until the wire connecting r and w is removed.

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

the thermostat normally will not short....it is generally the wire touching metal

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Hmmm let's go back a little bit. :-)
Customer reply replied 8 months ago
The wiring that you want me to do, what are we testing?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

We are wanting to eliminate any old/bad wiring . We cannot make progress if we have a bad thermostat wire

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Sorry for the delay. I don't think it's a bad thermostat wire. I replaced the thermostat last year. :-)
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

Then if you are confident it is NOT the wire, then you have a bad component in the furnace itself. Like a circuit board or gas valve.

Unfortunately this would need a tech onsite with a voltmeter to take readings.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok Just a minute.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

that is the limit switch..it can short the system if not centered in the square just right.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
All of the repairs that I've done to the furnace we with Just Answer. They have been good repairs. I am very handy. I have also replaced the wheelie thing. See the picture. In our other furnace, I replaced both of these circular things using Just Answer. No problems. So I don't think the limit switch suddenly went awry.
Customer reply replied 8 months ago
typo - were with Just Answer.
Customer reply replied 8 months ago
I just replaced the fuse again and will see what happens.
Customer reply replied 8 months ago
I have to run an errand but will check back in later. Thanks
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

this would leave the gas valve....IF...IF the thermostat wire is good/new and there are no obvious spots of damage

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I hooked up a replacement thermostat and connected the Blue
I hooked up a replacement thermostat and connected the Blue wire from the Carrier HVAC unit to the B terminal on the new thermostat. The new one is a Honeywell and the old one is the original Carrier … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
I just blew my secondary blower fuse on my carrier comfort
I just blew my secondary blower fuse on my carrier comfort 80 and can't figure out where it is located so I can see what kind of fuse it is.… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
Bill has been my HVAC tech for JA, my furnace has quit working
Bill has been my HVAC tech for JA, my furnace has quit working and flashing a code of 24, I have a carrier 9200 weather maker and I have had previous questions, can you pull up that information… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi billy. I have an existing Carrier thermostat that I want
Hi billy. I have an existing Carrier thermostat that I want to replace but I want to confirm compatibility with the air handler. I have a FV4BNF002 and a FV4BNB006. My thermostat is a tstatccprh01-B. … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
We changed the position of our Carrier thermostat (from parlor
We changed the position of our Carrier thermostat (from parlor wall-straight through a few inches to the hall wall. Neither furnace nor air would come on. We bought a new manual Honeywell thermostat a… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
i just removed my humidifier from my carrier 58pav090 furnace
i just removed my humidifier from my carrier 58pav090 furnace and now the led is showing a short circuit error, error 24 and ive checked for and bare wires or loose connections and found no problems… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
I have a Bryant Plus 80 high efficiency hetar model 395CAV024070AGJA.
I have a Bryant Plus 80 high efficiency hetar model 395CAV024070AGJA. I am getting a code 24 (secondary voltage is open). How do I check to see if it as fuse problem?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
My Lennox 80UGH furnace is about 12 years old now. Never any
My Lennox 80UGH furnace is about 12 years old now. Never any issues. Annual inspection/cleaning by local gas company, etc. Recently the gas company switched gas meters and this morning the furnace isn… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
I have a problem with my carrier gas furnace. The problem is
I have a problem with my carrier gas furnace. The problem is this . The inducer fan is not coming on I try the reset switch and it did not work I opened the cover touch a few wire check the fuze. Then… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
Status code #24 on a carrier 58mcb furnace. 6yr old thermostat
Status code #24 on a carrier 58mcb furnace. 6yr old thermostat time flashed as if there is a power outage. Tried replacing with a new one. Neither the new or old thermostat works now. Disconnected the… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
I have a Bryant Plus 90 Propane furnace. The system will not
I have a Bryant Plus 90 Propane furnace. The system will not start at all. There is a repeating LED blink code: 2 short / 4 long. What does this indicate?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
I am getting code 14 for our carrier HVAC - it appears to be
I am getting code 14 for our carrier HVAC - it appears to be a code calling for heat problem but the system should be calling for cooling is there a simple reset I can do to bring the air back on?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
Bryant 340MAV furnace + AC not working. See 2 red quick flashes,
Bryant 340MAV furnace + AC not working. See 2 red quick flashes, then pause, then 4 slow flashes on furnace led light (24 code?). What does this mean? Is this the reason our AC won't work? Thanks for … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
I have a lennox Furnace/AC, and the 3a fuse on the circuit
I have a lennox Furnace/AC, and the 3a fuse on the circuit board blew recently. I've replace the fuse and the unit comes up normally (2 green slow blinking lights) but upon the next cycle (thermostat … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
I have an Carrier model 58STA070-12 (Serial # XXXXX).
I have an Carrier model 58STA070-12 (Serial # XXXXX). The flashing display is giving an error code 24. Is that a fuse that I can replace and where would it be located?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
I pulled the wires off the old thermostate befor I read how
I pulled the wires off the old thermostate befor I read how to mark them.. now, nothing works.. help me.... I have an Honeywell rct8100 thermostate. The wires are red, white, green and blue..… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
With older model Tempstar units (model # NFCP3600A1), are they
With older model Tempstar units (model # XXXXX), are they compatible with the newer digitalized thermostats?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
I do not know what model Carrier I have, but i came home the
I do not know what model Carrier I have, but i came home the other day and the thermostat read low battery. The wires on the outside fan were cut because the dogs got to them. I replaced the wire like… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,155 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.