Have a Honeywell triple aquastat type l8124a. I have a

Customer Question
Have a Honeywell triple...

Have a Honeywell triple aquastat type l8124a. I have a burnham boiler with a beckett burner. this is a tankless hot water system. I am getting hot water, but when either thermostat calls for heat I am not getting heat. I have voltage at connections tt, but no voltage at connections c1 c2. I assume I'm getting voltage at b1 b2 because my burner is still working. is this something that I can fix or do I need to call a repairman?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Forced hot water system two zone. both zones calling for heat voltage at both zone valves

Contractor's Assistant: Do you plan on doing the work yourself?

I would like too, avoid the extra charge for the weekend service call

Contractor's Assistant: Anything else we should know to help you best?

I think i provided everything, i think...

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/16/2017
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,395
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

The L8124 will disable the heating pumps as long as boiler temp is below the set point of the LO limit. This is to prioritize DHW. If this was not the case you might not have hot water on real cold days. One thing you can try is to turn the LO down to around 140-150. This will allow the heating pumps to run and will give you enough DHW in most cases.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
my boiler is used for heat and hot water. I have hot water, no heat. the burner/boiler is working fine for hot water, temps are good.
Customer reply replied 7 months ago
no call, type is fine.
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

I got that and the answer I just posted addresses this issue. One other possibility IF the boiler temp is above the LO setting and the pumps still don't run is that you have a bad L8124. You can easily tun down the LO setting. Replacing the control may be something you want to leave to a plumber.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
there is a relay on the board, what is that for and can that be replaced? would that cause my issue?
Customer reply replied 7 months ago
hey, I did a lot of troubleshooting work to get to the l8124 board knowing that was the issue. I wanted to know if there was any way to check anything on the board to see if I could get some heat.thanks anyway.
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

I've answered this question explaining the function of the control. Did you try anything I advised? I've been at this for 45+ years and know this control inside and out. The first thing to try is turning down the LO setting.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,395
24,395 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Vaillant GA92-140 boiler in my home and it will not
I have a Vaillant GA92-140 boiler in my home and it will not start up this fall. The thermostat is calling for heat but no ignition cycle is started. I tried the ignition modual reset procedure posted… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
, I ran out of oil on my furnace. Now I am getting an error stating low voltage on my
Hello, I ran out of oil on my furnace. Now I am getting an error stating low voltage on my r7284. originally the display seem not to have power so I took the cover off and it seems like it was wired w… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
I want to replace the R8182D with a L7224 but what happens
I want to replace the R8182D with a L7224 but what happens to the cad wires? I have the new unit in and the house is getting cold. I need to fire this up.… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
How do I wire a Beckett 7600 AquaSmart Boiler Control in replacement
How do I wire a Beckett 7600 AquaSmart Boiler Control in replacement of a Honeywell L8151A aquastat?… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
I have an oil boiler/furnace that is about 30 years old and
I have an oil boiler/furnace that is about 30 years old and well maintained. I think it is a honeywell, but I am not sure as I can't find the information on it. It not only heats the house but also pr… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
I have a Honeywell aquastat relay type l8148e. I am trying
I have a Honeywell aquastat relay type l8148e. I am trying to get the circulator pump for the zone wired in properly, not the boiler circulator. Currently the outside zone circulator is wired into C1 … read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
Hi, I have a problem with no heat to my 2 heating zones.
Hi, I have a problem with no heat to my 2 heating zones. The boiler runs for the domestic hot water. I have a aquastat L8124a relay. Any suggestions?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Slant/Fin Model S-90DP With a Aquastat Relay Type
I have a Slant/Fin Model S-90DP With a Aquastat Relay Type L8148E. My question is how to wire it so that the circulator runs when the boiler reaches 180 shuts down the fire and the thermostat is still… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
We have just installed a newer New Yorker Boiler. The electrician
We have just installed a newer New Yorker Boiler. The electrician came and wired the pumps (taco),burner (Becket AFG),low water cut off (safegaurd) and auastat (l8124a,c Honeywell). When I turn the sa… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
I have a honewell l8124a c triple aquastat installed on a oil
I have a honewell l8124a c triple aquastat installed on a oil fired hot water boiler. the circulator does not come on when hooked up to the c1 c2 terminals, when contact is held in pump runs. disconec… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Wayne boiler controled by a Honeywell L8124A Triple
I have a Wayne boiler controled by a Honeywell L8124A Triple aqustat relay. The setings are High 190 Low 140 and Difrencial 15. Sometimes when the termostat calls for heat the controler does not turns… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
I have an Aquastat Relay L8148E. There is no power to any of
I have an Aquastat Relay L8148E. There is no power to any of the componets. If i hold down the switching relay everything works. What causes the switching relay to contact to provide power, and what c… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
This site has helped me on at least three different occasions
This site has helped me on at least three different occasions before, is there a link or a schematic that can get me through this process… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
How do i wire my Honeywell triple aquastat L8124A (Water heater
How do i wire my Honeywell triple aquastat L8124A? (Water heater boiler) We have 2 motorized valve, with 2 red and yellow wires on each of them, and two thermostat. The aquastat have T&T, ZR and ZC. I… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
i wanna do one room with radiant heat, i already have a hydro
i wanna do one room with radiant heat, i already have a hydronic heating systeam with 3 other baseboard zones. my question is can i just use another regular honeywell zone valve with a mixing valve fo… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
On the L7248A relay, I would like to activate the burner from
On the L7248A relay, I would like to activate the burner from a line voltage circulator relay. Do I feed ZR? or 1,2 under TT? Ralph… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
tankless boiler - Utica brand - four months ago the call for
tankless boiler - Utica brand - four months ago the call for domestic hot water did not kick on the boiler. The call for heat would still kick on the boiler. Today there the boiler will not start on a… read more
Rick
Rick
HVAC Supervisor
24,395 satisfied customers
I bought an electric hot water tank. I want to disable the
I bought an electric hot water tank. I want to disable the domestic hot water temp control because the furnace is turning on to heat the hot water when the house it at the correct temp. How can I disa… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x