Trane xl90 furnace tdc0808942a0 no power to ifc. They are…

Customer Question
Trane xl90 furnace tdc0808942a0...

Trane xl90 furnace tdc0808942a0 no power to ifc

Contractor's Assistant: Did you check the furnace's filters?

Yes they are new

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 hours by:
12/16/2017
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,348
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Sorry for wait. Check the fan board to see if there is a 5 or 3 amp auto type fuse.. It may be blown. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The fan runs when I turn it on manual.
Customer reply replied 7 months ago
Where is that located
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

Euse will be located on fan board it is auto type fuse. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

Fuse located on furnace board. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

If the fan comes on you have power to furnace and should have power to board on L1 and L2. Does the ignition module have a red LED on. Does it flash a code. Do you have 110 between L1 and L2.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
strangest thing. I checked the voltage between l1 and l2 9v. The induction fan turns on the green light came on and it had a flame for a second then shout off. I am now back to the beginning with no led on at all. There is no wire hooked to L2
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

Go from L1 to ground .You should get 115 volts. If you do bad board. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Yep brand new and bad. I had the same thing happen about 10 years ago. Ok thanks.
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

You are welcome. Good work. I will open rate box for you. Just google that number on furnace board and several sites will come up. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

Need anymore help. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Not sure yet I have to get the part on Monday.
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

Ok let me know. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok u changed it out same thing. 14 v from l1 to l2. L1 to ground is 115
Customer reply replied 7 months ago
I changed not u changed
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

The two power wires coming in Black L1 and white connect to L2 on board. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
That's strange i took them off and put them on exactly as they were on the old one. Can you see the picture I uploaded?
Customer reply replied 7 months ago
L1 Is a red wire in this furnace can you see the picture?
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask gotoman for ac Your Own Question
gotoman for ac
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,348
5,348 Satisfied Customers
Experience: 51 years of experience install design and repair of all makes and models of AC

gotoman for ac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I've looked all over the JA site and I canot find out how
Hello. I've looked all over the JA site and I canot find out how much it costs to ask a question. … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a Trane XL90 gas furnace with a 50E47-060 controller,
I have a Trane XL90 gas furnace with a White Rogers 50E47-060 controller, the furnace ignites but shuts right down. The light on the controller flashes. I shut the power off to reset but no change. Th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am trying to install a Honeywell WIFI thermostat to my XL90
I am trying to install a Honeywell WIFI thermostat to my XL90 Trane Furnace. I tried to follow the bypass for the C wire by using the G wire however there is no C connection in the furnace. Please hel… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a trane XL90 furnace that seems to be not lighting
We have a trane XL90 furnace that seems to be not lighting normally. I habe to shut the power off to the furnace, wait a couple minutes, and turn the power switch back on to get it to work. So far onl… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,348 satisfied customers
I have a Trane XL90 TUC series from 1987 that stopped working
I have a Trane XL90 TUC series from 1987 that stopped working yesterday. The exhaust fan turns on, the igniter glows, but no flame. Today is the coldest day of the year so far, any suggestions?… read more
MRANSWER
MRANSWER
TECHNICIAN
Bachelor\u0027s Degree
6,158 satisfied customers
I have a Trane furnance (80 family). About every 6 ours or
I have a Trane furnance (80 family). About every 6 ours or so the IFC gives a flame not sensed error. I have replaced the flame sensor and the electronic ignitor with no success. How can I determine i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Just did a gas range install and the furnace kicked on while
Just did a gas range install and the furnace kicked on while the gas was shut off. Gas is back on but no hot air coming out of the vents. I have tried turning the system off and then on again about a … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i have a trane xl90 furnace that is about 25 years old or so.
i have a trane xl90 furnace that is about 25 years old or so. my issue is when the furnance kicks on, everything starts up as normal for about a day or so, at which point when the gas kicks in and lig… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane XL90. When it should be cooling, the outdoor
I have a Trane XL90. When it should be cooling, the outdoor unit runs, but the circulating fan in the furnace part does not start. I've tried it in "Auto", "Circulate" and "On" fan modes on my thermos… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I am a mechanical engineer designing a hvac system for a small
I am a mechanical engineer designing a hvac system for a small office addition using a Trane XL90 gas furnace in a downflow configuration. All ductwork will be under the floor with air supplied to the… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a trane XL90 TUC100B8949A0 furnace, the ignitor comes
I have a trane XL90 TUC100B8949A0 furnace, the ignitor comes on but the gas valve doesn't let the gas out. It tries three times and then the control unit goes into lock-out mode. the control unit is a… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,348 satisfied customers
Trane XL90... early 1990s installation. Fan runs normally,
Trane XL90... early 1990's installation. Fan runs normally, venting fan comes on but burners never light. red light steady flashing… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a Trane TUX1 XR90 furnace and companion AC unit for
I have a Trane TUX1 XR90 furnace and companion AC unit for 2nd floor. I set the therm. to cool, fan control to auto, and temp to 78 to cool off upstairs for bedtime. In the AM the blower (but not AC) … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,514 satisfied customers
How do you wire an Aprilaire 600A to a Trane XL90. The XL90
How do you wire an Aprilaire 600A to a Trane XL90. The XL90 two stage has no heat pump and I just do know where to wire terminals W/G and CF from the 600 to the furnace. I do have the 24 Volt Transfor… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
We have a Rheem gas furnace that up until recently worked just
We have a Rheem gas furnace that up until recently worked just fine. For some reason now the draft inducer fan will not stop running and regardless of the thermostat setting cycles for heat. I am runn… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane xl90 2 stage furnace that is not working. I
I have a Trane xl90 2 stage furnace that is not working. I have followed the instructions on the outside of the unit for getting it to reignite but it has not worked. There is a red flashing light tha… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I just had a hvac mechanic replace my indoor and outdoor units.
I just had a hvac mechanic replace my indoor and outdoor units. I requested for Trane XL 15i and paid little extra for that specific unit. They installed the indoor unit and it shows no XL mark (only … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Would you buy a 2 stage or a 3 stage high efficency furnace
Would you buy a 2 stage or a 3 stage high efficency furnace & what make? we have a 1600 sq ft house detached upstairs & downstairs (full basement not finished or inc in 1600sq ft measurement.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x