My 59SC2b furnace blower running time and blow cold air

My 59SC2b furnace blower...

My 59SC2b furnace blower running long time and blow cold air after heating cycle.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes. The filter is clean. There is no error code. It dosn't happen all the time. It usually after the second or third heating cycle after program change, i.e. from 63 to 66 in the eveing.

Contractor's Assistant: Do you plan on doing the work yourself?

No. I will can for service tomorrow. But I am curious because the unit is only three years old and was checked twice a year by a HVAC company..

Contractor's Assistant: Anything else we should know to help you best?

Is the high-temperature limit switch failing?

Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
12/17/2017
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,545
Experience: Furnace, A/C and heat pump specialist.
Verified

If a limit switch is opening you should get an error code.Could be a relay on board sticking.How long does it run after heat cycles off?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Thanks. It is running until the next heating cycle starts in 5 to 10 minutes. The blower stops, then the next heating cycle starts. It is only happens a couple of cycles after program change, i.e. from day, (63 C) to evening (66 C) or night (63 C) to morning (65 C). I only noticed this since last Wednesday. The outside temperature is at high teens or the low 20s every time this happened. I had A maintenance service done on Nov. 8.
Customer reply replied 9 months ago
Not necessary to call.

But no error codes?

Ask Your Own HVAC Question

If fan is in auto mode on thermostat, the issue has to be with a sticking relay on board if it runs past 3 minutes or there is an issue with thermostat.

Give me model on thermostat and let's check to see if maybe a setting there needs to be changed.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
It is a carrier TB---PAC or TB---PHP, the one with hardwire power and battery backup. It's been running for the the last three years and has no issue.

If no changes were made the thermostat, issue is going to be the furnace control board

Ask Your Own HVAC Question
Customer reply replied 9 months ago
It doing it right now.

Try disconnecting R thermostat wire and see if fan stops.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
II released the red wire from the thermostat. It didn't stop.

Fan relay on board is sticking and board will need to be replaced.Should be covered under waranty

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Thanks.

If you have further questions, please let me know.
Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
One of the back-up battery is leaky. Does this have something to do with the long blower run?

Not if releasing red wire from thermostat did not make fan stop

Ask Your Own HVAC Question
Customer reply replied 9 months ago
The red wire is labeled 24VAC in the manual. The thermostat was on battery when first installed, but it drained the battery really quickly. I had to call the installer and a technician got it hardwired. The unit came with a new construction and the installer did bad jobs for the entire neighborhood. It was fired and is no longer in service.

The batteries will not be the culprit in this situation.

If thermostat related whether battery or 24vac from furnace, disconnecting R wire would allow fan to go off which it does not.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Thank you very much for all your help. I will call my HVAC company tomorrow.

If you have further questions, please let me know.
Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,545
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 9 months ago
The HVAC technician from a local Carrier dealer thought the same but he cannot replace the board because the system worked normally when he was here. I have to wait until it happens constantly before he can order a new board. It is a waiting game now.Thank you very much for all your help.

