I am getting error codes 35 and 223. Thoughts?

Customer Question
Hi Tim, I am getting error...
Hi Tim,
I am getting error codes 35 and 223. Thoughts?
Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
12/13/2017
HVAC Technician: airheatman, HVAC Technician replied 4 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,977
Experience: Furnace, A/C and heat pump specialist.
Verified

What is the model on the furnace and thermostat?And is error on thermostat or furnace board?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I will have that information to you shortly. The error is on the thermostat. This is been happening since we moved this furnace from the garage to the basement.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Take your time

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Since error is on thermostat give me that model too

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Can you pull front off wall and look inside for label with model

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I can in the morning
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

We will go from there

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Can’t get the front off
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

See any series number or name anywhere?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
No
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Sort of tough troubleshooting without knowing the system components.Let me see what I can find

Ask Your Own HVAC Question
Customer reply replied 4 months ago
That’s it
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

OK issue will be one of the following

1.Bad pressure switch

2.Water backed up in hoses in furnace

3.Issue with draft motor not pulling enough vacuum to close switch

4.Obstructed intake or exhaust vent.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I emptied out water that was in the draft motor
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

THere should not have been any in there. That indicates either there is a drain blockage downstream or issue with the secondary heat exchanger

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Where is the secondary heat exchanger?
Customer reply replied 4 months ago
Well I added a condensation pump. That helped but still getting water in exhaust blower.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Any kinks or restrictions in any of the rubber hoses inside furnace? Also if you can, we might try disconnecting the trapp and making a new trap using tubing to see if maybe the reservoir is clogged letting it back up

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My unit seems to be short cycling, and the temperature
My unit seems to be short cycling, and the temperature sensor on the unit in the attic has a high temperature light on. … read more
airheatman
airheatman
HVAC Technician
8,977 satisfied customers
How to clean heat exchanger coils, filters have been clean
filters have been clean recently and I am getting an airflow alarm on the thermostat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,702 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
airheatman
airheatman
HVAC Technician
8,977 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
278 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
airheatman
airheatman
HVAC Technician
8,977 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Funky smell coming from heat exchanger outside...... repair
funky smell coming from heat exchanger outside...... repair guy said the gas not m ixing with the air properly..true? said probably just clogged … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Heat exchanger is a month old and heat stopped working.
Heat exchanger is a month old and heat stopped working. Three lights are blinking saying it is a limit or rollout switch … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,702 satisfied customers
I have a property with a Keeprite heat exchanger installed.
I have a property with a Keeprite heat exchanger installed. I believe the filter is clogged but I don't know where it's located. The model is PGF018K040E … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,702 satisfied customers
How can I clean the inside of the heat exchanger on my
how can I clean the inside of the heat exchanger on my furnace? … read more
airheatman
airheatman
HVAC Technician
8,977 satisfied customers
My carrier heating heat exchanger is plugged. I understand
My carrier heating heat exchanger is plugged. I understand it is civered under a recall action. if bI purchase a new systeem 59mn7a080-20 what price drduction do I receive? … read more
airheatman
airheatman
HVAC Technician
8,977 satisfied customers
How much time should be allowed to change a heat exchanger
How much time should be allowed to change a heat exchanger for a 48tjf016 series 580ba and 2 men?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,702 satisfied customers
I was looking into a trane tud060 heat exchanger and noticed
I was looking into a trane tud060 heat exchanger and noticed a buildup of white powder at one of the factory seams and need to know what is causing this. I attached a pic. Thanks… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x