I have a new Honeywell R8184G 4033 and it doesn’t work. I put my old one back on and it works fine

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Just today.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes I always do. The old one is the same as my new one. But for some reason when I have the new one hooked up it runs for 30 sec or so the red light comes on. Don’t understand why

Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
12/18/2017
HVAC Technician: Rick, HVAC Supervisor replied 5 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,034
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

If you have both wired exactly the same then the only possibility is the new control is defective

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I took it back twice now. The part alone is 150 bucks.didnt think it would be possible to have two faulty parts. Everything is wired the same.
Customer reply replied 5 months ago
I don’t want to talk on the phone. This already cost me 40 dollars to talk with you.and I’m getting no where’s
HVAC Technician: Rick, HVAC Supervisor replied 5 months ago

Something is different or the new control would work like the old one. There is a chance, assuming no ignition with new control, that the ignition transformer is weak and for some fluke it puts out enough voltage when you have the old one hooked up. Have you checked the transformer

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 5 months ago

Call prompt is automatic I have no control over it. We can continue here

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I have two furnaces. One in my house one in garage. Both forced air. Oil furnace. Now, old 8184 works in both furnaces. Put new 8184 in either furnace and it runs then shuts off with red light on
HVAC Technician: Rick, HVAC Supervisor replied 5 months ago

Since I can't be there all I have to go on is what you tell me. So far all you've told me is that apparently the burner will start but won't fire with the new control. I've given you the possibilities based on the limited info you provided.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
It fires but shuts off after 40 seconds and puts red light on
HVAC Technician: Rick, HVAC Supervisor replied 5 months ago

If it shuts down when it's firing you have a cad cell problem. I'd replace the cad cell and the cad cell socket.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Why do I have to replace those parts. It works fine with the old 8184. But when I put the new 8184 on that’s when it acts up
HVAC Technician: Rick, HVAC Supervisor replied 5 months ago

I'm assuming you have the cad cell leads connected to the FF terminals on the control. Your description indicates the cad cell isn't seeing the flame so the fix is to replace it

Ask Your Own HVAC Question
Customer reply replied 5 months ago
it’s all connected right. I’m just gonna have to call a a service guy. This is getting me no where’s.
HVAC Technician: Rick, HVAC Supervisor replied 5 months ago

Ok, only so much I can do from here.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
This site was no help at all. Every thing I was doing and knew to do. You just told me to do again. Not a good way to waste 40 dollars
HVAC Technician: Rick, HVAC Supervisor replied 5 months ago

do you want a refund?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
please
HVAC Technician: Rick, HVAC Supervisor replied 5 months ago

ok will let customer service know. please do not respond to this thread

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Honeywell R7284 and I need a manual for it
Hi there. I have a Honeywell R7284 recently installed on a furnace that was allowed to let the oil run out. I hold down the button and it will test ignition and fire right up and run for 30 seconds (c… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
got a thermo pride oil furnace . red button pushed to reset
got a thermo pride oil furnace . red button pushed to reset burner. seem to come on for 10sec and then shuts off. green light next to reset button is flushing , when reset button is pushed in it shuts… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
what should the fan limit switch tempature settings be for
what should the fan limit switch tempature settings be for each set switch on a lennox oil furnace.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Oil furnace blower comes on, no flame or ignition. I buy the
oil furnace blower comes on, no flame or ignition JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: I buy the parts JA: Anything else we shou… read more
Rick
Rick
HVAC Supervisor
24,034 satisfied customers
My old oil furnace needs rest=ettiung in the mornings, but
My old oil furnace needs rest=ettiung in the mornings, but OK in the day. does the bi metal actuator itself ever need changing as the scavenge time is opnly 45 seconds … read more
Rick
Rick
HVAC Supervisor
24,034 satisfied customers
Oil furnace not hot just added fuel today. Flashing light
oil furnace not hot just added fuel today JA: Did you check the furnace's filters? Customer: flashing light says lockout mode JA: Do you plan on doing the work yourself? Customer: no JA: Anything else… read more
Rick
Rick
HVAC Supervisor
24,034 satisfied customers
Try trying to Prime my Thermo Pride oil furnace just turned
Try trying to Prime my Thermo Pride oil furnace just turned it on twice bled out some fuel now nothing … read more
Rick
Rick
HVAC Supervisor
24,034 satisfied customers
I have an oil furnace and the flame went out and i just hit
i have an oil furnace and the flame went out and i just hit the reset button like i have done in the past but it is stuck in now, the button.… read more
Rick
Rick
HVAC Supervisor
24,034 satisfied customers
Trane XV90 Oil Furnace. My furnace made some extra noise and
My furnace made some extra noise and then cut off... the red light on the oiled burner unit is flashing … read more
Rick
Rick
HVAC Supervisor
24,034 satisfied customers
Oil furnace will not turn on message says standby but it
Oil furnace will not turn on message says standby but it doesn't do anything can anyone help… read more
Rick
Rick
HVAC Supervisor
24,034 satisfied customers
Oil furnace will run if reset but will on run to degree,
oil furnace will run if reset but will on run to 69 degree, even if you have is set thermostat set on 80 degrees. Nozzle has been replaced, oil filter was changed.… read more
Rick
Rick
HVAC Supervisor
24,034 satisfied customers
Flashing light on Beckett oil furnace. The pump was seized,
Flashing light on Beckett oil furnace JA: Did you check the furnace's filters? Customer: Yes JA: Do you plan on doing the work yourself? Customer: The pump was seized , I installed a new one JA: Anyth… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,808 satisfied customers
i need a wiring diagram for a coleman mobile home gas furnace
i need a wiring diagram for a coleman mobile home gas furnace model # XXXXX… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
i have a patriot 80 oil furnace. sometime during the nite it
i have a patriot 80 oil furnace. sometime during the nite it shut off. theres a tiny grn light flashing. when we first hit it the furnace tried to fire. now nothing happens. theres a slight humming no… read more
Rick
Rick
HVAC Supervisor
24,034 satisfied customers
I own a mobile home with a Lear-Siegler oil furnace Model No.
I own a mobile home with a Lear-Siegler oil furnace Model No. MMG-82-COC. It heats up the oil but does not blow out the hot air. Can I get a manual somewhere so I could troubleshoot? Are there still p… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a honeywell th9421c1004 thermostat and the screen has
I have a honeywell th9421c1004 thermostat and the screen has gone blank… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
We are trying to install a RTH2510 thermostat - there are only
We are trying to install a RTH2510 thermostat - there are only two wires leading into the old round honeywell thermostat - what do we do?… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
We have an oil furnace that sputters when started, but comes
We have an oil furnace that sputters when started, but comes on and there are fumes that we smell as it is coming one. The sputtering does stop, but sometimes happens again after the heater has been o… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x