I have a Janitrol unit heater WH-250. It has been converted to propane. What I need to do is change it back. The conversion was done prior to me buying the garage.
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 2 months ago
I’ll add photos
Customer reply replied 2 months ago
I need to change it back to natural gas.
Answered in 12 hours by:
12/19/2017
MattR757
MattR757, HVAC Technician
Category: HVAC
Satisfied Customers: 67
Experience: 18+ Years experience in residential and commercial HVAC service and repair
Verified

The conversion from natural gas to propane involves several parts - the burner orifices and the gas valve regulator spring get replaced. To convert back you would need the natural gas orifices, and the natural gas regulator spring. These should be very inexpensive parts but you likely need to contact a Goodman/Janitrol distributor to order them. I've checked some aftermarket parts sources - There are a number of sources that sell the LPT-03 kit to convert from natural gas to LP but so far I haven't located a conversion kit to go from LP to natural gas. You need to order the OEM orifices and regulator spring for the original natural gas burner and I haven't found a parts list for that particular model heater.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Would you know the number size for the orifice it takes for that size heater

I have access to most of the residential equipment catalog, but my literature does not include the self-contained unit heaters . Almost all of the Goodman janitrol 80% efficiency equipment used a #45 for natural gas and a #50 for LP to attain an output of approx 25,000 but per burner. However, there is some variation depending on how many BTUs per burner that heater was designed for. A distributor should have access to the original OEM parts list to tell you with a hundred percent certainty what the original orifices we're.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
If I could find a distributor. That’s the problem.

I have put in an information request with two of my local distributors to see if I can locate and identify the orifices and regulator spring to get you back to Natural Gas. As soon as I hear back from them I will let you know what I have found

Ask Your Own HVAC Question
Unfortunately all of my parts sources are telling me this unit is obsolete and no longer supported by janitrol. I'm pretty sure that the janitrol unit heater line was sold to Modine several years ago. Tech support says you can use #45 burner orifices. Originals could have been #47 but he said we'd rather use 45 and under-fire it by a couple thousand BTUs then over fire it and risk overheating the heat exchanger. You should be able to get a replacement regulator spring from any supplier that sells that brand of gas valve (original should have been a Honeywell). They actually advised me to replace the whole gas valve if possible.
Ask Your Own HVAC Question
He also said to very carefully inspect the heat exchanger for any cracks or areas that are rusted thin. Apparently propane gas has a higher water content than dry natural gas and usually causes the Heat exchangers to rust at temperature stress points.
Ask Your Own HVAC Question
Customer reply replied 2 months ago
There isn’t hardly any use on the heater at all no rust anywhere, and I have found the exact same gas valve for sale new but they are on the Lennox brand now
Customer reply replied 2 months ago
Do you think a person could take the right number drill bit and drill press and drill the orifices out or try to find new ones
The propane orifices are actually bigger than the natural gas orifices so you couldn't take the propane orifices and drill them out. Your best bet would be to take one of the propane orifices to one of the bigger suppliers that sells to the public like Grainger, Noland or Sears Parts Center so they can make sure the thread size matches up. I'm pretty sure they're all universal fine threads but I don't think I've ever tried to replace them when they didn't come directly from the manufacturer. You could also check with some local contractors. Most will typically replace one or two furnaces a week and a natural gas furnace should have the same size burner orifices as the original unit heater. You might find one that's willing to take the orifices out of an old furnace instead of trying to find new ones.
MattR757
MattR757, HVAC Technician
Category: HVAC
Satisfied Customers: 67
Experience: 18+ Years experience in residential and commercial HVAC service and repair
Verified
MattR757 and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 2 months ago
Thank you a lot
Customer reply replied 2 months ago
Propane orifices are actually smaller than natural gas
You're right. My mistake. A number #45 orifice is an equivalent decimal of 0.0820 so if you had a precise drill bit and drill press you could gently drill out the propane orifices to the larger size. Before I looked at my orifice chart I honestly thought they went the other way...
Ask Your Own HVAC Question
Customer reply replied 2 months ago
in your past comment if I went a couple sizes smaller diameter it would under fire the heater to be safe smaller than 45 that is

Correct. According to my burner orifice chart a #50 at 7.0 in (lp) pressure is 17594 btu - a #45 at 3.5 in (nat) pressure is 17072 btu which would be the closest equivalent output.

A #46 - one size smaller - is 16658 btu and a #44 - one size larger - is 18778 btu. A #46 would underfire the heater by about 6000 BTUs - a #44 would over fire it by almost 25,000 BTUs - looking back at my email from Goodman tech support he did say that are natural gas orifice options were #43, #45 and #47 - and he recommended 45 to avoid over firing but he didn't really clarify in his email that it was the 43 that would actually be too big.

It's been awhile since I've done any of these calculations and I guess I just defaulted to - bigger number = bigger hole - but it's actually the opposite. Now that I'm actually in the orifice charts I hope that everything is more clear

Ask Your Own HVAC Question
Was this answer helpful?
Ask MattR757 Your Own Question
MattR757
MattR757
MattR757, HVAC Technician
Category: HVAC
Satisfied Customers: 67
67 Satisfied Customers
Experience: 18+ Years experience in residential and commercial HVAC service and repair

MattR757 is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a new Rheem 95P single stage natural gas furnace and
I have a new Rheem 95P single stage natural gas furnace and I'm getting a code 56, not listed in the manual. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a ruud ultra series natural gas furnace. it will not
i have a ruud ultra series natural gas furnace. it will not light the burner when it tries. it is flashing code 45. what it wrong … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Rheem classic 90 plus natural gas furnace that is
Hi, I have a Rheem classic 90 plus natural gas furnace that is not properly igniting. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
277 satisfied customers
Ruud rgrc07erbgs natural gas furnace wont recognize flame
ruud rgrc07erbgs natural gas furnace wont recognize flame after cleaning flame senser … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have Ruud natural gas furnace and the gas valve opens after
Have Ruud natural gas furnace and the gas valve opens after the purge does its thing and only stays on for approx 3-5 seconds. Then goes off. The flame rod sensor light never comes on. Changed the rod… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Payne Forced air Natural gas furnace with a
I have a Payne Forced air Natural gas furnace with a condenser pumo on the side. the pump will not shut off. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Natural gas furnace: Conquest 80 Circuit board: Honeywell
Natural gas furnace: Conquest 80 Circuit board: Honeywell S9200U1000 Universal Hot Surface Ignition Integrated Furnace Controlfurnace shut of itself after around every 20 minutes, although still under… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Natural gas furnace exhaust vent has a strong propane ordor.
natural gas furnace exhaust vent has a strong propane ordor. nothing is smelled inside the house … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Weil McLain cg 4 natural gas furnace, the pilot
I have a Weil McLain cg 4 natural gas furnace, the pilot stays lit all the time but the furnace doesn't start … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
432 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hooking up a nest thermostat, I have natural gas furnace set
Hooking up a nest thermostat, I have natural gas furnace set as emerg heat on my old thermostat, main heat set as heat pump. Always Used emerg heat. Of course a/c. I have every wire hooked to my nest … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a 19 year old Nordyne natural gas furnace. This past
I have a 19 year old Nordyne natural gas furnace. This past winter it was intermittent in igniting the gas. The first thing I did was replace the igniter. That did not clear the issue. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x