Carrier gas furnace 394gaw00010. Woke up to no pilot light…

Customer Question
Carrier gas furnace 394gaw00010. Woke...
Carrier gas furnace 394gaw00010. Woke up to no pilot light or heat this morning.
Blower works damper works gas is on
Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 6 months ago
Checked circuit breaker
Checked filter
Checked thermostat
Can’t afford to replace the old girl right now
Help
Answered in 8 minutes by:
12/19/2017
HVAC Technician: airheatman, HVAC Technician replied 6 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,175
Experience: Furnace, A/C and heat pump specialist.
Verified

This is an old one before we had the eror lights on board to help us with troubleshooting.Let me see if I can find a manual. Meanwhile jump R to W on board and see if heat will come on

https://i.imgur.com/JprQdYv.png

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Can you clarify “board”
Customer reply replied 6 months ago
I don’t have alligator clips. What can I use?
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

BOard is in blower compartment.Use needle nose pliers or a paperclip

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Okay will check when I get home form teaching today. Thanks
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

We will go from here.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Did the jump at thermostat then furnace. No pot light ignition
Customer reply replied 6 months ago
That’s pilot light
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

OK there are several limits in the circuit between transformer and valve. Just for a test bypass each one (or test continuity) to see if one is open.

Here are the limits:

1.Fusible link

2.Main limit

3.Vent safety switch

4.Aux limit

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Furnace blowing, no flame or heat, power went out yesterday
Furnace blowing, no flame or heat, power went out yesterday so assuming the pilot light went out … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a newer keep rite gas furnace in my home in Cobourg,
Hi.... I have a newer keep rite gas furnace in my home in Cobourg, Ontario where it is currently minus 22 Celsius. In the past 12 hours the furnace keeps on cutting out after a few minutes of operatio… read more
airheatman
airheatman
HVAC Technician
9,175 satisfied customers
My furnace is blowing cool air. Reset dozens of times.
My furnace is blowing cool air. Reset dozens of times. Occasionally will work (mostly during day) but not so much at night … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have a carrier weathermaster and the pilot light keeps
i have a carrier weathermaster and the pilot light keeps going out, we do have extremely cold temps. tonight … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I've got a Carrier 17C natural gas furnace. We just replaced
I've got a Carrier 17C natural gas furnace. We just replaced the blower motor, and now the furnace won't heat the building. The inducer motor comes on, pilot fires, but no main burner. It fired up cor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 30 year old Payne Heating Unit. The pilot is lit
I have a 30 year old Payne Heating Unit. The pilot is lit but the burners are not coming on. I turned off the pilot, three different times, and turned it back on. The pilot lit just fine, but still no… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have a Trane XE90. The furnace signits but the blower
Hi I have a Trane XE90. The furnace signits but the blower doesnt' come on. Any idea as to waht I could do? … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I recently changed my thermostat and now the AC unit will
I recently changed my thermostat and now the AC unit will not turn on at all. The LED light on the furnace is also not coming on. Both thermostats (1 upstairs and 1 downstairs) are on and light up. I'… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Payne gas furnace 394JAW036045 igniter keeps sparking while
Payne gas furnace 394JAW036045 igniter keeps sparking while pilot light is on but does not start the main burners. I know its time or past to replace the furnace but can i get it running for now?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 2 story house with, I believe only 1 furnace but 2
I have a 2 story house with, I believe only 1 furnace but 2 thermostats. (1 for upstairs and 1 for downstairs). We've experienced some extremely cold weather for our area and the heat downstairs has n… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Phil - My 30+ year old Carrier super saver furnace has turned
Phil - My 30+ year old Carrier super saver furnace has turned it self off intermittently recently. When it shuts off, the blower and the gas / burner stop at once. I would guess the flame sensor is fa… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
1. I have Carrier WeatherMaker 8000 gas furnace, which does
1. I have Carrier WeatherMaker 8000 gas furnace, which does not have a pilot. The furnace was working until last night. This morning it is dead. My desired temperature on the thermostat is 75 but the … read more
airheatman
airheatman
HVAC Technician
9,175 satisfied customers
We have a CARRIER 2-zone gas heating furnace that is about
We have a CARRIER 2-zone gas heating furnace that is about 11 years old. This morning, both zones stopped heating. I checked the pilot and neither unit was firing. Blowers are working ok. Checked the … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I woke this morning,our power is on but the Carrier infinite
I woke this morning,our power is on but the Carrier infinite control thermostat is "off"as in no light or signal onat all. My understanding is that it doesnotrun onbatteries but draws electricity. It … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Woke up this morning to no heat from the gas furnace (20 years
Woke up this morning to no heat from the gas furnace (20 years old, Duomatic-Olsen). Thermostat calls for heat, induction fan starts, intermittent igniter-sensor lights the pilot, which then goes out … read more
ClimateCreator
ClimateCreator
28 satisfied customers
woke up this morning heater wouldnt come on so i changed thrmostat
woke up this morning heater wouldn't come on so i changed thrmostat checked fuse and breaker ,made sure gas was still on but won't come on still. When i turn fan to on, the fan will operate. but the f… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
good morning, Last night i turned the heat up to 70 before
good morning, Last night i turned the heat up to 70 before going to bed. It kicked on and warmed up perfectly. This morning when I woke up the thermostat read 65 and the heat was not coming on. I trie… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have an older Climatrol gas/forced air furnace. Woke up
We have an older Climatrol gas/forced air furnace. Woke up this morning to 57 degrees in the house. Pilot light is on. No response from furnace when we turn the thermostat up. Anything we can do ourse… read more
Electrifier
Electrifier
Owner - Contractor
Bachelor's Degree
147 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x