After having a Nest 'installed' I am not getting any power from the boiler. The Nest 'pro' indicated it might be a fuse. It is a Burnham kv-73 boiler

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

A couple weeks

Contractor's Assistant: Do you plan on doing the work yourself?

If I can yes

Contractor's Assistant: Anything else we should know to help you best?

I just installed a new carlin primary control unit but still no luck with the power from the boiler

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

The thermostat was working for about an hour, I turned it off, left and when trying to turn it back on there was no power... the old thermostat does not work either now. I think the filters are food

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
12/13/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,713
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Where did you connect the C wire to?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
No C wire on the thermostat. Only R bad W1
Customer reply replied 7 months ago
the W1 wire
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

The Nest can not function without a C wire or it will always need to be recharged. If you interlock the R and W wires at the thermostat does it come on?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Interlock how? I am not following. The Nest was running when first installed, it was turned off. When I tried to turn back on it indicated no power. When I tried to install the old thermostat it indicated no power either. Seems like no power is coming from the boiler
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

There is no power to the thermostats the way you have it wired...The Nest needs a C wire or will need to be recharged. Your old one would be a battery powered unit. If you just interlock the wire ends so they are connected does the unit come on.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
touch the r and w wire and see if the boiler/ heat kicks on?
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Yes correct!

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Trying now
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

ok thanks!

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Nothing from the boiler when the two wires have been connected
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

OK go to the boiler and can you get to the board or do you have a beckett burner with red button?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I have a burnham. The primary control has a red reset button but there does not appear to be power going to the control
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Can you check for power to the control with a volt meter there is not fuse on the control. You can try to hard reset the control by pressing the red button in for 30-40 secs. If nothing happens check for power to the control you may have lost it.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I don't have a bolt meter but I am certain there is no power coming to the control.... the control is new too so I am guessing the lack of power is comin from the high voltage(110?) box above it. Would there be a fuse there?
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

There could be a fuse or did you check the breaker to the unit? This is a power issue to it it seems for sure.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Definitely a power issue. The breaker looks good... but how would I check for sure? When I looks in the high voltage box I don't see a fuse but I might just me missing it... I am not sure
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

There should not be one there unless it was added. Check for incoming power on the BLACK and WHITE wires to the unit for 120 volts.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Is there a way to check without a volt meter?
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Not really you would need one to confirm power

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,713
18,713 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Just changed Honeywell thermostat to nest brand. It would
Just changed Honeywell thermostat to nest brand. It would not come on I reworked the Honeywell from the photo i took to be sure wiring right and now the heat, emerge heat or a won't come on neither wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Not enough heat from Burnham Boiler to keep house warm in
Not enough heat from Burnham Boiler to keep house warm in these cold conditions. Boiler water is cycling between 160F and 200F as seen on the temperature gauge. Can the temperatures be raised to provi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My furnace reaches 70 and shuts off the thermostat is set at
My furnace reaches 70 and shuts off the thermostat is set at 73 can shut power on thermostat off and will usually start do I need a new thermostat. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My boiler is not firing. Has power. Circulating pump is
My boiler is not firing. Has power. Circulating pump is working but seems no power to burner controls … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Hvac is not working per the setting. But when it is
My Hvac is not working per the setting. But when it is working it heating the house properly. Why doesn't it heat per the setting in thermostat?Earlier I worked with JustAnswer and after analysis I wa… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Carrier unit with a Nest Thermostat which has been
I have a Carrier unit with a Nest Thermostat which has been working fine for a year. I had the Nest set on Heat/Cool to maintain the house between 70 and 73. Last night, since it has been warm outside… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My breaker was tripped to my rooftop unit. Now it won't come
My breaker was tripped to my rooftop unit. Now it won't come back on. Can I temporarily shut off the main power switch to my building, then turn it back on? Would that reset the breaker so I can then … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Honeywell digital electronic thermostat. Recently
I have a Honeywell digital electronic thermostat. Recently I ad the relay on my oil heater replaced by my heating contractor. Ever since that time my bottom level thermostat is not functioning correct… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Anyone there? I have a newer Weil McClain gv90+ nat has boiler
Anyone there? I have a newer Weil McClain gv90+ nat has boiler and with no other problems ever it just stopped working this morning. The indicator lights that are light are POWER and TSTAT CIRC. Help… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have 2 Burnham Alpine 80s. Installed new, a month ago. Oil-to-gas conversion. Had noi
I have 2 Burnham Alpine 80s. Installed new, a month ago. Oil-to-gas conversion. Had noise issues and both boilers required "tuning" - adjusting CO2 levels and other settings. Now my boiler is quiet an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Problem with new hydro air system. Burnham Alpine condensing
Problem with new hydro air system. Burnham Alpine condensing boiler with 2 First Aire air handlers and indirect HW tank.I thought this was related to Nest tstat update yesterday but now unsure. Taco i… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a oil fired steam boiler 250k btu can I convert to gas
I have a oil fired steam boiler 250k btu can I convert to gas and power vent out the side of the building ?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a basic Burnham hot water heating system and domestic
I have a basic Burnham hot water heating system and domestic hot water supplied by a burnham propane fired boiler and controlled by a basic Burnham 2 wire thermostat. Will the 2nd generation nest ther… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We leave in a 2 apt brownstone (5 stories) in nyc. 1/3 of the
We leave in a 2 apt brownstone (5 stories) in nyc. 1/3 of the building is heated by radiator (water), the other 2/3 is radient heat. Our boiler just died and we are evaluating diff proposals. One reco… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
We have a six year old Burnham V8 series (del KV 86) oil burner.
We have a six year old Burnham V8 series (del KV 86) oil burner. can it be converted to gas? and, how do we go about it?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Burnham V904A Oil Fired Boiler. Is there a gas conversion
I have a Burnham V904A Oil Fired Boiler. Is there a gas conversion kit available and wiil it be efficient if I convert it. The boilers is approx. 6 years old Thanks… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I HAVE AN OLD BUNHAM V3-228 BOILER IN MY HOME. I WISH TO INSTALL
I HAVE AN OLD BUNHAM V3-228 BOILER IN MY HOME. I WISH TO INSTALL A CARLIN 101 CRD BURNER. ARE THEY COMPATIBLE? NOZZLE TO BE USED IS 1.65 GPH. THANKS FOR YOUR ATTENTION.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We haave just purchased a Burnham # XXXXX with Carlin burner
We haave just purchased a Burnham # XXXXX with Carlin burner iin December 2008. It keeps shutting off and we have no heat. Our repair man keeps coming here and he is at a lost as to the problem. We ha… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x