I have a weil Mclaine ultra gas boiler in warm weather

Customer Question
Hi. I have a...

Hi. I have a weil Mclaine ultra gas boiler in warm weather shutdown mode. How do I get the heat turned back on?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Thermostats are calling for heat, filters are clean

Contractor's Assistant: Do you plan on doing the work yourself?

Maybe

Contractor's Assistant: Anything else we should know to help you best?

How to get it back into heat mode. I also tried cycling the power. did not change anything

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 11 minutes by:
12/12/2017
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,398
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

If your unit is in WWSD now as cold as it is then the sensor has probably failed. You can get it back up and running by disconnecting the outdoor sensor from the ODS terminals. Those terminals are on the low voltage terminals strip the same strip the thermostat is connected to.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Weil Mclain Ultra Gas Fired Boiler. It is fired
I have a Weil Mclain Ultra Gas Fired Boiler. It is fired with propane. I have had it about 15 years. It quits at least once a week. I hit restart and it will fire back up. The system has been very unr… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
We lost power last night, but it has been restored, yet our
We lost power last night, but it has been restored, yet our Weil-McLain furnace has not come back on. The maintenance screen color is gray & does not change to any other color by pressing select & say… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I have a ultra 155 weil mclain boiler, the background screen
I have a ultra 155 weil mclain boiler, the background screen stays gray all the time, never changes to a blue screen. is it in a lockout mode boiler is running fine please help brian … read more
hvacdave84
hvacdave84
53 satisfied customers
I have Ultra model 230 and cannot get boiler to fire due to
I have Ultra model 230 and cannot get boiler to fire due to "Warm Weather Shut Down." It is colder inside than outside after several days of cooler weather. This is first start up of this season. … read more
hvacdave84
hvacdave84
53 satisfied customers
I have a Weil mclain boiler, and a nest thermostat. the
I have a Weil mclain boiler, and a nest thermostat. … read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I have a Weil-McLain EG-40 natural gas steam boiler. It
I have a Weil-McLain EG-40 natural gas steam boiler. It worked fine all winter. When the heating season was over, I shut off the power switch on the side of the boiler, but left the pilot lit. I turne… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Is there a shutdown procidure for 30.0 btu natural gas
is there a shutdown procidure for 30.0 btu natural gas weil-mclain boiler to replace a in-line service ball valve … read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Our unit thermostat is set at 74 degrees but the temp on the
our unit thermostat is set at 74 degrees but the temp on the thermostat shows 66 degrees. There is little or no heat emitting from the exhaust vent. We live in Big Timber Montana. … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have a Weil MClain Ultra 155 gas boiler that is in Warm Weather
I have a Weil MClain Ultra 155 gas boiler that is in Warm Weather Shutdown mode . We have no domestic hot water. I would like to know how to set the U-control menu items so that I can get hot water. I… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Weil_Mclain Ultra 105 - Goes from mode 3 at about 116 degrees
Weil_Mclain Ultra 105 - Goes from mode 3 at about 116 degrees to mode 1 then 6. I checked the maximum temperature and it is set at 190 degrees and I disconnected outside sensor just in case it was mal… read more
V12Tech
V12Tech
252 satisfied customers
Weil McLain Ultra gas fired boiler heat wont turn on
I have a Weil McLain Ultra gas fired boiler. I have hot water but the heat will not turn on and the display screen reads "warm weather shutdown" I have never touched the system since it was installed.… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I have a two year old weil mclain ultra series 3 boiler which
I have a two year old weil mclain ultra series 3 boiler which is given me the ignition fault message.… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Need assistance reseting Weil McLain Ultra O-4 boiler. Had
Need assistance reseting Weil McLain Ultra O-4 boiler. Had run out of oil and now have refilled oil tank, however, boiler will not run. It is blinking in the 'recycle' mode. I hit the reset switch, bu… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I had a new Armstrong pump installed to my hot water furnace.
I had a new Armstrong pump installed to my hot water furnace. When I tried to turn the heat on, the button lights for maybe 3 seconds and the system never turn on. NO HEAT. I do have a message to chan… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I programmed my weil mclain boiler but it stays in standby
I programmed my weil mclain boiler but it stays in standby mode. How do I correct that to accept the priority 3 settings… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have no heat. I have a weil mclain gas boiler with a taco
I have no heat. I have a weil mclain gas boiler with a taco 506 six zone relay. My indirect water heater is on priority zone whicch is working. My other thermostats wont call for heat. If i turn up th… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a weil mclain boiler furnace we started to update the
I have a weil mclain boiler furnace we started to update the house and want to change the thermostats well we did but both weve tried are not working i called weil mclain and they have told me i need … read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
We have a Weil Mclain ultra gas fired water boiler that supplies
We have a Weil Mclain ultra gas fired water boiler that supplies our in floor heat and hot water. Recently it has started sending heat to the floor even when it is not called for basically all of the … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x