I have a Gibson furnace model kg7sa090c-24b and the code on circuit board keeps flashing pressure switch pressure switch circuit board and inducer assembly are new have any ideas?

Contractor's Assistant: Did you check the furnace's filters?

Yes

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Furnace Is only six years old it runs sometimes for a day then goes out

Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 minutes by:
12/14/2017
HVAC Technician: Rick, HVAC Supervisor replied 2 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,345
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Given all you've replaced the only things left are a problem with the exhaust vent or possibly the switch vac tube connection at the draft assembly port is blocked

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Actually removed flue pipe chimney and pipe are clear and I ran wire through port on inducer
HVAC Technician: Rick, HVAC Supervisor replied 2 months ago

Since this is an 80+ not a 90+ unit condensate back up wouldn't be an issue. I got nothing else.

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
HvacmanSean
HvacmanSean, HVAC Technician
Category: HVAC
Satisfied Customers: 237
Experience: Owner HVAC company
Verified
Good morning. Are you still needing assistance. I can see if i can help
Ask Your Own HVAC Question
Customer reply replied 2 months ago
I still need help
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
Alright. Lets start from beginning it will be easier and make sure i dont miss.anything.What Was orginal issue and what did you do.Ill spend some time with you regarding this. Please be patient wkth me at times as i am still active in the field so there may be a slight delay.
Ask Your Own HVAC Question
Customer reply replied 2 months ago
Original issue was code on board showing pressure switch. Changed switch worked for awhile. Draft inducer was really noisy changed that then was told circuit board might have short so changed that. Checked voltage at pressure switch I have 25 volts at switch then when draft inducer starts voltage drops out but code on board still flashes pressure switch
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
If your voltage is dropping at pressure swith then thats fine.Ok next step what diagnostic led are you going off. The new control board or old from control board before. They often change
Ask Your Own HVAC Question
Customer reply replied 2 months ago
New control board
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
Does it immediately say pressure switch or does it Run normally until it faults out ?
Ask Your Own HVAC Question
Customer reply replied 2 months ago
Sometimes immeadiatly sometimes works for awhile before dropping out
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
Have you went across pressure switch and see it drop out or only going by control board ?
Ask Your Own HVAC Question
Customer reply replied 2 months ago
My checking has been at pressure switch
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
you have seen it go from 0 to 25 volts at pressure switch ? While it ead running
Ask Your Own HVAC Question
Customer reply replied 2 months ago
No I have voltage at pressure switch,when inducer starts and pressure switch opens voltage drops out like it’s supposed to but circuit board flashes pressure switch problem
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
2 pressures switches on this model ?
Ask Your Own HVAC Question
Customer reply replied 2 months ago
No just one
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
Can you attach a picture of wiring diagram so i can see it
Ask Your Own HVAC Question
Customer reply replied 2 months ago
May not be able to get it till tomorrow
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
Ok.
Ask Your Own HVAC Question
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
Havent heard back on this?
Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a gibson furnace and the ignitor wont turn on. I
I have a gibson furnace and the ignitor wont turn on. I checked the resistance and it was 89. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Gibson furnace, was working wekk until one day the
I have a Gibson furnace, was working wekk until one day the thermostat started making some clicking sounds prior to start the heating cycle, I changed the batteries then the little fan motor would not… read more
Rick
Rick
HVAC Supervisor
23,345 satisfied customers
Have a gibson furnace that wont ignite. The fan runs but the
Have a gibson furnace that wont ignite. The fan runs but the igniters wont even get hot. There is a consistant green led that flashes … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
May name is victor, I have a Gibson furnace and want out. I
Hi may name is ***** ***** have a Gibson furnace and want out. I check to se if I can get it to go and I replace the ignator because the existing will not get red hot. now I replace the pressure switc… read more
Rick
Rick
HVAC Supervisor
23,345 satisfied customers
I have a Gibson furnace model kg7sa090c-24b and the code on
I have a Gibson furnace model kg7sa090c-24b and the code on circuit board keeps flashing pressure switch pressure switch circuit board and inducer assembly are new have any ideas? … read more
HvacmanSean
HvacmanSean
HVAC Technician
237 satisfied customers
I have a Gibson furnace which has both blowers running with
I have a Gibson furnace which has both blowers running with no heat. Error code "Limit Circuit open or external load on W. I have read a previous similar question, but the model is not the same, and t… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My Gibson furnace stopped working. Could you advise how I
My Gibson furnace stopped working. Could you advise how I can turn it back on? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Gibson Furnace A/C. How do I clean the A/C drain? New
Gibson Furnace A/C. How do I clean the A/C drain? JA: Did you check the furnace's filters? Customer: New filter JA: Do you plan on doing the work yourself? Customer: yes. odor coming out of the floor … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a 12 year old gibson furnace. The first two burners
I have a 12 year old gibson furnace. The first two burners ignite, but the flame doesn't make it to the third (out of 7). Then it shuts down. If I blow on it lightly, I can get it to catch. It only st… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a code 1 hour lockout, how can i fix this code, One
Hello, i have a code 1 hour lockout, how can i fix this code … read more
Rick
Rick
HVAC Supervisor
23,345 satisfied customers
Gibson furnace model kg7sa. Is there a control for the speed
Gibson furnace model kg7sa. Is there a control for the speed of the blower fan? With heat selected it operates at a very high speed as if air conditioning is selected. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a Gibson furnace in my home that is about 6 years
I have a Gibson furnace in my home that is about 6 years old. I had a problem last year that required a furnace repair guy twice....having the same problem this year 4 times so far this last week. The… read more
Rick
Rick
HVAC Supervisor
23,345 satisfied customers
I have a problem with my Gibson furnace. They are fine. the
i can give you the model # and which limit switch is tripping… read more
Rick
Rick
HVAC Supervisor
23,345 satisfied customers
Wondering about how a pilot light on a Gibson GC3BA-030C-A
Wondering about how a pilot light on a Gibson GC3BA-030C-A gas furnace … read more
Rick
Rick
HVAC Supervisor
23,345 satisfied customers
I came home today and the display for my air conditioning
I came home today and the display for my air conditioning unit was bland. It was also not on. I put batteries in the display and got numbers but still don't seem to be getting a response from the unit… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Gibson furnace 904727K with central AC. Connecting General
Gibson furnace 904727K with central AC. Connecting General 1040 power humidifier. HUM terminal at bottom of board looks like 120v. Top of board, screw terminals:y2-open ,y1-open, G-green to thermostat… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
A hot air Gibson furnace that was install last year is now
A hot air Gibson furnace that was install last year is now tripping roll-out switches. Is the gas pressure to high?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Gibson furnace. I am not sure which model (found
I have a Gibson furnace. I am not sure which model (found many numbers, not sure which is the model number). The problem I am having is that the rollout switch located on the inducer blower keeps trip… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x