Customer Question
I have just purchased...

I have just purchased and installed a RTH360 series Thermostat. Our situation is such that we have to have our coils repaired and the freon reloaded so we are using emergency b/U heat (electric coils).

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

When I wired the thermostat I did so as directed by the installation manual wit h the System Setup Number 221 at 1. Upon restating the furnace the thermostat quickly responded and heat came on. Our problem is that the thermostat is not responding, I have the temp set to 72f, and the heater continues to run with a current temp of 75f. I have deenergized the furnace until such time that I can resolve the problem.

Contractor's Assistant: Do you plan on doing the work yourself?

No I have a contractor affecting the repairs. This is to get us thru until next week. My wife and I are aged and cold affects us terriby.

Contractor's Assistant: Anything else we should know to help you best?

I can provide all the System Setup Options chosen.m Woulld that help?

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/14/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,330
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Are you sure the thermostat is causing the issue? What wiring do you have to the thermostat and to what terminals, colors and terminal list please.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I wired in as follows:Y to Y, G to G, I have no C so C is wired to O(range), W to W and R to R.
Customer reply replied 4 months ago
Original wiring was W to Aux/E, G to G, O to O to O/B, Y to Y and R to R. The old thermostat was a Honeywell , but unable to ID model.
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Ok if you remove the W wire from the thermostat does it still heat?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
NewThermostat was wired as shown on page 13 of the installation manual; Wiring-heat pump, not Alternate Wiring.
Customer reply replied 4 months ago
You still there?
Customer reply replied 4 months ago
With the White wire disconnected at the thermostat and pwr resotored, the fan is NOT running.
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Ok if you are not running the heat pump at all set the unit up for regular air furnace operation and connect the W to the W and it should turn off at the set point. In heat pump mode it likely will not.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Change wiring to "conventional systems" as shown on page 12?
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Yes

Ask Your Own HVAC Question
Customer reply replied 4 months ago
OK , hang tight while I shift wiring.
Customer reply replied 4 months ago
No good boss, this is the same configuration I started with. All wires match except Orange is connected to C.
Customer reply replied 4 months ago
The face plate is showing the unit in Emergency Heat, is this correct?
Customer reply replied 4 months ago
The temp has now dropped to 72F which is what I hasd it set o, however the fan is still running.
Customer reply replied 4 months ago
OK, now I have had the thermostat set at 70 and the heater is running with temp rising to 73.
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

You can not have it set to a heat pump setting if the display still shows emergency heat you have it in a heat pump mode

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Should I manually shift it to Heat as opposed to Emer Heat?
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Yes so no WIRE to the O/B only White to W and put it to HEAT

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I have no wire in O/B. It is wired per the instruction maual represents with the exception I hvce my orange wire connected to terminal "C".
Customer reply replied 4 months ago
Should I connect my Orange wire to terminal O/B?
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

You need your C terminal connected to power the themostat, but nothing in the O/B terminal

