I am trying to replace a Dico heat pump thermostat with a Honeywell RTH3100C .trying to figure out the wiring.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes the old one has a glitch in it some times and mess with it and it ends up work .

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I have 8 wires one is not used and there is a jumper wire on the old one

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 15 minutes by:
12/16/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 8 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,747
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 8 months ago

Can you list the wire colors and terminals they were on, on the old thermostat?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Black on C terminal
Red on R
White on W2 with a jumper wire to E
Yellow on Y
Green on G
Orange on O/B
Blue not used
And brown not used
HVAC Technician: HVAC Guru, HVAC TECH replied 8 months ago

Yes that is just how you would connect them on the new one. Make sure there is a jumper from R to RC, and if your new one has a AUX then White would go to that and a jumper to E if you have one.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
On the new one I have
E
Aux
Y
G
O
L
R
B
C
Customer reply replied 8 months ago
how would that wire up
HVAC Technician: HVAC Guru, HVAC TECH replied 8 months ago

All thew same but you have to check the thermostat settings since the new thermostat has an O and B and you only have an O wire.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I want to convert my non-working Honeywell TA32H01 thermostat to a new Honeywell RTH3100C.
I want to convert my non-working Honeywell TA32H01 thermostat to a new Honeywell RTH3100C. I have a Waterfurnace heat pump system with aux. heat. Not sure of wiring the E and AUX terminals on the new … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
hHunter 441 series to replace old Honeywell round 5 wire. what
hHunter 441 series to replace old Honeywell round 5 wire. what to I do with the blue wire? Conventional heat/cool system.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Im replacing a Ritetemp8010 thermostat with a Honeywell RTH3100C
I'm replacing a Ritetemp8010 thermostat with a Honeywell RTH3100C thermostat. I marked all the wires from the old connection and reconnected all the cors back to the new thermostat however the RC wire… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How do I wire a Honeywell RTH3100C The directions call for
How do I wire a Honeywell RTH3100C? The directions call for 8 wires and my old thermostat has only 4 wires?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Trane TWVO36B14FA1 ah and 2TWR3030A1000AA heat pump.
I have a Trane TWVO36B14FA1 ah and 2TWR3030A1000AA heat pump. Am attempting to replace original t-stat (Trane dual-bulb mercury model Baystat240A, 3AAT82B1B1) with a Honeywell RTH3100C digital unit an… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Im trying to replace a Honeywell model LR69071 thermostat
I'm trying to replace a Honeywell model LR69071 thermostat with a Honeywell model RTH3100C on a Goodman HVAC system. The wiring seems a little confusing using the installation guide. Old thermostat Te… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I need help wiring a honeywell RTH3100C thermostat, my old
I need help wiring a honeywell RTH3100C thermostat, my old one is a trane and I'm not sure what the model # XXXXX Honeywell thermostat has E AUX Y G O L R B C. I labeled the wires coming out of the wa… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Carrier Heat Pump that I am trying to change the thermostat
I have a Carrier Heat Pump that I am trying to change the thermostat on. The new thermostat (Honeywell model RTH3100C) does not have a W1 psot nor a W2 post. The Y post on the old one is bridged to th… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
This house has a Coleman thermostat control,with a red and
This house has a Coleman thermostat control,with a red and a white wires only.I picked up a Honeywell RTH3100C the other day to replace it ,but am not shure how to hook it up.The instructions expect y… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I am trying to replace an old Robertshaw thermostat on an America
I am trying to replace an old Robertshaw thermostat on an American Standard heat pump with a Honeywell RTH3100c thermostat. The old thermostat only has 4 wires going to it. They are W O G and Rc. It l… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I am replacing my old thermostat (janitrol HPT18-60) with a
I am replacing my old thermostat (janitrol HPT18-60) with a non- programmable Honeywell RTH3100C thermostat. I have a goodman central air/heat pump system. Old one has 7 terminals with 6 wires. The wh… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have Rheem rbhc 24, I want to install a new thermostat, my
I have Rheem rbhc 24, I want to install a new thermostat, my wires on old thermostat as follows: W- white wire RH- Black jumper wire from RC B- no wire RC-Red wire, with black jumper to RH O- no wire … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have just installed a Honeywell RTH3100C. I installed using
I have just installed a Honeywell RTH3100C. I installed using installation guide. Everything works as it should, air conditioner works, heater says it is onbut no heat comes out when the fan comes on.… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a Honeywell RTH6400. I am trying to replace an old
I have a Honeywell RTH6400. I am trying to replace an old Trane thermostat. The Honeywell has G WO/B not used Y R Rc My old thermostate has 7 wires going to G O X2 W Y T R B W has its own wire and a j… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I just replaced a merc controlled thermostat with a rth3100c
I just replaced a merc controlled thermostat with a rth3100c honeywell non-programmable digital one ( a heat pump ). all the wires matched the new one except the old one did not have a L wire coming f… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I am replacing my current thermostat with a honeywell RTH3100C
I am replacing my current thermostat with a honeywell RTH3100C version.I noticed that the color of my existing wires are red,white yellow and green but the new terminal on the RTH3100c does not show a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Heating/AC system uses a four wire White, Red, Green, Yellow
My Heating/AC system uses a four wire White, Red, Green, Yellow cable to the thermostat. The colors seem to correspond to convention. I have a Honeywell RTH3100C thermostat. Hooking up the Red, Green … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I need to know how the wireing should hook up on a janitrol
I need to know how the wireing should hook up on a janitrol heat pump the old wireing is different colors. We tried to hook up a honeywell thermostat and the outside unit will not comed on.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x