Customer Question
I have just purchased...

I have just purchased and installed a RTH360 series Thermostat. Our situation is such that we have to have our coils repaired and the freon reloaded so we are using emergency b/U heat (electric coils).

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

When I wired the thermostat I did so as directed by the installation manual wit h the System Setup Number 221 at 1. Upon restating the furnace the thermostat quickly responded and heat came on. Our problem is that the thermostat is not responding, I have the temp set to 72f, and the heater continues to run with a current temp of 75f. I have deenergized the furnace until such time that I can resolve the problem.

Contractor's Assistant: Do you plan on doing the work yourself?

No I have a contractor affecting the repairs. This is to get us thru until next week. My wife and I are aged and cold affects us terriby.

Contractor's Assistant: Anything else we should know to help you best?

I can provide all the System Setup Options chosen.m Woulld that help?

Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/14/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,885
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago

Are you sure the thermostat is causing the issue? What wiring do you have to the thermostat and to what terminals, colors and terminal list please.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
I wired in as follows:Y to Y, G to G, I have no C so C is wired to O(range), W to W and R to R.
Customer reply replied 9 months ago
Original wiring was W to Aux/E, G to G, O to O to O/B, Y to Y and R to R. The old thermostat was a Honeywell , but unable to ID model.
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago

Ok if you remove the W wire from the thermostat does it still heat?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
NewThermostat was wired as shown on page 13 of the installation manual; Wiring-heat pump, not Alternate Wiring.
Customer reply replied 9 months ago
You still there?
Customer reply replied 9 months ago
With the White wire disconnected at the thermostat and pwr resotored, the fan is NOT running.
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago

Ok if you are not running the heat pump at all set the unit up for regular air furnace operation and connect the W to the W and it should turn off at the set point. In heat pump mode it likely will not.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Change wiring to "conventional systems" as shown on page 12?
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago

Yes

Ask Your Own HVAC Question
Customer reply replied 9 months ago
OK , hang tight while I shift wiring.
Customer reply replied 9 months ago
No good boss, this is the same configuration I started with. All wires match except Orange is connected to C.
Customer reply replied 9 months ago
The face plate is showing the unit in Emergency Heat, is this correct?
Customer reply replied 9 months ago
The temp has now dropped to 72F which is what I hasd it set o, however the fan is still running.
Customer reply replied 9 months ago
OK, now I have had the thermostat set at 70 and the heater is running with temp rising to 73.
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago

You can not have it set to a heat pump setting if the display still shows emergency heat you have it in a heat pump mode

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Should I manually shift it to Heat as opposed to Emer Heat?
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago

Yes so no WIRE to the O/B only White to W and put it to HEAT

Ask Your Own HVAC Question
Customer reply replied 9 months ago
I have no wire in O/B. It is wired per the instruction maual represents with the exception I hvce my orange wire connected to terminal "C".
Customer reply replied 9 months ago
Should I connect my Orange wire to terminal O/B?
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago

You need your C terminal connected to power the themostat, but nothing in the O/B terminal

Ask Your Own HVAC Question
Customer reply replied 9 months ago
OK, so the question still stands: Where do I connect my Orange wire?
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago

Orange should only be to O/B... you should have never connected it to C or it could be the reason you are having this issue.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
OK, so how do I go about clearing it back to factory settings and starting all over again?
Customer reply replied 9 months ago
First you have repatedly instructed me that nothing is to be connected to O/B, and then you tell me to cnnect my Orange to O/B and nothing to C. However earlier you instructed me that I must have a connection to C or the thermostat will not work, So what and where?
Customer reply replied 9 months ago
Additionally you now tell me I should never have any connection to terminal C, whats up. Im at a loss for what goes where?
HVAC Technician: HVAC Guru, HVAC TECH replied 9 months ago

