Customer Question
I have Honeywell gas...

I have Honeywell gas controller WV4262W1107 that will not light and displays LED code with 7 flashes and 3 sec pause.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Just today

Contractor's Assistant: Do you plan on doing the work yourself?

Maybe. I am still investigating diagnosis

Contractor's Assistant: Anything else we should know to help you best?

There are no combustable vapor sources. The unit stopped working without changes made. I can not see issues with blocked airflow or loose wires. No visible damage to vapor sensor. Gas supply is available external to controller.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Have tried different settings for temperature. Don't know about the filters.

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
12/16/2017
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,405
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

What's the brand and model of your water heater?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Rheem XG50T
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

This is a gas controller failure error. The gas control valve will need to be replaced. How old is the unit?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Only a couple years
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Then it should be under warranty. Call Rheem on Monday and make a warranty claim(###) ###-####

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Thank you for that information. Do you know a way we might test the controller?
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

There is no test. The unit is self diagnostic. When you get this error the control itself has determined it is defective.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
That is pretty close to what the manual said. Thanks.
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

You're welcome

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,405
24,405 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an AO hot water heater model GPVH 40 100 Serial
I have an AO Smith hot water heater model GPVH 40 100 Serial Number 0950A012871. The water heater ins not operating. The gas control valve has the vacation light and the very hot light illuminated and… read more
Rick
Rick
HVAC Supervisor
24,405 satisfied customers
I have a Rheem model prog50-42-rh67 its giving me a 7 blink
Hi I have a Rheem model prog50-42-rh67 its giving me a 7 blink with 3 second pause which is saying my flammable vapor sensor is lockout how do I reset it. Its not even a year old… read more
Rick
Rick
HVAC Supervisor
24,405 satisfied customers
hi my flammable vapor sensor was open. I replaced it and I
hi my flammable vapor sensor was open. I replaced it and I still get seven blinks on my led telling me the vapor switch is out of range. when I place a 33k ohm resistor in place of the sensor I still … read more
Rick
Rick
HVAC Supervisor
24,405 satisfied customers
No heat - I have a Trane XV 80 gas system with a White Rodgers
No heat - I have a Trane XV 80 gas system with a White Rodgers 50A51-507 controller. Thermostat (Train XT 302C) is calling for heat (System is on heat and little flame is on) but nothing is happening.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an American Standard Freedom 80 model AUD100C945K4.
I have an American Standard Freedom 80 model AUD100C945K4. It's not working and the red light on the front is solid (not blinking). Is this something I can troubleshoot and fix or do I need to call a … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier WeatherMaker 8000 2 speed furnace (17 years
I have a Carrier WeatherMaker 8000 2 speed furnace (17 years old). It used to switch into high speed if it took, say more than 10 minutes to bring the room temp. up to the thermostat setting. I have n… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
TOSHIBA RAS M13 Inverter series air conditioner... my remote
TOSHIBA RAS M13 Inverter series air conditioner... my remote is working, and so is the air con, but when i point the remote to it, it does not do anything ( doesnt read the remote i think )… read more
V12Tech
V12Tech
252 satisfied customers
We have two Burnham Alpine 150, purchased in Dec 2010 and installed
We have two Burnham Alpine 150, purchased in Dec 2010 and installed in Oct 2011. Both performed well for winter 2011--12. On our first cold snap this season we called for heat and one started up and t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My arcoaire gas furnace (H9MPV125L20B1) will not start the
My arcoaire gas furnace (H9MPV125L20B1) will not start the combustion blower, stopping the startup procedure at the beginning. I can cycle the circulating air blower on and off with the thermostat whe… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a 2 year old Lennox G61MP furnace. It has begun stopping
I have a 2 year old Lennox G61MP furnace. It has begun stopping before reaching the thermostat set point. When checked it is displaying a 4+3 watch guard code. Power off and back on resets the unit an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Payne furnace for the lower zone of my house. The
I have a Payne furnace for the lower zone of my house. The blower run continuously but there is no ignition, no heat. The LED has 3 slow flashes and 3 fast flashes indicating a limit circuit fault or … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a new split heat pump system install. The heat pump
I have a new split heat pump system install. The heat pump is a model 25HPA6. The unit is extremely noisy to the point of vibrating the outside wall of the house. We have had to move out of that area.… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
What would cause the over temperature limit switch to keep
What would cause the over temperature limit switch to keep opening during the heating cycle on a Trane XL1100?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Armstrong model EG801000DC20-1.....roughly 15 yrs old; When
Armstrong model EG801000DC20-1.....roughly 15 yrs old; When furnace tries to light, ignitor sparks and pilot lights for 3-5 secs, then shuts off before main burner lights. Ignition module retrys after… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My furnace controller LED is flashing twice and pausing. The
My furnace controller LED is flashing twice and pausing. The legand sticker on the inside panel shows "external lockout, retries or recycles exceeded". What does this code mean and what can I do about… read more
Rick
Rick
HVAC Supervisor
24,405 satisfied customers
I have a trane gas hot air furnace model TDE 060A936A1 -Igniter
I have a trane gas hot air furnace model TDE 060A936A1 -Igniter energizes and gas vlve opens and gas ignites. -After running contiuously for 10-15 minutes the gas valve clicks several times in repid s… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
2STAGE FURN DRAFT MOTORRUNS AND SPARK AND GAS VALVE INGAGE
2STAGE FURN DRAFT MOTORRUNS AND SPARK AND GAS VALVE INGAGE SPLIT SEC OFF LED LEFT LIGHT BLICKS 6 TIMES THEN STEDY BOTH ON AND BLOWER MOTOR RUNS TRIES AGAIN IN ABOUT A MENUT… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
i have a gms81155cna heating unit. it keeps blowing the 3 amp
i have a gms81155cna heating unit. it keeps blowing the 3 amp fuse. when replaced it runs but reoccurs allmost immed. i dont get any diognostic flashing what could be causing it.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x