Ask Your Own HVAC Question
Customer reply replied 4 months ago
OK, so the question still stands: Where do I connect my Orange wire?
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Orange should only be to O/B... you should have never connected it to C or it could be the reason you are having this issue.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
OK, so how do I go about clearing it back to factory settings and starting all over again?
Customer reply replied 4 months ago
First you have repatedly instructed me that nothing is to be connected to O/B, and then you tell me to cnnect my Orange to O/B and nothing to C. However earlier you instructed me that I must have a connection to C or the thermostat will not work, So what and where?
Customer reply replied 4 months ago
Additionally you now tell me I should never have any connection to terminal C, whats up. Im at a loss for what goes where?
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Your new thermostat will require a C wire to work, let me see if another tech can help you out, stand by please.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
What is the function of the C wire?
Customer reply replied 4 months ago
By the way, while I am waiting I checked my balance on my checking account, and low and behold there is a charge of $27 to "just answer *EX. What this all about?
Customer reply replied 4 months ago
I have not in any fit, form or function agreed to a "call me" situation. What gives?
Was this answer helpful?
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,330
18,330 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Rheem model 13Ajn24A01 outside condenser. Last
I have a Rheem model 13Ajn24A01 outside condenser. Last night I noticed the thermostat room temperate was 74 and the thermostat was set on Cool 72. I removed filter on inside furnace unit and saw fros… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm wandering about some way to prevent the air condition
I'm wandering about some way to prevent the air condition from running water inside the room while turning it on for the first time in summer season. Because last year there was complete mess with a lot of water run just into the room which was caused by a spider which desided to make a nest in some of the pipes. Is it possible to avoid my last summer's situation for sure without calling a HVAC engineeer to check all pipes or whatever that calls? … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,210 satisfied customers
I have a question on a Munchkin boiler. A few weeks, I get
a few weeks, I get either an f05 or f06 fault code … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a jennair jfi2089aep12 I was fine this morning. I cam
i have a jennair jfi2089aep12 I was fine this morning. I cam home and the control board in front is blank and I don't hear the rerrigerator running … read more
Webb-Guy
Webb-Guy
Maitenance Supervisor
Associate Degree
2,804 satisfied customers
I have a Bathroom exhaust fan upstairs that vents out to the
I have a Bathroom exhaust fan upstairs that vents out to the roof and every couple months it stops working. Can anybody help me with this?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
The hood fan is in auto mode and I can't turn it off! Just
The hood fan is in auto mode and I can't turn it off! … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
Pl have Lennox hs25-311. Have Lennox hs25-311. Need to know
Have Lennox hs25-311. Need to know where the two blue wires from the hi pressure switch aware connected. One goes to the right side of contactor switch. Where does the other connect. Time delay? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Cm907 honeywell heater thermostat wall unit. The
Hi, I have a Cm907 honeywell heater thermostat wall unit. The LCD display is scrambled, even after resetting the unit and replacing the batteries. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
My Armstrong Furnance shut down last Dec. the service man
My Armstrong Furnance shut down last Dec. the service man came and after a long serch told me all was now well within an hour I had to call back he then said I should turn off the humidfier it ran ok … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
Why does my unit hiss? I've cleaned the blades and it's even
Why does my unit hiss? I've cleaned the blades and it's even louder now … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
I have a 2 year old Trane AC which has just started to leak
I have a 2 year old Trane AC which has just started to leak water from the coils into the air box below. The unit is on the second floor. When the unit was replaced they opted to remove the filter on … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My water heater is not heating. It is an AO Model GPVH. The
My water heater is not heating. It is an AO Smith Model GPVH. The Intelli-Vent controller shows a green light next to Warm (far left) and yellow light on C (far right). … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My furnace stopped blowing warm air in the middle of the
my furnace stopped blowing warm air in the middle of the night. When we got up to try and figure out what was going on we noticed it would start and then stop and then start and then stop again. We le… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
We are trying to heat our spa and the message SW OPEN keeps
We are trying to heat our spa and the message SW OPEN keeps coming up. what does this mean? … read more
David Bowden
David Bowden
Owner
768 satisfied customers
I have a older thermostat & I need to know to set the
I have a older thermostat & I need to know hoe to set the controls. … read more
HVAC Guru
HVAC Guru
HVAC TECH
18,330 satisfied customers
I have a A A unit M/N A93UH1D707B12A-03 She will start the
I have a A A unit M/N A93UH1D707B12A-03 She will start the combustion air providing motor and sometimes the igniter will glow and sometmes not. If it ignites which it is not at all now It give's the t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a York diamond 90 furnace. Recently I had to replace
I have a York diamond 90 furnace. Recently I had to replace the draft inducer. The original had two hoses going to it. One at the top which goes to the pressure switch and the other came from the neck… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Thank you. My ac blower doesn't stop this is been going on
my ac blower doesn't stop this is been going on for a week … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x