My 59SC2b furnace blower running time and blow cold air

My 59SC2b furnace blower...

My 59SC2b furnace blower running long time and blow cold air after heating cycle.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes. The filter is clean. There is no error code. It dosn't happen all the time. It usually after the second or third heating cycle after program change, i.e. from 63 to 66 in the eveing.

Contractor's Assistant: Do you plan on doing the work yourself?

No. I will can for service tomorrow. But I am curious because the unit is only three years old and was checked twice a year by a HVAC company..

Contractor's Assistant: Anything else we should know to help you best?

Is the high-temperature limit switch failing?

Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
12/17/2017
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,085
Experience: Furnace, A/C and heat pump specialist.
Verified

If a limit switch is opening you should get an error code.Could be a relay on board sticking.How long does it run after heat cycles off?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Thanks. It is running until the next heating cycle starts in 5 to 10 minutes. The blower stops, then the next heating cycle starts. It is only happens a couple of cycles after program change, i.e. from day, (63 C) to evening (66 C) or night (63 C) to morning (65 C). I only noticed this since last Wednesday. The outside temperature is at high teens or the low 20s every time this happened. I had A maintenance service done on Nov. 8.
Customer reply replied 6 months ago
Not necessary to call.

But no error codes?

Ask Your Own HVAC Question

If fan is in auto mode on thermostat, the issue has to be with a sticking relay on board if it runs past 3 minutes or there is an issue with thermostat.

Give me model on thermostat and let's check to see if maybe a setting there needs to be changed.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It is a carrier TB---PAC or TB---PHP, the one with hardwire power and battery backup. It's been running for the the last three years and has no issue.

If no changes were made the thermostat, issue is going to be the furnace control board

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It doing it right now.

Try disconnecting R thermostat wire and see if fan stops.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
II released the red wire from the thermostat. It didn't stop.

Fan relay on board is sticking and board will need to be replaced.Should be covered under waranty

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Thanks.

If you have further questions, please let me know.
Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
One of the back-up battery is leaky. Does this have something to do with the long blower run?

Not if releasing red wire from thermostat did not make fan stop

Ask Your Own HVAC Question
Customer reply replied 6 months ago
The red wire is labeled 24VAC in the manual. The thermostat was on battery when first installed, but it drained the battery really quickly. I had to call the installer and a technician got it hardwired. The unit came with a new construction and the installer did bad jobs for the entire neighborhood. It was fired and is no longer in service.

The batteries will not be the culprit in this situation.

If thermostat related whether battery or 24vac from furnace, disconnecting R wire would allow fan to go off which it does not.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Thank you very much for all your help. I will call my HVAC company tomorrow.

If you have further questions, please let me know.
Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,085
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 6 months ago
The HVAC technician from a local Carrier dealer thought the same but he cannot replace the board because the system worked normally when he was here. I have to wait until it happens constantly before he can order a new board. It is a waiting game now.Thank you very much for all your help.

Thanks fr the follow up

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,085
9,085 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My goodman furnace blower wont start running when the a/c
My goodman furnace blower wont start running when the a/c unit starts running outside. The blower fan runs slowly then shuts off. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
Needing a replacement compressor for a carrier 38YRA024310,
Needing a replacement compressor for a carrier 38YRA024310 … read more
airheatman
airheatman
HVAC Technician
9,085 satisfied customers
I'm looking at an infinity series carrier system with the 4
I'm looking at an infinity series carrier system with the 4 wire connection terminals "a,b,c, and d" could you tell me what the letters correspond to? The thermostat says indoor communication error an… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
My air furnace blower motor wont come on i replaced the
My air furnace blower motor wont come on i replaced the transformer as it was bad still nothing … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Carrier vs Rheem brand? Which one better? For carrier we got
Carrier vs Rheem brand? Which one better? For carrier we got 10 year warranty, 3 years labor and 5 year maintenance plan For rheem we got 10 year warranty, 2 year labor and 2 year maintennacr plan Any… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What Carrier thermostat will replace a Carrier Thermidistat
What Carrier thermostat will replace a Carrier Thermidistat installed in 2000? I want an exact functional replacement. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My furnace blower will not turn off. I removed the
My furnace blower will not turn off. I removed the thermostat but it continued to run. I had to run it off st the unit, is this a fan switch issue? Or could it be resolved with a new thermostat? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Furnace blower will kick on for a minute or two then stop.
Furnace blower will kick on for a minute or two then stop. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Oil furnace blower comes on, no flame or ignition. I buy the
oil furnace blower comes on, no flame or ignition JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: I buy the parts JA: Anything else we shou… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How does the cover get removed on a Carrier Carrier
How does the cover get removed on a Carrier Carrier TSTATBBP2S01B thermostat so I can replace it with an Ecobee? … read more
hvacdave84
hvacdave84
53 satisfied customers
Rheem furnace blower runs on low but will not run on high
rheem furnace blower runs on low but will not run on high furnace goes off on high heat limit … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
My Rudd furnace blower vibrates the entire house. Research
My Rudd furnace blower vibrates the entire house. Research indicates a motor/fan set screw may need tightening, but I can't see one. Where is it found? Can it be adjusted without removing the motor?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I, I installed a furnace control Board part # 62-24084-82.
I, I installed a furnace control Board part # 62-24084-82. It cycled once and will will not cycle again. all the controls are ok after checking them. any Ideas? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Goodman GVC9 furnace: blower will turn on, but no heat.
Goodman GVC9 furnace: blower will turn on, but no heat. Checked intake and exhaust, they look ok. Flashing code 4 so replaced the filter which needed replacing. Limit switch in middle of unit shows no… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My RUUD furnace blower is not turning on. The circuit board
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My '92 Carrier model 58ssc furnace blower motor has finally
Hi! My '92 Carrier model 58ssc furnace blower motor has finally quit. I wonder what I can replace it with … read more
airheatman
airheatman
HVAC Technician
9,085 satisfied customers
This is the same guy with the Goodman furnace control board
Hi, this is the same guy with the Goodman furnace control board / transformer. My plumber said what caused the board to fail was a short in the blower motor from water from AC unit backing up into blo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x