I have an ruud rgrl-07emaes. And the status light on the…

Customer Question
I have an ruud...

I have an ruud rgrl-07emaes

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

And the status light on the board is steady on

Contractor's Assistant: Do you plan on doing the work yourself?

Ugh

Contractor's Assistant: Anything else we should know to help you best?

It doesn't work

Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
12/14/2017
HVAC Technician: airheatman, HVAC Technician replied 9 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,542
Experience: Furnace, A/C and heat pump specialist.
Verified

Look on control board and let me know if there is a green light that flashes when furnace fails.Does anything at all come on?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
There are three lights. Left is off, middle steady lit, and right steady lit
HVAC Technician: airheatman, HVAC Technician replied 9 months ago

Lets do this. Jump the R and W terminals on control board and see if it will light and work.https://i.imgur.com/JprQdYv.png

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Hello?
HVAC Technician: airheatman, HVAC Technician replied 9 months ago

Lets do this. Jump the R and W terminals on control board and see if it will light and work.https://i.imgur.com/JprQdYv.png

Ask Your Own HVAC Question
Customer reply replied 9 months ago
No idea what that means.. I see r and w and they have wires there in those slots
HVAC Technician: airheatman, HVAC Technician replied 9 months ago

Yes.JUmp the R and W together using a jumper or an opened paper clip.Wires can stay attached.I sent a pic

Ask Your Own HVAC Question
Customer reply replied 9 months ago
take a paper clip and just touch the screws that hold the wires?
HVAC Technician: airheatman, HVAC Technician replied 9 months ago

Correct.Connect R to W and see if heater will work

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Will this further damage anything?
HVAC Technician: airheatman, HVAC Technician replied 9 months ago

No . I would not tell you to do if if so

Ask Your Own HVAC Question
Customer reply replied 9 months ago
it starts small fan temporarily
Customer reply replied 9 months ago
Turns back off though
HVAC Technician: airheatman, HVAC Technician replied 9 months ago

Leave it jumped ,Do not remove the jumper and see if burners and blower come on

Ask Your Own HVAC Question
Customer reply replied 9 months ago
everything came on but then shut off when I let go again
HVAC Technician: airheatman, HVAC Technician replied 9 months ago

OK now what we did is bypass the thermostat.That tells us issue is with thermostat or wiring between thermostat and furnace, not the furnace

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 9 months ago

Look inside thermostat and give me model.If it has batteries replace them

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Classic 90plus with comfort control, mod #rcfl-hm2417ac,,,
Classic 90plus with comfort control, mod #rcfl-hm2417ac,,, when power turned on it purges and can barley hear the ignitor click... no fire??? … read more
airheatman
airheatman
HVAC Technician
9,542 satisfied customers
I have a rudd achiever 90 with no heat. Blower Fan works (in
I have a rudd achiever 90 with no heat. Blower Fan works (in fan mode) but exhaust fan never comes on and I never hear igniter … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Rheem 90 plus furnace installed 1995 model rgra-07emaes
rheem 90 plus furnace installed 1995 model rgra-07emaes purge fan comes on then cycles off, occasionally the igniter will heat and lite but will not burn for a full cycle.… read more
airheatman
airheatman
HVAC Technician
9,542 satisfied customers
honeywell sv9520h8034, status light is steady green, no
honeywell sv9520h8034, status light is steady green, no heartbeat. The Furnace is an armstrong ultra V 80. Its got a honeywell SV9520 smartvalve with a ST9160 fan board. There was a bad relay on the f… read more
Expert
Expert
Ruud achiever 90 plus comes on then flame goes out after afew
Ruud achiever 90 plus comes on then flame goes out after afew seconds , flame light never comes on , has new board… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hi -- my 95% efficiency (not sure what model, but thats a
Hi -- my 95% efficiency (not sure what model, but that's a good clue as to what line) Rheem furnace does not ignite this morning. Two solid green status lights. Blower works when switched to continuou… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Ive got a Ruud Silhouette II that wont ignite. Ive noticed
I've got a Ruud Silhouette II that won't ignite. I've noticed my Inducer motor isn't running but it feels very hot. Blower is blowing. T-stat seems to be working. Just won't ignite. Power and Status L… read more
V12Tech
V12Tech
252 satisfied customers
I have a gibson model kg6rl 080c-168 my status light is a solid
I have a gibson model kg6rl 080c-168 my status light is a solid red instead of green what does that mean… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Where can I buy ONLINE part for Integrated Furnace Control
Where can I buy ONLINE part for Integrated Furnace Control Board (IFC) for RHEEM Furnace model: RGRL-07EMAES. Looks like existing one has a part # XXXXX… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
ruud ugta-07emaes does not ignite blower and draft fan start
ruud ugta-07emaes does not ignite blower and draft fan start runs constantly but does not light ifc board displays three flashes every 2 seconds or so could this be the pressure switch ?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
i need help my Ruud heater/ac will come on and pilot will light
i need help my Ruud heater/ac will come on and pilot will light and then shut off it will try several times and then stop i for what ever reason it came to me took some steel wool and cleaned the pilo… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Payne PG9MAB furnace. I smell an electrical burning
I have a Payne PG9MAB furnace. I smell an 'electrical burning' smell which prompted me to check the furnace. I removed the front panel and see the red LED status light is solid red - should it be soli… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Heil N9MP2 90+ single state. Heat does not come on. The Honeywell
Heil N9MP2 90+ single state. Heat does not come on. The Honeywell SV9541M "Smart Valve" gives no trouble codes. The LED status light is on, no flashing . It does not blink (no Heartbeat?) I measured 2… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We are planning on installing a new 60,000 BTU furnace and
We are planning on installing a new 60,000 BTU furnace and would like to know the quality, reliability and /or any problems associated with the (a) Luxaire TG9S060B12MP11 high efficiency furnace with … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Ruud gas furnace, model UGPH07EAUER, it has an intermitttent
I have a Ruud gas furnace, model UGPH07EAUER, it has an intermitttent problem, where on start up the burners ignite, then go off after 10 or 15 seconds. Sometimes turning the power off, then back on h… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a RUUD Super Quiet 80 Two-Stage. Presently operating
Have a RUUD Super Quiet 80 Two-Stage. Presently operating on heat cycle. When looking through blower compartment window, I see the 4 LED's lit up in this order from left to right: yellow/steady - gree… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
i have a goodman gas heater and it is short cycling i replaced
i have a goodman gas heater and it is short cycling i replaced the flame sensor and it is still doing ti i bypassed all safteys and still the same it has a circuit board that will tell in a series of … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
fan cycles on/off every 5-10 minutes but the thermostat is
fan cycles on/off every 5-10 minutes but the thermostat is off (a/c compressor doesn't cycle, just the fan)… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x