Customer Question
Hello How are you...

Hello How are you? goodman gmh81405dncd Is my model number

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

I am not getting the maximum airflow to my ducts. My house is not getting very warm

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I would like to make sure my wires are connected to the right blower speeds

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
12/15/2017
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

CHECK TO SEE IF FURNACE IS SET TO 1ST STAGE HEATING OR TWO STAGE HEATING

Dip switchs are on the control board bottom part of furnace.

Set to 2 stage, read explanation ;

The normal operational sequence in sequence is as follows:

R and W thermostat contacts close, initiating a call for heat.

Integrated control module performs safety circuit checks.

Induced draft blower is energized for 15 second prepurge

period causing pressure switch contacts to close.

Igniter warm up begins after 15 second prepurge expires.

Low and high-stage gas valves open at end of igniter warm

up period, delivering gas to burners and establishing flame.

High-stage gas valve closes after five seconds; low-stage

gas valve remains open.

Integrated control module monitors flame presence. Gas

valve will remain open only if flame is detected.

Circulator blower is energized on low heat speed following

a fixed thirty second blower on delay. Electronic air cleaner

terminals are energized with circulator blower.

Furnace is now operating in low-stage heating mode.

Furnace operates; integrated control module monitors

safety circuits continuously.

If low-stage delay period expires, control will shift operation

from low-stage heating mode operation to high-stage

heating mode operation. Control will energize circulator

blower high heat speed and high stage gas valve

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago
Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago
I noticed question is still opened, please dont forget to rate the 5 star rating if we are done. Sincerely
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
937 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a G26 series furnace. We are not getting enough air
I have a G26 series furnace. We are not getting enough air to the living space. The G26 has a variable speed blower adjusted through speed taps on the motor harness connector. Installation instruction… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I recently replaced my HVAC with a new 2ton unit including
I recently replaced my HVAC with a new 2ton unit including furnace/air handler. The fan speed had to be turned down (1/2) due to the existing duct system. The ducts are all flexible, and I plan on mov… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I installed a Goodman GPD14 and am not getting any heat in
I installed a Goodman GPD14 and am not getting any heat in fossil fuel although the burners are firing.… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a MBR1200 aa1 electric furnace. I want to keep the blower
I have a MBR1200 aa1 electric furnace. I want to keep the blower on at all times. I was able to do that with my oil furnace. The problem is that the blower makes too much noise. I can't keep it on at … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
We have a Ducane SVS 1 propane fired furnace. It comes on but
We have a Ducane SVS 1 propane fired furnace. It comes on but doesn't get beyond just warm. The fan is terrific with all kinds of cool air blowing about. The dealer has said it is the high efficiency … read more
jhvac
jhvac
2 satisfied customers
blower motor makes a strange sound like it is not holding speed.
blower motor makes a strange sound like it is not holding speed. revving sound repeats at 1 to 2 seconds… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Hello, I have a Goodman Furnace Model GMS80703ANBA. It currently
Hello, I have a Goodman Furnace Model GMS80703ANBA. It currently has 1/3 H.P. motor. This model furnace has a 14" Cabinet. I would like to install a 1/2 h.p. motor. I called Goodman, who referred me t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am looking for fan speed setting recommendations for my goodman
I am looking for fan speed setting recommendations for my goodman MVC950905DX. The installers that put the system in have no clue...UGH… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Has anyone experienced a furnace that starts moving a lot more
Has anyone experienced a furnace that starts moving a lot more air than it has in the past. the duct work actually creaks as the return air ducts seem to want to collapse although they have new filter… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
We are experiencing some problems with our furnace...It is
We are experiencing some problems with our furnace...It is only a year or 2 old...gas furnace. Lately when we turn up the temp on the thermostat the furnace stays on for about 5 minutes then shuts off… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a pre-existing 4 ton Carrier single stage model 38 CKC
I have a pre-existing 4 ton Carrier single stage model 38 CKC 10 Seer Air conditioning unit that was installed about 10 years ago. I recently had a Carrier Infinity Modulating Gas Furnace (Model 58MVC… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a 90plus Reehm furnace with a 3 ton AC unit installed
I have a 90plus Reehm furnace with a 3 ton AC unit installed in March 2011. Fan motor has made a humming sound when first trying to start up ever since I have owned. Installer has experimented continu… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My Trane 80 system (gas) is running full blast but only putting
My Trane 80 system (gas) is running full blast but only putting out lukewarm air. What do I need to look at to generate more heat coming from the vents?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I was in the middle of asking a question when my internet went
I was in the middle of asking a question when my internet went out. I'll repost my question. I have a Rheem Corsaire series furnace, 100,000 btu. Whenever I want to increase the temperature in the hou… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
how do i get a goodman central ac unit model #a36-00 to run
how do i get a goodman central ac unit model #a36-00 to run the blower unit at a higher rate of speed, i feel as if the is not running that strong is there anything i can do??? please help… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
The blower on my Monessen direct vent gas fireplace hardly
The blower on my Monessen direct vent gas fireplace hardly moves any air at all. Turning the rheostat increases sound, but I pretty much have to wet my finger to feel any airflow. Is this normal opera… read more
G Wurtz
G Wurtz
Instructor of HVACR Program
Master's Degree
57 satisfied customers
We had a Goodman 1.5 ton system installed today it replaced
We had a Goodman 1.5 ton system installed today it replaced a 16 year old Goodman system. everything including copper lines was replaced. the return air is much noisier. the old grille is a 10x30 do w… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My Goodman GMNTE120-5 has been shutting off after 2 minutes
My Goodman GMNTE120-5 has been shutting off after 2 minutes of the natural gas burner coming on. The main limit operates and opens the circuit shutting down the burners. The duct blower fan kicks into… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x