Thanks fr the follow up

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,545
9,545 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My York furnace fired up for about 40 minutes and stopped
My York furnace fired up for about 40 minutes and stopped with red LED blinking 4 times. I can restart it by switch off electric power and switch on again. Air filter is brand new. What do you think i… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
It appears the furnace's gh limit switch is malfunctioning.
It appears the furnace's high limit switch is malfunctioning. The switch resets but then kicks off after a short while. How much should I expect to pay to have it replaced?… read more
Rick
Rick
Supervisor
24,666 satisfied customers
I have a Trane XR80 furnace, I was getting the gh limit
I have a Trane XR80 furnace, I was getting the high limit switch error message, we replaced the high limit switch and still get the same message, the burners go out at 66 degrees.… read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have a 2002 Goodman GMS 809003BNA furnace. I have taken a
I have a 2002 Goodman GMS 809003BNA furnace. I have taken a three week vacation each year and when I come back after setting the temp. to 60 it is no longer working. It cycles but never kicks in. Last… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a 6 year old mobile home we just moved in too. The
We have a 6 year old mobile home we just moved in too. The furnace heats the home very well. The blower comes on 4 times for about 15 seconds after the thermostat stops calling for heat. Is this blowe… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
Hello, I have a very old York Diamond 90 furnace, Model P3URC16N07501D.
Hello, I have a very old York Diamond 90 furnace, Model P3URC16N07501D. The furnace sometimes does not respond to the thermostat (i.e., thermostat set for 70, temp is at 66, furnace not on, even if ch… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
i have a DGAA070BDTA Coleman Furnace the light flashes 4 times
i have a DGAA070BDTA Coleman Furnace the light flashes 4 times indicating the limit switch i isolated it to the lower limit switch it is a 140-30 so it opens a 140 i put a thermometer in its place and… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello, I have furnace model TG9S080B12MP11A. When i program
Hello, I have furnace model TG9S080B12MP11A. When i program my thermostat to drop the house temperature when i leave my house and raise it 1hr before i get home, the furnace blows hot air then cold ai… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a propane furnace app 5 yrs old . when on a long heat
I have a propane furnace app 5 yrs old . when on a long heat cycle i.e. programmed low setting 62 degrees to 70 degrees the burner will stop sometimes before reaching set point but the fan will keep r… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
I have a goodman furnace flashing four lights (code) which
I have a goodman furnace flashing four lights (code) which by the panel said high limit issue. I checked the vent and it appears clean I even diconnected it and it still started flashing four lights w… read more
A-1 Tech
A-1 Tech
Service Manager
Vocational, Technical or Trade Scho
361 satisfied customers
Frigidaire fg6ra096c-16b This is for heat. I adjust the thermostat
Frigidaire fg6ra096c-16b This is for heat. I adjust the thermostat to 66. It comes on it runs fine. It then shuts down before the internal temp hits 66. For about 1min then turns back on. The internal… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
we have a Bryant Day and Night 376CAV036080 - 90 with Honeywell
we have a Bryant Day and Night 376CAV036080 - 90 with Honeywell F350 air cleaner. This does a number of things 1) stops before thermostat goal is reached - i.e. thermostat is set for 66 at 5:00 - heat… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Is it necessary to have my HVAC checked as often as they claim
Is it necessary to have my HVAC checked as often as they claim it needs to be checked? I.e. twice annually? Our HVAC service people charge extremely high prices for what doesnt appear to be much actua… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Air Ease Ultra V Tech 80 furnace with a new Honeywell
I have a Air Ease Ultra V Tech 80 furnace with a new Honeywell SV9520H valve and ST9160B control board installed. With thermostat turned down(no heat demand) the combustion fan cycles on/off every few… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a heildc90 motor and blower are staying on even after
I have a heildc90 motor and blower are staying on even after I've unhooked the red wire from the thermastat.… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Lennox warm air furnace Model 61MPV-60C with matching
I have a Lennox warm air furnace Model 61MPV-60C with matching evaporator coil, and media air cleaner model PMAC-12C. It is connected to a Lennox 49M55, or 49M56, or 49M57 programmable thermostat.It w… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I purchased a 80t furnace and ac unit this is my second heating
I purchased a 80t furnace and ac unit this is my second heating season I change my media filter every 3 months and unit is clean I woke up to a very cold house and notice my thermostat was calling for… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
fg6ra 096c 12b fRIGIDAIRE FURNACE SHORT CYCLES. GAS HEAT TURNS
fg6ra 096c 12b fRIGIDAIRE FURNACE SHORT CYCLES. GAS HEAT TURNS OFF AS SOON AS THE MAIN FAN STARTS. ERROR CODE IS 4 RED LIGHTS BLINKING ONE PER SECOND AND TEN 4 SECONDS OF NO RED LIGHT. fILTER WAS VERY… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x