Customer Question
Bryant heater mod #398baz03680...

Bryant heater mod #398baz03680, error code 12, blower calibration lockout, replaced blower motor, still get error 12

Contractor's Assistant: How old is the appliance? Have you gotten error messages before?

20 + years old, had same problem 10 years ago,replaced blower motor and solved problem

Contractor's Assistant: Do you plan on doing the work yourself?

I just replaced the blower motor myself again.

Contractor's Assistant: Anything else we should know to help you best?

Does this new motor need to be programed

Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 hours by:
12/12/2017
HVAC Technician: airheatman, HVAC Technician replied 9 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,542
Experience: Furnace, A/C and heat pump specialist.
Verified

Does the error 12 remain more than 1 and a half minute?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
That is another question, do not plan on using you again, have a known qualified tech coming to my home, this was a waste of money.
HVAC Technician: airheatman, HVAC Technician replied 9 months ago

Troubleshooting these motors requires a special tool as they are high voltage powered but low voltage controlled. Under normal circumstances the blower will run for 1.5 minutes and give a 12 error for the first 1.5 minutes after power is applied to furnace.

The bell control does indeed have to be programmed to work properly with the control board,

If the motor was purchased as direct replacement it should be programmed already.

If you are having the same issue with new motor as with old, the issue is most likely the control board rather than the motor.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Just replaced my fan blower motor on my ruud furnace and it
hi , just replaced my fan blower motor on my ruud furnace and it spoils up and right back down with a error code 68 - no blower communications any ideas, steve … read more
airheatman
airheatman
HVAC Technician
9,542 satisfied customers
I have a Furnance and am getting error code 33. The filter
I have a Bryant Furnance and am getting error code 33. The filter is clean, The limit switch is new, the capacitor on the blower is new and the blower is only a year old. I even swept the blower compa… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My carrier furnace model: 59MN7A080v17--14, when call, the
My carrier furnace model: 59MN7A080v17--14, when call for heat, the blower motor runs 10 second and shut down automatically, and the furnace shut down. Flash code shows 42. The flash code list only ha… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
, I have a Carrier Comfort 92 furnace and use it to heat
Hello, I have a Carrier Comfort 92 furnace and use it to heat a hot yoga studio to 112 degrees for several classes throughout the day. The heater was installed about 7 years ago and it has begun to ha… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I just had a company out to "tune-up" my Bryant Plus 80 heat
I just had a company out to "tune-up" my Bryant Plus 80 heater and he said the unit is 16 years old and the blower motor bearings are going. Could stop at any time. Repair cost would be 1200.00. But d… read more
type2technician
type2technician
253 satisfied customers
Have a Carrier Infinity Furnace 58CVA110 that is cycling
Have a Carrier Infinity Furnace 58CVA110 that is doing something strange. The t-stat is set for "heat" mode and is set for a few degrees above where the temp is now (it's a Totalline P374-1100FM t-sta… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 14 year old Bryant Plus 90i 355MAV that had blower
I have a 14 year old Bryant Plus 90i 355MAV that had blower issues the day after a neighborhood power outage. I took the 1 HP blower motor (HD52AE120) apart and found a capacitor fried to the thermist… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Please help. Frigidaire Furnace FG6RA072C-12A, serial #FGA010204217.
Please help. Frigidaire Furnace FG6RA072C-12A, serial #FGA010204217. Installed in new home 12 years ago. November 2003 = bearings on inducer motor whining; need to replace motor cycled on/off December… read more
airheatman
airheatman
HVAC Technician
9,542 satisfied customers
I have a Bryant 90 plus furnace that is 5-6 years old. Yesterday
I have a Bryant 90 plus furnace that is 5-6 years old. Yesterday when I pushed the button on the thermostat for the air conditioner, it went dark after a few seconds. I found the furnace was flashing … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a BRYANT 383K Heater/Furnace in my townhouse. It is
I have a BRYANT 383K Heater/Furnace in my townhouse. It is about 6 years old. I have had nothing but trouble with it since I moved in . Every year there has been $500.00+ in repairs Virtually everythi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Ducane Gas heater - about 10 Years old. The model
I have a Ducane Gas heater - about 10 Years old. The model number is XXXXX We used programmable Thermostat (Honeywell). Currently, the heater is signal error code as follow : 4 flash stop for 2 second… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
A year ago we moved from an all electric home to this one that
A year ago we moved from an all electric home to this one that has a Rheem PowerVent 2. 50 gal natural gas water heater that was manufactured 10/2004. Since the water heater was in the house when the … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a 88,000 btu Bryant furnance Model number 395CAV042091AEJA
I have a 88,000 btu Bryant furnance Model number 395CAV042091AEJA Series E Serial # XXXXX I keep showing a flashing code 13 but then later it will go to 33. I have checked and replaced my filters and … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
An eighty-two year old neighbor just had her 10 year old Bryant
An eighty-two year old neighbor just had her 10 year old Bryant FWA furnace stop working. The technician said it needs a circuit board, blower, motor, thermostat and "capit" whatever that means. He sa… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have Bryant Model 355MAV060100ADKA furnace. I am getting
I have Bryant Model 355MAV060100ADKA furnace. I am getting the error code of 4 Amber LED flashes followed by 4 Green LED flashes. I cleaned the filter & cannot get the error code to clear.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Bryant 383kav error code 31. I have ran into this problem
Bryant 383kav error code 31. I have ran into this problem a couple of years ago. The technician had me do a "reset". I am out of town, trying to walk my wife through this. Any help...… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Bryant Plus 90i furnace with an Evolution thermostat
I have a Bryant Plus 90i furnace with an Evolution thermostat and Honeywell HE260 bypass humidifier installed. Event though I have the humidity set to the max in the t-stat, I am only geting to 23% hu… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
carrier mvp 080 14 series 140 blower did not work replaced
carrier mvp 080 14 series 140 blower did not work replaced curcuit board and blower motor module blower now works but led code flashs 12 "blower calibration lockout"… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x