Your new thermostat will require a C wire to work, let me see if another tech can help you out, stand by please.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
What is the function of the C wire?
Customer reply replied 9 months ago
By the way, while I am waiting I checked my balance on my checking account, and low and behold there is a charge of $27 to "just answer *EX. What this all about?
Customer reply replied 9 months ago
I have not in any fit, form or function agreed to a "call me" situation. What gives?
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,885
18,885 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am looking for a little help installing my new Honeywell
I am looking for a little help installing my new Honeywell thermostat for my Heat Pump Day & Night AC system. Is someone there?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Five year old AC/Furnace (gas) in Austin, Tx. First year our
Five year old AC/Furnace (gas) in Austin, Tx. First year our tenant has problem. Says the temp at vents is 60 F but room temp is 80 F. With paper strip can see air movement. Tenant put thermostat to O… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have dc90 furnace when it gets to the temp say 68 it shuts
I have dc90 furnace when it gets to the temp say 68 it shuts off then when the temp goes to 67 ican hear a small fan come on but the frunance does't come on… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a honeywell nonprogramable thermostat installed with
I have a honeywell nonprogramable thermostat installed with my new hot water boiler keeps clicking on asking for heat then clicks off before radiators could possibly raise temp bought house thermomete… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Help! My Brant 95% furnace won't shut off. My contractor
Help! My Brant 95% furnace won't shut off. My contractor left two hrs ago after reinstalling the thermostat after our remodel. He is out of cell coverage and I can't get it to shut off. I have tried: … read more
HVAC Guru
HVAC Guru
HVAC TECH
18,885 satisfied customers
An r-22 unit gh side normal, low side normal, superheat of
an r-22 unit high side normal, low side normal, superheat of 34 sub cooling of 15 flow check piston what can it be?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Goodman CPLE30-1C heat pump with a Janitrol HPT 18-60
I have a Goodman CPLE30-1C heat pump with a Janitrol HPT 18-60 thermostat. I bought a new Honeywell TH5220D thermostat but am a little confused about where the wires go on it. Before I try the Honeywe… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have an Amana dual furnace (electric primary and propane
I have an Amana dual furnace (electric primary and propane gas for auxiliary). Our propane tank gauge is broken and tank is empty. The problem is with the current dropping temperatures the unit reache… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Brian, We have a Lennox Model CR33-48C-F. The A coil is freezing
Brian, We have a Lennox Model CR33-48C-F. The A coil is freezing up despite only having the thermostat at 70 degrees. The outside temp in the high 70s. What should my first steps be to help with this … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
we have a bryant furnace and air conditioner at our house.
we have a bryant furnace and air conditioner at our house. the heat works but the air conditioner doesn't. No air comes out at all when the thermostat is set on cool. Also, the unit outside doesn't tu… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
MY HONEYWELL FOCUS PRO TH5000 THERMOSTAT IS SHOWING THE HEAT
MY HONEYWELL FOCUS PRO TH5000 THERMOSTAT IS SHOWING THE HEAT AT 9 DEGREES HIGHER THAN THE DEGREES I HAVE SET FOR COOL. I NEED HELP AS I THINK IT IS NOT WORKING WELL.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I installed a Goodman heat pump in January. My heat bills have
I installed a Goodman heat pump in January. My heat bills have been unusually high every month since (over 200.00/month). After checking I noticed that my heat strips are coming on every time the unit… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a new Lennox Gas furnace (LP) and Heat Pump that seem
I have a new Lennox Gas furnace (LP) and Heat Pump that seem to work fine, but when it gets below the set point on the HP (20 Deg.) it shuts off but the furnace (emergency heat) doesn't come on. I've … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My coil is clean and the filter is changed. My air flow is
My coil is clean and the filter is changed. My air flow is at 45 degree, and 18 degrees on the suction line 2 foot from the A coil, at the unit outside the liquid line is at 92 degrees. My PSI are 145… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman heat pump/propane furnace heating system,
I have a Goodman heat pump/propane furnace heating system, with a TSTATG3273 controller. The heat pump is model GSH140601 and the furnace is a GME81155CX.The controller is new this winter because the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a RTH 7600d honeywell thermostat. just found out that
i have a RTH 7600d honeywell thermostat. just found out that compressor is shot for our furnace. they did a bypass to keep the heat going till they can order a new one. of course heat will not come on… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a TH8320 thermostat with a gas furnace and heat pump.
I have a TH8320 thermostat with a gas furnace and heat pump. Our electric bill was over $350 a month using the heat pump. I have had a tech look at it an nothing found. When running the heat pump the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I purchased with installation system FV4BNB00600 with condenser
I purchased with installation: system FV4BNB00600 with condenser 25HCB360A003. Upon install completion, the condenser has a constant buzz when the system is off. I was informed that the buzz was commi… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x