My Carrier 58SXA 120 gas furnace keeps locking out after I…

Customer Question
My Carrier 58SXA 120...

My Carrier 58SXA 120 gas furnace keeps locking out after I restart it from my thermostate

Contractor's Assistant: Did you double-check the thermostat? And what about the pilot light?

The unit comes on it starts to heat the house but locks out once it gets to the thermostat temperature

Contractor's Assistant: Do you plan on doing the work yourself?

If I can, but there also seems to be a lose connection to the auto-igniter. I move the connection and the unit will start

Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 hours by:
12/18/2017
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello,

So far it sounds like a bad printed circuit board. If the furnace is older and you have not been replacing the air filter regularly or if the air filter is dirty it could also be a bad high limit switch... tell me please about how old the furnace is and if you have furry pets in the house.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, and the connection you moved that allows a restart and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Thanks, ***** ***** is to tighten up or repair that loose connection... restore it bright metal.

Next remove power from the furnace and reach inside the blower wheel. if you can dig any dirt from the blower wheel, the cooling coil if you have AC is likely clogged with dirt, that will cause problems such as tripping the high limit switch.

We can go from there without any limits

Ask Your Own HVAC Question
Customer reply replied 2 months ago
What does bright metal mean? How do I make it bright metal. I can clean out the blower and ac coil in a few hours . I feel dumb, can you tell me where to look for the ac coil?
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Bright metal means no rust, no corrosion, and no burnt wire on the connector.

If the wire is burnt you have to cut the terminal off and fit a new terminal, then you have scrape the female side of the connection with a knife blade until all corrosion, rust, or other stuff is removed and the metal is bright and shinny.

This typing above refers to the LOOSE WIRE CONNECTION ONLY.

The blower if its dirty needs to be removed from the furnace and cleaned with bottle brushes and a vacuum cleaner

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

The AC coil fits into a 20" square metal box, often wrapped in insulation, and sitting on top of the furnace in most cases, if its not there its under the furnace.

If the furnace is in the attic it is on one end of the furnace or the other.

It has 2 copper tubes attached, one insulated in black foam rubber, and a white plastic drain line at the bottom.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Cleaning the coil is a big job....if it needs cleaning we need to discuss it extensively.

.

First step is to see if there is any heavy coating of dirt in the blower. If you are not handy or if you do not like hard dirty work you can have this done by an AC service contractor, prices vary between $300 and $900 I will advise you when the time comes

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Excellent thanks . I will work on this when I get home this evening
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

That will work, I am in until 10 pm Chicago time... and in all day tomorrow

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Hello, I did my best to make the connection bright metal. The blower fan was not checked yet. However, the heat worked all night when I had it set at 68. When I try to move the temp up, the thermostat calls for heat but the unit will not turn on. If I turn the heat off at the thermostat, it will start and run until it reaches the set temp. Strange huh? What do you think I should do?
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Hello, if I understand what you say correctly, the thermostat is bad.... however that is a very uncommon failure mode, it could be that you do not understand the OFF switch correctly.... play with it for a while and lets see how it goes.

.

Meantime click the 'Finish and rate your expert' link near the top of your page to get me paid.... that way I will be able to hold the question open to you for as long as it takes to get the thermostat figured out.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Thanks. The strange thing about it is that when the house reaches the set temp and I raise the temp at the thermostat, it won’t start and it says heat on. But if I lower the temp so the thermostat stops and raise it about the room temp it will start. But when it gets to room temp it won’t start again . What does that sound like?
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

If the furnace trips its high temperature safety cut off, it can be reset by turning the thermostat OFF then back ON.... so far I have not seen that work by changing the setting up or down, but its possible.

Make sure you have a clean air filter in the furnace and that none of the vents are blocked... we can go from there

Ask Your Own HVAC Question
Customer reply replied 2 months ago
My question is what would cause the above behavior? What could be causing the high temp safety cut off? You said the thermostat could be bad, but not usual. Please see my question today. The unit has a Clean filter. It runs to temp but when it runs to temp, I want to make the house warmer. I raise the temp, the thermostat says heat on, but the unit will not start. I must turn off the heat at the unit or the thermostat before it starts. What does this tell you?
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Insufficient air flow due to a dirty air filter, or on older systems a dirty cooling coil cause the furnace to over heat. anything that restricts the air flow will cause the high temperature limit switch to trip..... OR ...a bad limit switch will trip when it should not trip.

A qualified technician would use a multi meter to measure ohms across the limit switch within 10 seconds of the furnace going off, if its 'open' then we know the limit switch tripped.

There are a few dozen other potentials that require tests on the electronics. let me know if you want to dig into those potentials...you will need a few hours and a multi meter

.

