I just purchased a condo in Nashville TN with an 'older'

Customer Question
Hi. I just purchased...

Hi. I just purchased a condo in Nashville TN with an 'older' heat pump system which is running virtually non-stop in order to hold temp. The 'aux heat' is cycling on and off, so I think the system is functional. My question - is it possible to adjust/reduce the fan speed on the inside unit (Carrier 40AQO24300EH, S/N J7A 35742). Thank You! ***** ***@******.***

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Just installed Honeywell RTH3100C thermostat days ago, and have re-checked installation, wiring and settings with Honeywell twice. Filter is a few weeks old - it's 3M filtrete 20x25x1 'clean living' electrostatic. Is there a spec for air filters - do I have too much air resistance?

Contractor's Assistant: Do you plan on doing the work yourself?

Yes if I can - but I have my limits in which case I would contact an expert. We've worked with Lee Heating & Cooling here in Nashville.

Contractor's Assistant: Anything else we should know to help you best?

Not sure, but this is our first experience with a heat pump system, so we realize it will 'run more'. Just seems to us more noise and 'drafty feeling'.

Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
12/15/2017
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 months ago
Kcrand36
Kcrand36, HVAC Mechanic
Category: HVAC
Satisfied Customers: 80
Experience: Owner at Advantage Repair
Verified

Hello, I am Kevin, one of the Tech's here on JA. Are you available to chat?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Hi Kevin,
Yes I'm available but in and out today (Saturday). A little more current info to add - last night the unit ran all night, but held temp at a steady 67 F. This morning I went outside to see what was going on with the outside unit. It was about 49F outside at the time, the compressor was running, the fan was not running, and the smaller of the two copper pipes running from the unit was hot. Unit smelled hot/overheated, so I shut it off completely. The outside unit appears to be pretty old - it's a Goodman model CPKE24-1B, S/N(###) ###-#### So before this morning, I actually thought it was running all right, just all the time with a noisy fan blower, but now I'm not so sure. Thanks, *****
btw we live in a 'tri-level' condo in Nashville, TN - the system in question heats/cools the lower level, basically two normal sized rooms and a smaller bathroom. There is a separate heat pump system which does the middle and upper levels and is running perfectly.
Customer reply replied 2 months ago
Hi Kevin, Today is Sunday December 17, and I thought I would circle back with you. Yesterday my wife and I decided we had to take action because subject system was totally not working properly. We called Lee Company here in Nashville and received outstanding service. System is now up and running perfectly. Turns out the bot***** *****ne seemed to be 3 things 1) old thermostat seemed to have been wired improperly, so when I installed the new one, it was wired wrong also, 2) the outside fan motor is marginal and needs replacement, and 3) the whole system is old (1975! inside and 1995 outside) and so we're going to look at proposals to replace the whole thing in the future. Meanwhile it's working now and so the case is closed in regard to this inquiry. Thank You.
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Carrier furnace. Igniter comes on, but no flame. There was
Carrier furnace. Igniter comes on, but no flame. There was an electrical issue earlier today on the electric company's side of the meter. It has been repaired. Furnace was OK prior to that. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace rated at 1865 cfm was recently installed in
carrier furnace rated at 1865 cfm was recently installed in Jan 2018. Total cfm for all vents is 1056 cfm. heat distrbution for 16 vents ranges from 69 to 95 cfm. what could be the problem? Please adv… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier model 58mec100 and the heater will not
I have a carrier model 58mec100 and the heater will not cycle back on and the light will blink 1 then 6 green on the control board. I can switch the power off for a minute then it tries again and come… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace model 58CTA090-12114 that was
I have a Carrier furnace model 58CTA090-12114 that was installed in 2005,I am currently having an issue with it when it is called upon for heat, it will start the burner sequence with the ignitor glow… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The ignitor to my Carrier furnace will not trigger so no
Hi Pearl. The ignitor to my Carrier furnace will not trigger so no heat can enter the house. I've manually reset the limit switch and cleaned the flame sensor and was looking for suggestions on what t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a carrier infinity model 58CVA090 that seems to be
hi! i have a carrier infinity model 58CVA090 that seems to be only blowing cold air, wondering if pilot light out since i just changed filters and my thermostat reset how can i tell if my pilot light … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
I have a thermostat that says it is Carrier on the front and
I have a thermostat that says it is Carrier on the front and has Class 2 30V Max, LR1620 marked on the back. I want to move to a Wi-fi thermostat? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm trying to find a blower motor for a carrier 58wav045.
I'm trying to find a blower motor for a carrier 58wav045 … read more
MattR757
MattR757
HVAC Contractor / Owner
Associate Degree
14 satisfied customers
Non working furnace issue - Carrier Weathermaker 8000. The
Non working furnace issue - Carrier Weathermaker 8000. The ignition module was changed a couple of years ago. There's a clicking sound but not burning. Ideas? Cost?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Our carrier infinity says "system malfunction". The fan is
our carrier infinity says "system malfunction". The fan is working but it is not cool. I went to the attic and changed the filter but code is still there. What does this mean? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Phil, we have a Carrier Infinity Weathermaer natgas
Phil, we have a Carrier Infinity Weathermaer natgas furnacethis week the limit switch had to reset at lest 4 ties. We replaced the limit switch,ever since then the furnace runs but the top of the plen… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Need an interconnect schematic for my carrier furnance. Need
Need an interconnect schematic for my carrier furnance … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Have a Carrier Weather Maker 8000 ts and the light on the
Have a Carrier Weather Maker 8000 ts and the light on the front panel is blinking … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Carrier Infinity System Thermostat Model #
We have a Carrier Infinity System Thermostat Model # SYSTXCCUIZ01-A and the plastic "heat" and "zone" buttons are broken. We are looking for a new unit with this model number to replace our current un… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Im changing my thermostat from a carrier to honeywell
Im changing my thermostat from a carrier to honeywell rth6580wf. The orange wire, not sure where to connect it on the honeywell … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Airheatman, Trying to source a control board for a Carrier
Hi airheatman, Trying to source a control board for a Carrier forced air furnace that a technician said was no longer available. The number is ***** obscured, looks like 3057?5 702 working with a 3012… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have Carrier fan coil unit model FV4CNB003. Have Carrier Fan
Have Carrier Fan Coil unit # FV4CNB003. Seemed to run and change speed during operation. Is this normal? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.