Furnace just started shutting down before it reaches temp.

Customer Question
Furnace just started shutting...

Furnace just started shutting down before it reaches temp.

Contractor's Assistant: Did you check the furnace's filters?

Yes they have been changed

Contractor's Assistant: Do you plan on doing the work yourself?

Not sure how old the furnace is. it is a comfort air model and is 90%

Contractor's Assistant: Anything else we should know to help you best?

Not sure.

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 52 minutes by:
12/20/2017
HVAC Technician: airheatman, HVAC Technician replied 7 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,346
Experience: Furnace, A/C and heat pump specialist.
Verified

Can you look inside the burner compartment on label on side panel and get me the model on your furnace? Then look in blower compartment and see if there is an error light blinking that will guide us in determining what is failing with the furnace.)Not if no peep hole and you have to remove blower panel to see control board, it will be necessary to hold door switch in to have power to board)

Ask Your Own HVAC Question
Customer reply replied 7 months ago
GLUA120-E5A Comfort Air 2006
No code flashing
This only happens when program goes from 60 to 70 when outside temp is below 30.
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

If no error code, it may be a thermostat issue.What thermostat do you have and does furnace work with a heat pump as auxilliary heat or independantly?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
White Rogers programmable. Stand alone NG unit. Everything working fine today. Issues last week through yesterday morning when weather was much colder. Thermostat seems to be fine.
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

OK the reason I asked about thermostat is some of todays digital thermostat have settings which can control weather furnace operates or heat pump operates depending on outdoor temp.

Since it is a stand alone furnace the issue is going to most likely be with the furnace itself, but to troubleshoot, we will have to be in "non working" mode as you can not fix what is not broke as they say.

I suspect when it fails, there IS an error code.The two most likely issues are going to be a pressure switch or a limit switch.

If furnace fails to operate and the board does not give an error code, the board itself is failing us.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I will need to wait until the next cold morning when the furnace won't reach temp with the program calling to bring the temp to 70. Then I will check again for an error code. One more thing that may help you is when the furnace shut off I was able to get it to restart just by setting the stat down to 1° under room temp and then after click turn it back above. Or I can turn stat off and back to heat. Seems strange to me.
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

That sounds like a thermostat issue.If it was furnace, you would actually need to kill power to furnace to reset. I would go ahead and replace thermostat and see if that doesn't solve the problem honestly.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Can I bypass the stat? If the stat is what is bad then it should not shut down with a jumper on it. Am I correct in assuming that?
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

THat is absolutely correct. The reason I say I now suspect it to be stat is that you say lowering temp and re raising makes it come on

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

If issue were with a pressure switch, limit or something in furnace, just messing with tstat would have no effect

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Although I have not changed anything yet, the issue has not occured again.
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

