JBM. Lennox G26. Furnaces runs normal for approx 30 secs…

Customer Question
Hi JBM. Lennox G26. Furnaces...
Hi JBM. Lennox G26. Furnaces runs normal for approx 30 secs then blower motor stops. Furnace continues to run until limit switch tripped. Throws "Primary/secondary limit switch open" code. I cleaned the flame sensor and installed new limit switch so far.
Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 38 minutes by:
12/16/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 8 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,751
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 8 months ago

Can you see what limit is opening?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I'm not sure how to tell which limit it is. I replaced the temperature limit switch. At first I couldn't get the blower motor to turn on at all, then after reading that it might be the vacuum switch, I blew into one of the vacuum tubes and that seemed to get the furnace running for 30 seconds.
HVAC Technician: HVAC Guru, HVAC TECH replied 8 months ago

This is likely a thermal rollout issue. There are high limit safety thermostats that are around the burner housing area that can trip open if they fail or the unit is overheating. Some of these have reset buttons on them that you can manually press down to reset while others do not. The ones that do not either are one time limits or are limits that are suppose to manually reset when cooled down. Now that does not always happen when they go bad so you will have to check them for continuity with an ohm meter across the two leads going to them. If you do not pwn a ohm meter you can physically bypass each rollout to make sure it is good by connecting the two wires to each rollout sensor together to see if the unit will then operate. Now once you have found the bad one you can change it out or reset it and then you should check your furnace filter for blockages and make sure you main furnace blower is running to speed. These two things can cause a unit to overheat and trip one of these rollout sensors. Mosts units have 3 of these devices and here is a link to what they can look like on your unit.

CLICK HERE

CLICK HERE

CLICK HERE

All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I have the first two limit switches. The one with the reset button doesn't push in or pull out so not sure if it is tripped. I did bypass it but furnace still doesn't stay running.
What would happen if the vacuum switch was bad? Would furnace run at all?
Customer reply replied 8 months ago
How do I check if the motor is running to speed? It seems to be running normally.
HVAC Technician: HVAC Guru, HVAC TECH replied 8 months ago

If the pressure switch opened nothing would run. Can you upload a picture of the wiring diagram on your unit here for me to check out?

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 8 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,751
18,751 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Lennox G50UH-48V110-05 furnace that the gas valve
I have a Lennox G50UH-48V110-05 furnace that the gas valve is not coming on. The right green light flashes slowly and the code says Flash sensed without gas valve energized. What could that be? I am a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennoxG43UF-36B-70-09 furnace. Fan running but no
I have a lennoxG43UF-36B-70-09 furnace. Fan running but no heat. Filter clean. Message lights indicate"a)primary … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My furnace start wont turn on it says primary secondary
my furnace start wont turn on it says primary secondary limit switch open its a lennox … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Lennox G60UHV-36B-090-06 furnace. Burners comes on
I have a Lennox G60UHV-36B-090-06 furnace. Burners comes on and it runs for 1 minute or so. Shuts off. Blower Moyer does not run. Diagnostic code- says primary/secondary limit switch open. Why is blow… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox G60UHV, the furnace will light and run for
I have a Lennox G60UHV, the furnace will light and run for a short time and kick off. It gives the fault Primary/secondary limit switch open Primary secondary or rollout switch open. Any help would be… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I HAVE A LENNOX G26 PUT IN 1997 BURNERS KICK ON RUNS FOR
I HAVE A LENNOX G26 PUT IN 1997 BURNERS KICK ON RUNS WHILE SHUTS DOWN NO BLOWER COMES ON REPLACED MOTOR LAST YEAR REPLACED FLAME SENSOR WITH GENARIC ONE… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Lennox gas furnace will not kick on the blower motor-have
My Lennox gas furnace will not kick on the blower motor-have tried everything I know to do.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi my lennox mod 70625441 wont ignite. The fan blower kicks
Hi my lennox mod 70625441 wont ignite. The fan blower kicks on but no heat. then the fan does not shut off. help Thank you Tony… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
i have a goodman gas furnace model gmp125-4 that i am having
i have a goodman gas furnace model gmp125-4 that i am having trouble with here's what it does "the thermostat will click to turn furnace on the induction motor for exhaust gas will come on and run nor… read more
hvac-technician
hvac-technician
Service Manager
Vocational, Technical or Trade Scho
62 satisfied customers
I have a elite model ghr26q3-75 My problem is that the furnace
I have a elite model ghr26q3-75 My problem is that the furnace will start and run for a bit then shut down it shows a error code of left led on right led slow flash I cleaned filter and then removed f… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
Are there 2 parts to the furnace starting up This fall I noticed
Are there 2 parts to the furnace starting up? This fall I noticed the furnace starts to warm up for about 30 sec, the fan does not turn on and the furnace stops. It waits 10 sec and repeats over and o… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Lennox G2603-75-3 that the blower is running constantly
I have a Lennox G2603-75-3 that the blower is running constantly but will not ignite. The Diag lights show that the Primary/ Secondary Limit Switch is open. How do I find the limit switch so I can res… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
F8AUH Gas Furnace. When there is a demand for heat the unit
F8AUH Gas Furnace. When there is a demand for heat the unit starts up normally. After about 30 seconds after the burner ignites it shuts off. The blower continues to run. The two LED's, left slow flas… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
coleman furnace with code 4 and 11...thinking blower motor....any
coleman furnace with code 4 and 11...thinking blower motor....any suggestions? When I turn it on small intake fan runs....then igniter fires up then...shuts down and throws codes. Blower motor never c… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a lennox G26 furnace. The fan runs and blows cold air.
I have a lennox G26 furnace. The fan runs and blows cold air. The LED indicator was the left light flashing slow and the right light was solid, this indication based on the info on the cover of the fu… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
my furnace isnt working right it was just blowing cold air
my furnace isnt working right it was just blowing cold air last night when i turned it off waited 5mins and turned it on it would work for a little bit but then the warm air turned cold again today th… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a rheem fuenace model rgle-12erajs. It keeps short cycling
I have a rheem fuenace model rgle-12erajs. It keeps short cycling what could be causing this?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Lennox G23 series furnace. The pilot is lighting,
We have a Lennox G23 series furnace. The pilot is lighting, but blower will not kick on. The diagnostic code indicates "PRIMARY/SECONDARY LIMIT SWITCH OPEN". What is the primary/secondary limit switch… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x