I hope so since...

I hope so since it's 12F out there. I have a York 90% hi-Eff Furnace with Modulating Gas valve and main blower. It is leaking water during heating cycle. I have replaced the clear collector box with the new solid black one because it was cracked and leaking. Now i getting a small puddle of water coming out the front of the unit. NOT the collector box all surfaces under the the burner section are dry. Checking i see it leaking from the bottom of the blower housing?? Have you see this before? is it the secondary heat-X issue?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes and YES the unit is heating fine no problem house is very comfortable. it the water that im worried about..

Contractor's Assistant: Do you plan on doing the work yourself?

I'm a retired HVAC tech .. YES

Contractor's Assistant: Anything else we should know to help you best?

I just am not familiar with this type of furnace internal flow and I have checked with local supplier and there are no recalls for the secondary Heat-X like there was on the collector box. The unit is 4 years old

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
12/15/2017
HVAC Technician: airheatman, HVAC Technician replied 7 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,188
Experience: Furnace, A/C and heat pump specialist.
Verified

1. What is the model on the furnace?

2.Can you attach pics showing where it is leaking using add file button?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

Can't tell much from pic. Is this water underneath and side entrance return?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
SEE attached.. water falling into blower housing and coming out bottom then rolling towards the back
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

Take a look at that pic and tell me if it looks good and matches your installation

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The middle unit condensate out the right side
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

OK, that should all be ok then.Do you know if unit was properly sized?Does it seem to run long enough. The only two things I can think of is the unit is oversized or the heat exchanger is the problem.I have actually seen it almost "rain" inside the vent pipe when oversized.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Here is my thoughts....there was a 100,000 before I replaced it with an 80,000... For water to collect in the bottom of the housing it must happen after the heating cycle if finished. main ECM motor running at reduced speed Just looking to see if with all your exposer have you heard of the secondary cracking on a unit this young... was not there first few years just started this year. Small amount of water as you see never get much bigger.
Thanks
Ed
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

ED I think I would have that heat exchanger checked.I am not aware of any recalls or widespread issue with the 90plus Yorks, but that is not to say there can't be a few out there,especially with the inferior materials we are getting imported.

There defintely should not be any water near that ecm motor at anytime.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,188
9,188 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Rheem (Ruud) gh Eff. Furnace with a Code # 58, no
I have a Rheem (Ruud) High Eff. Furnace with a Code # ***** no water present in system. How do I get rid of the fault and get the unit running again? Will jumping the sensor out restart the unit. Resi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
; I have a Carrier model 58MVB120-20 gas furnace set up
Hi; I have a Carrier model 58MVB120-20 gas furnace set up for propane. It was built in 2006. It has required little service since it was installed. In the past couple of years I was noticing some stai… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 2001 Amana 90 Air Command gas furnace that has a moisture
I have a 2001 Amana 90 Air Command gas furnace that has a moisture problem and will not run. They thought it was the ignition control unit, as the unit tries to start, then stops. But there is visible… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a XL 90 and I noticed the condensate drain on the furnace
I have a XL 90 and I noticed the condensate drain on the furnace isn't draining into the trap. when I opened the door to the compartment where the condensate hoses are I found water puddling up inside… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hi Rick, I have a 23 year old 90% efficiency Carrier 58SXA.
Hi Rick, I have a 23 year old 90% efficiency Carrier 58SXA. All of my drain hoses are well clamped & go into a condensation pump. Upon a recent inspection I found water located in the area below the h… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have two York Diamond 90 furnaces (P2URD16N07501A). On the
I have two York Diamond 90 furnaces (P2URD16N07501A). On the same weekend, as temperatures dropped into the 20s, I had the blades on one vent motor break apart, ruining the motor, and the vent motor o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Armstrong Ultra SX 90 High efficiency gas furnace with Ametek
Armstrong Ultra SX 90 High efficiency gas furnace with Ametek Circulating Pump, Model No.(NNN) NNN-NNNN2. The Ametek Pump is collecting water, please advise. Thanks, Stanley… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a rheem Rudd weather king that started dripping water
I have a rheem Rudd weather king that started dripping water on to the tray under the induced draft blower. I removed the entire idb and sealed it with a new tube of premium waterproof silocone. clean… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a 85% high efficiancy Amana approximately 10 years old.
I have a 85% high efficiancy Amana approximately 10 years old. I discovered a water puddle under it several days ago. It is not the condensate pump or lines. It is leaking condensate from behind the b… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Temp Star high eff. 97. I have been having problems
I have a Temp Star high eff. 97. I have been having problems with moisture getting into the blower assy and causing the furnace to shout down with a code 3. Any time the door is put back on and it cyc… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Furnace leaking when on. Broken fitting with loose drain hose.
I have a Carrier 58SX100-JG-1 furnace that is leaking water when it is on...There is a rectangular black pan just under the small blower motor. The fitting was leaking, but I broke it off getting the … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a bryant furnace model 350MAV. Last year I noticed
I have a bryant furnace model 350MAV. Last year I noticed a puddle of water at the base of the unit. I just took of the bottom panel and i noticed rust. It looks like the water was dripping down just … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Water is leaking from the bottom of my Lennox Elite Series
Water is leaking from the bottom of my Lennox Elite Series furnace.... about 8 years old. What's going on? Bill… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Trane XR90, and I live in Minnesota. During heating
I have a Trane XR90, and I live in Minnesota. During heating season, the furance box leaks water (it runs down the right hand side somewhere and puddles such that their is a very light stream (not con… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Carrier Weathermaker 9200. I have been told by 2 different
I have a Carrier Weathermaker 9200. I have been told by 2 different technicians that there is a problem with the secondary heat xchanger on these. And that there might be a program that Carrier will f… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
I have a Rheem RGLD 06EC ER that is not coming on. It sounds
I have a Rheem RGLD 06EC ER that is not coming on. It sounds like when the tstat is actuated the igniter module is trying because I hear a click but the hot surface doesnt come on???… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman-Janitrol GMPN-080 Furnace on natural gas.
I have a Goodman-Janitrol GMPN-080 Furnace on natural gas. No water drains from the Flue collector box. Water is leaking into the cabinet area and building up on the cabinet floor under the blower ass… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a York stellar plus P2ud16p upflow gas furnace, installed
I have a York stellar plus P2ud16p upflow gas furnace, installed fall 1993. The plastic cover of the secondary heart exchanger has hairline cracks near the bold holes The gas company will not repair t… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.