Just keep an eye on it and you have further issues we will go from here.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,346
9,346 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Notification from my nest thermostat is that my furnace runs
Notification from my nest thermostat is that my furnace runs for 3 or 4 minutes and shuts down for a few minutes before coming on again until the set temperature is reached. Have had conference calls … read more
Charles Bodenheimer
Charles Bodenheimer
Owner
Associate Degree
78 satisfied customers
My Lennox furnace seems to start up fine, runs for a little
My Lennox furnace seems to start up fine, runs for a little while, then shuts down before the thermostat temp is reached. It will do this over and over again for hours until the temp is finally reache… read more
airheatman
airheatman
HVAC Technician
6 years college
9,346 satisfied customers
I have a 1998 g23 series Lennox. We keep it at81 degrees.
I have a 1998 g23 series Lennox. We keep it at81 degrees. replaced motor last year. Repairman cleaned ignition switch, said it keeps running and keeps dropping temp because it needs to be replaced. We… read more
airheatman
airheatman
HVAC Technician
6 years college
9,346 satisfied customers
I have a Trane XE 90 Furnace. After the furnace has been
Customer: I am Vickie. I have a Trane XE 90 Furnace. After the furnace has been running for a while it starts to blow cold air. … read more
airheatman
airheatman
HVAC Technician
6 years college
9,346 satisfied customers
I have an old tempstar furnace that has a fan/limit switch.
I have an old tempstar furnace that has a fan/limit switch. When heat is called for, the burners ignite, the fan comes on at the proper temperature, and the burners will run for about 5 minutes until … read more
Rick
Rick
Supervisor
24,392 satisfied customers
MY Trane XE80 gas furnace blower continues to run after reaching
MY Trane XE80 gas furnace blower continues to run after reaching thermostat temp and the gas shuts off then it's blowing cold air unless I raise the temp on thermostat… read more
airheatman
airheatman
HVAC Technician
6 years college
9,346 satisfied customers
I have a xe 90 heat and ac . After it runs for a while (heat)
I have a xe 90 heat and ac . After it runs for a while (heat) it shuts down ..fan stops but as soon as it begins to stop it will start again. Less than a second and back at full speed. When the t-stat… read more
jhvac
jhvac
2 satisfied customers
I have an American standard single stage 90. 2 thermostats
I have an American standard single stage 90. 2 thermostats up and down. Down calls for heat shuts down when temp is reached no problem. Upstairs which also controls the ac calls for heat and shuts dow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My furnace is not shutting off when the temp is reached on
My furnace is not shutting off when the temp is reached on the thermostat - at least not always. I just replaced the thermostat so I'm assuming it must be a limit switch or something on the furnace?… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Ok, I have a Hunter 44668 thermostat. i believe i connected
Ok, I have a Hunter 44668 thermostat. i believe i connected the wires as described. I currently have the Home temp set at 85 degrees yet it won't go higher than 71 degrees… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
I have an Armstrong gas furnace, model no. 911-G6-120, that
I have an Armstrong gas furnace, model no. 911-G6-120, that is at least 45 years old. I have lived in my house for 13 years and haven't had any problems with the furnace. When the furnace is not call … read more
airheatman
airheatman
HVAC Technician
6 years college
9,346 satisfied customers
I have a bryant +90 furnace model 398AAW036080D.The burners
I have a bryant +90 furnace model 398AAW036080D.The burners come on and run then shut off when the blower kicks on.Is this the way it should run?Or should the blower and the burners be on at the same … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox merit series furnace that will run and heat
I have a lennox merit series furnace that will run and heat my house well but when it shuts off it will stay off for a long time before kicking back on. It will let the temperature get well below the … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
i have a goodman gmnt 120-5 gas furnace and have had for 5
i have a goodman gmnt 120-5 gas furnace and have had for 5 years having trouble with it. when i turn the heater on goes on for about 5-10 mins then kind of shuts off starts back on does the same start… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a miller oil furnace cfm60-po when I run the furnace
I have a miller oil furnace cfm60-po when I run the furnace the fan limit control switch turns the fan on at 90 deg and run up to 110deg and it puts the r4184g primary control into lock out befor it r… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
MY ROOM TEMP HAS NOT CHANGED A EVEN THROUGH MY THERMOSTAT IS
MY ROOM TEMP HAS NOT CHANGED A EVEN THROUGH MY THERMOSTAT IS SET FOR 72 (ROOM TEMP 65) WOULD LIKE FOR ROOM TO GET UP TO 72.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Hello I have a Honeywell RTH110B thermostat. When using the
Hello: I have a Honeywell RTH110B thermostat. When using the A/C this summer, it worked fine for a couple of weeks after I installed it, then when the A/C cooled the air down to the set temp. the unit… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I am installing a honeywell thermastat CT87N/CT87K round replaceing
I am installing a honeywell thermastat CT87N/CT87K round replaceing an old honeywell mercury 2 wires red/white having problem furnace turns on but will not turn off when temp is turned down?… read more
Johnribs
Johnribs
Service Technician
Associate Degree
4 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x