HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

I have a chronotherm III and I turned off the heat and put…

Customer Question
I have a chronotherm...

I have a chronotherm III and I turned off the heat and put the fan on manual. When I returned the setting to heat/ auto the heat came on for about 2 minutes and then displayed hold ac. After a little while the heat will come back on and stop and display hold ac,over and over.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I didn't check the filter

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

The furnace is a Lennox forced hot air

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
12/13/2017
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,799
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far it sounds like a bad printed circuit board, 90% chance that is that is the case.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally.. and with over 8,000 questions answered here since 2009, with a 98.5% satisfaction rating.

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

That said, I cannot guarantee that you will not do something unsafe, or cause damages. You take that risk.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

.

Tell me a lot about your technical background and instruments on hand so that I can coach you most effectively. We can go from here as you keep asking follow up questions without any limits …

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I am a millwright so I have an extensive mechanical and electrical background. Hvac is my only shortcoming
Customer reply replied 8 months ago
No phones
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago

Phone calls are entirely optional.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed , after you rate this answer.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,799
9,799 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,799 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a honeywell chronotherm iii, since yesterday was on
since yesterday was on vacation and came back and found heater is not working … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,799 satisfied customers
I have a Honeywell Chronotherm III. I tried to put the heat
I have a Honeywell Chronotherm III. I tried to put the heat on multiple tomes using the hold temp button and it is not kicking in. The display says Hold-AC. Any suggestions?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
- I have a Honeywell Chronotherm III thermostat. If I turn
Hi - I have a Honeywell Chronotherm III thermostat. If I turn the unit from Off to Heat, the heat comes on for a minute or two then goes off. Adjusting the heat up on the display doesn't make the heat… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Lennox central AC and heat. Everything was working
I have a Lennox central AC and heat. Everything was working fine a couple of days ago until we switch gas providers. So when the gas was cut back on I noticed on the Honeywell thermostat it said " Hol… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Honeywell Chronotherm III unit shows 9642 and 189459D inside. We
Honeywell Chronotherm III unit shows 9642 and 189459D inside. We had a normal yearly service and now it keeps resetting the unit internally to cool when it is set on heat for the bottom setting and th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a honeywell chronotherm iii that is heat only. I juist
I have a honeywell chronotherm iii that is heat only. I juist bought a chronotherm iii from ebay that has heat/cool. Can I just plug it into thte base that I have and will it work for my heat?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need to replace a Chronotherm III thermostat. I believe it
I need to replace a Chronotherm III thermostat. I believe it is model T8611R1000. I have forced air heat, central a/c, and a heat pump. The stat has 4 settings: Em. Heat, Heat, Off, Cool And a switch … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox Furnace controlled by a Chronotherm III thermostat
I have a Lennox Furnace controlled by a Chronotherm III thermostat which has been working perfectly - until this morning. I push "Hold Temp" then increase the temperature setting a few degrees and pus… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My honeywell chronotherm III seems not to be working correctly.
My honeywell chronotherm III seems not to be working correctly. I don't think the fan is coming on at all in the AUTO setting. I can turn it on so it runs all the time, but if it is not in that positi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
from the chronotherm thermostat III when it is set to auto,
from the chronotherm thermostat III when it is set to auto, the heat comes on but the blower does not. The thermostat will then click and the display will flash with a "AC" in the right corner. If I p… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
how do i get it to clear the program or break the sleep
how do i get it to "clear" the program or break the "sleep" mode? It's an old chronotherm III. The thermostat won't talk to the heating unit and i brought the spare down from upstairs and it wont talk… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Hello, my honeywell chronotherm III is displaying -AC where
Hello, my honeywell chronotherm III is displaying "-AC" where the temperature is usually displayed. I have the heat setting on, and the heat is not turning on. Any ideas what '-AC' means?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
For the chronotherm lll during the heat cycle the system
For the chronotherm lll during the heat cycle the system light shuts off and -AC is displayed instead of the temperature. The furnace combustion fan shuts off but the blower continues to run. It resta… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Honeywell Chronotherm III energy saver thermostat
I have a Honeywell Chronotherm III energy saver thermostat that is displaying "Hold - AC". It has been set to "Hold - 69°" on Heat setting when it switched over to the current mode and shut off the he… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Re our Chronotherm III thermostat, the screen began flashing
Re our Chronotherm III thermostat, the screen began flashing "repl batteries", so I did with three triple A's, and put the unit back on the base on the wall. Now the words on the screen are very clear… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier weathermaker sx gas furnance that has been
I have a carrier weathermaker sx gas furnance that has been regularly maintained and is in good working order. Problem: I turned the heat on for the first time a couple of days ago. The fan and heat c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Chronotherm III controller started displaying the time and
My Chronotherm III controller started displaying the time and -AC and the Rheem Furnace/AirCond Fan wouldn't shutoff. Removing the Chronotherm face and replacing the batteries and it still shows -AC, … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Chromotherm III - After the heat has been on and it
I have a Chromotherm III - After the heat has been on and it is up to temperature, the "Heat On" display goes off, but the burner keeps running. However, if I manually shut the heat off, the oil burne… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.