Thermostats do not fail in this fashion... the odds that your thermostat is good are nearly 100%

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Phil, thanks for putting up with me. Is it correct that unit stops at 68 because it over heats? When I raise the temp at the thermostat about 68, it won’t start, when I remove the ignigtor connection and reconnect it it will start and run until it hits the temp on the thermostat . So should I have a tech change the connection and clean the a/c coil?
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

It is not absolutely correct that the unit stops at 68 because it over heats.... but that is most likely the case.

Try setting the thermostat o 76F if it still stops at 68F then the problem IS in the furnace, either the high limit switch (80% chance) or a bad printed circuit board etc (20% chance).

If the house warms much above 72F then the problem IS with the thermostat.

Lets do these tests before we discuss the other issues,

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Excellent thank you
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Let me know how the tests turn out, we can go from there

Ask Your Own HVAC Question
Customer reply replied 2 months ago
will do
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
9,200 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,200 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Carrier Steam Humidifier - HUMXXSTM3134. The red
I have a Carrier Steam Humidifier - HUMXXSTM3134. The red light was blinking, so technician replaced canister. Red like is STILL blinking. red light … read more
Bill
Bill
Service Mgr
22 satisfied customers
I have a Carrier unit with heater that will not turn on. My
Hi I have a Carrier unit with heater that will not turn on. My house is only 5 years old and the company which installed the unit seems to no longer be in business. How can I get the warranty honored … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My furnace (Carrier) is not coming on. There is power going
My furnace (Carrier) is not coming on. There is power going to the furnace but yet it won't come on. The panel attached to the furnace (Honeywell) indicates a red light for both heat and zone 3. I hav… read more
Bill
Bill
Service Mgr
22 satisfied customers
Carrier furnace. Igniter comes on, but no flame. There was
Carrier furnace. Igniter comes on, but no flame. There was an electrical issue earlier today on the electric company's side of the meter. It has been repaired. Furnace was OK prior to that. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace rated at 1865 cfm was recently installed in
carrier furnace rated at 1865 cfm was recently installed in Jan 2018. Total cfm for all vents is 1056 cfm. heat distrbution for 16 vents ranges from 69 to 95 cfm. what could be the problem? Please adv… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier model 58mec100 and the heater will not
I have a carrier model 58mec100 and the heater will not cycle back on and the light will blink 1 then 6 green on the control board. I can switch the power off for a minute then it tries again and come… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace model 58CTA090-12114 that was
I have a Carrier furnace model 58CTA090-12114 that was installed in 2005,I am currently having an issue with it when it is called upon for heat, it will start the burner sequence with the ignitor glow… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The ignitor to my Carrier furnace will not trigger so no
Hi Pearl. The ignitor to my Carrier furnace will not trigger so no heat can enter the house. I've manually reset the limit switch and cleaned the flame sensor and was looking for suggestions on what t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to find a blower motor for a carrier 58wav045.
I'm trying to find a blower motor for a carrier 58wav045 … read more
MattR757
MattR757
HVAC Contractor / Owner
Associate Degree
14 satisfied customers
Non working furnace issue - Carrier Weathermaker 8000. The
Non working furnace issue - Carrier Weathermaker 8000. The ignition module was changed a couple of years ago. There's a clicking sound but not burning. Ideas? Cost?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Our carrier infinity says "system malfunction". The fan is
our carrier infinity says "system malfunction". The fan is working but it is not cool. I went to the attic and changed the filter but code is still there. What does this mean? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Rental hot water tank - serviced and insulated pipes Oct
rental hot water tank - serviced and insulated pipes Oct 2017 by Reliance tech-ice build up at elbows on insulated outside plastic pipe - when fan comes on -can hear running water outside from inside … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have a Carrier Weather Maker 8000 ts and the light on the
Have a Carrier Weather Maker 8000 ts and the light on the front panel is blinking … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Carrier Infinity System Thermostat Model #
We have a Carrier Infinity System Thermostat Model # SYSTXCCUIZ01-A and the plastic "heat" and "zone" buttons are broken. We are looking for a new unit with this model number to replace our current un… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Airheatman, Trying to source a control board for a Carrier
Hi airheatman, Trying to source a control board for a Carrier forced air furnace that a technician said was no longer available. The number is ***** obscured, looks like 3057?5 702 working with a 3012… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have Carrier fan coil unit model FV4CNB003. Have Carrier Fan
Have Carrier Fan Coil unit # FV4CNB003. Seemed to run and change speed during operation. Is this normal? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Question about basement insulation... It's not a problem -
It's not a problem - it's a question...we live in the Atlanta area. 3 years ago, we purchased an existing home that has a full, unfinished walk-out basement, which means that the entire north and west side of the basement is above grade. The south and east walls are poured concrete and are below grade. When we bought the home, it had zero insulation in the stud walls on the north and west sides. The concrete walls also were not insulated. However, there was faced fiberglass insulation stuffed between the floor joists in the basement ceiliing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The yellow wire on the blower motor through insulation. It
The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x