Carrier rooftop unit mod #48hjd015..... (6) six flashes ..

Customer Question
carrier rooftop unit mod...

carrier rooftop unit mod #48hjd015..... (6) six flashes .. draft inducer... replaced with part # hc30gb230 factory part.. still (6) flashes... replaced igniter module part #lh33wp002... still (6) flashes.. proved good ground.. still (6) flashes

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Thermostat is calling .. jumped R+ to W1 24vac present.. filters have been changed...

Contractor's Assistant: Do you plan on doing the work yourself?

Yes... 06A and CFC lic.

Contractor's Assistant: Anything else we should know to help you best?

Tested all my safety and roll-out switches but all these things must be in place before inducer will go ..no other codes... unit next to it (same mod) also gives (6) flashes when I pull inducer sensor.. thought bad board. it happens out of the box so installed new and new sensor on motor.. still (6)

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
12/15/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,121
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy. Does the draft fan run when started?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

and when you say you replaced sensor...is it the Hall Effect Sensor?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
replaced with new out of box motor and control board have them both on shelf...(x2)
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

Thank you,

And the board you replaced...is the board the hall effect sensor plugs on to?...3 prong molex?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
oem part # Lh33wp002
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

Thank you. And you checked the vent assembly to make sure no blockage?...did you check the heat exchanger at the back turns where these are notorious for holes?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
no blockage... no pressure switch.. did not check heat exchanger..
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

Ok ,

Is this series rtu one that has a limit switch in the blower section? A reset limit?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
tested ok but jumped for piece of mind cause im losing mine
Customer reply replied 7 months ago
two limits and one role out
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

Wow...there is not much more.....I assume you already confirmed a proper ground?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
added an extra from service ground lug..
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

single or 3 ph?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
3 phase unit .. 208 inducer
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

The strange thing is the hall effect is just magnetic response...as long as the idm shaft spins it creates the pulse....you can actually do this by spinning the unit by hand.

It must be in the ground, supply, phase etc....the effect sensor itself is just a dc reaction....

Ask Your Own HVAC Question
Customer reply replied 7 months ago
changed magnet even added an extra still (6) flashes
Customer reply replied 7 months ago
she is running at full speed motor is 3400 rpm but I have used two new motors and two new control boards
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

Well you won the award today for the stump the panel....

I am going to open this up to the others to have a look and see if we can come up with something.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
even ruffed up inside of last sensor body
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
York diamond 80. I just bought this house as a rental and
York diamond 80. I just bought this house as a rental and when I turn on the furnace I get 5 short blinks. I go to the flame rollout switch and see it was removed by the previous owner. I then connect… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Model48tme006-a-501 no heat p/c board led flashes 6 times. 3
model48tme006-a-501 no heat p/c board led flashes 6 times … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have a carrier rooftop unit that heat want come on. The board
I have a carrier rooftop unit that heat want come on. The board is flashing purge motor failure but it runs continuously. The blower will run also if set to fan ON at TS. I replaced the igniter board … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have a Carrier WeatherMaker 8000 2 speed furnace (17 years
I have a Carrier WeatherMaker 8000 2 speed furnace (17 years old). It used to switch into high speed if it took, say more than 10 minutes to bring the room temp. up to the thermostat setting. I have n… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Carrier 38CKC048 and last night it stopped working.
I have a Carrier 38CKC048 and last night it stopped working. I have no experience fixing these kinds of things but today is Christmas so I'm probably on my own with a house full of cold people. How do… read more
V12Tech
V12Tech
252 satisfied customers
Goodman stage warm air furnace settings for the dip switches
I have a Goodman GCH90703BX 2-stage warm air furnace that I only want to run as a single-stage with high blower fan speed heat. What settings do I need for the dip switches and which wires on the wiri… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
90plus 10 yrs old. furnace would not start, servece man
bryant 90plus 10 yrs old . furnace would not start, servece man replaced mother board furnace would than cycle to combuation, fan would not come on. servece man condemed the furnace. recomded a new am… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
have a Trane XL80 2 stage unit. when I turn on heat just
have a Trane XL80 2 stage unit. when I turn on heat just get a click sound as if the thermostat is sending a signal to start the heater; however nothing turns on, no fan, nothing cooling works just fi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
carrier 48hjd005 rooftop unit. If the draft inducer fan is
carrier 48hjd005 rooftop unit. If the draft inducer fan is running, is it the hall-effect sensor that has failed when we get 6 flashes, indicating a bad motor?… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a carrier model 58PAV135-20 furnace. It wont start
I have a carrier model 58PAV135-20 furnace. It won't start and the LED appears to be flashing a code (2 short flashes followed by 4 long flashes). Is there a place online that describes these codes?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,121 satisfied customers
Furnace will not go to stage 2 - Have MVP 80 Model #2404A10954
Furnace will not go to stage 2 - Have MVP 80 Model #2404A10954 Carrier Furnace installed 11/09/04 - 2 service men have been out - one said he rewired the "circuit board to run on low but that we neede… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
trane furance not heating three flashes stating pressure switch
trane furance not heating three flashes stating pressure switch problems,but switch reads good but not voltage going to inducer mtw to start heating cycle but 120volts from transformer to white rodger… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
i have a amana air command 80 sse, blows cold air, cleaned
i have a amana air command 80 sse, blows cold air, cleaned flame sensor, nothing? thanks Jim… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Goodman/Janitrol Model # GMP125-4. The circuit panel
I have a Goodman/Janitrol Model # XXXXX The circuit panel is flashing red light 3 times. Can I jump out the Pressure switch, part number B13701-26?| I don't have a new part for it and the supply house… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Hi,my carrier hvac rooftop model # 48NLT036300 just quit working
Hi,my carrier hvac rooftop model # XXXXX just quit working , i open the door panel to inspect , turn on the power the draft inducer come on then the ignitor start clicking sound but no sound of gas to… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,121 satisfied customers
I have a gas furnace (carrier 58dhb075-cc/1986) which induce
I have a gas furnace (carrier 58dhb075-cc/1986) which induce draft moter wont come on. What is the problem… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hi there, I have a Carrier Weathermaker 8000. From 1994.
Hi there, I have a Carrier Weathermaker 8000. From 1994. My LED diagnostic light is blinking but I do not have an error code legend on my furnace, so I do not know what the flashes mean. Help!… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,121 satisfied customers
Armstrong Furnace Ultra V Tech 90 wont start. The LED is on
Armstrong Furnace Ultra V Tech 90 won't start. The LED is on and does not flash. I checked the hose from the pressure switch to be sure it was not clogged. I can hear the light buzz of electrical powe… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x