carrier rooftop unit mod #48hjd015..... (6) six flashes .. draft inducer... replaced with part # hc30gb230 factory part.. still (6) flashes... replaced igniter module part #lh33wp002... still (6) flashes.. proved good ground.. still (6) flashes

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Thermostat is calling .. jumped R+ to W1 24vac present.. filters have been changed...

Contractor's Assistant: Do you plan on doing the work yourself?

Yes... 06A and CFC lic.

Contractor's Assistant: Anything else we should know to help you best?

Tested all my safety and roll-out switches but all these things must be in place before inducer will go ..no other codes... unit next to it (same mod) also gives (6) flashes when I pull inducer sensor.. thought bad board. it happens out of the box so installed new and new sensor on motor.. still (6)

Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
12/15/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,920
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy. Does the draft fan run when started?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 months ago

and when you say you replaced sensor...is it the Hall Effect Sensor?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
replaced with new out of box motor and control board have them both on shelf...(x2)
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 months ago

Thank you,

And the board you replaced...is the board the hall effect sensor plugs on to?...3 prong molex?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
oem part # Lh33wp002
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 months ago

Thank you. And you checked the vent assembly to make sure no blockage?...did you check the heat exchanger at the back turns where these are notorious for holes?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
no blockage... no pressure switch.. did not check heat exchanger..
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 months ago

Ok ,

Is this series rtu one that has a limit switch in the blower section? A reset limit?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
tested ok but jumped for piece of mind cause im losing mine
Customer reply replied 2 months ago
two limits and one role out
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 months ago

Wow...there is not much more.....I assume you already confirmed a proper ground?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
added an extra from service ground lug..
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 months ago

single or 3 ph?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
3 phase unit .. 208 inducer
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 months ago

The strange thing is the hall effect is just magnetic response...as long as the idm shaft spins it creates the pulse....you can actually do this by spinning the unit by hand.

It must be in the ground, supply, phase etc....the effect sensor itself is just a dc reaction....

Ask Your Own HVAC Question
Customer reply replied 2 months ago
changed magnet even added an extra still (6) flashes
Customer reply replied 2 months ago
she is running at full speed motor is 3400 rpm but I have used two new motors and two new control boards
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 months ago

Well you won the award today for the stump the panel....

I am going to open this up to the others to have a look and see if we can come up with something.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
even ruffed up inside of last sensor body
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Carrier WeatherMaker 8000 which is 11 years old and
I have a Carrier WeatherMaker 8000 which is 11 years old and is installed in the Attic. It has been cycling on with heat for about 8 or 9 minutes, shuts down, and then restarts withiin a minute. It do… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
0 satisfied customers
getting code 32 on my carrier weathermaker 8000. What is the
getting code 32 on my carrier weathermaker 8000. What is the fix… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
How much does it cost to replace a Variable-speed blower motor
How much does it cost to replace a Variable-speed blower motor on a WeatherMaster 8000VS? I got a quote for $1300 and they suggest rather than dumping money into old furnace (13 yrs old); buy a new on… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier Weathermaker 9200 is showing 1 short light and 3
Carrier Weathermaker 9200 is showing 1 short light and 3 long ones … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
277 satisfied customers
The ignitor to my Carrier furnace will not trigger so no
Hi Pearl. The ignitor to my Carrier furnace will not trigger so no heat can enter the house. I've manually reset the limit switch and cleaned the flame sensor and was looking for suggestions on what t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Phil, we have a Carrier Infinity Weathermaer natgas
Phil, we have a Carrier Infinity Weathermaer natgas furnacethis week the limit switch had to reset at lest 4 ties. We replaced the limit switch,ever since then the furnace runs but the top of the plen… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I Have a Carrier gas furnace model PG9MAB060120A. The
I Have a Carrier gas furnace model PG9MAB060120A. The burners blow but the air from the heat exchange at the furnace is luke warm. Is there a problem with the heat exchange? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have Carrier fan coil unit model FV4CNB003. Have Carrier Fan
Have Carrier Fan Coil unit # FV4CNB003. Seemed to run and change speed during operation. Is this normal? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I HAVE A CARRIER CNPHP HVAC SYSTEM THAT IS LEAKING WATER
I HAVE A CARRIER CNPHP HVAC SYSTEM THAT IS LEAKING WATER INTO THE SAFETY PAN BELOW. THE TECHNICAIN DIAGNOSED THE PROBLEM AS THE SECONDARY HEAT EXCHANGER HAS A CRACK. THE UNIT IS TEN YEARS OLD. RATHER … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,920 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x