I have a standing pilot unit heater (75000 btu) I replaced…

I have a standing...

I have a standing pilot unit heater (75000 btu)

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

I replaced the pilot/thermocouple assembly this year. the unit lights just fine, but once it goes through a cycle and the main gas valve shuts off, the pilot also goes out.

Contractor's Assistant: Do you plan on doing the work yourself?

If i can, I did install this unit, and i also replaced the main valve a few years ago.

Contractor's Assistant: Anything else we should know to help you best?

Nothing that i can think of

Show More
Show Less
Ask Your Own HVAC Question
Answered in 15 minutes by:
12/12/2017
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified

Hi I am Gaztech1, a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

Are you ready?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Yep
Customer reply replied 8 months ago
I just paid $36, I do not want to pay another $24
What should I check first? The thermostat is working, there are no filters

dont need phone option

2 things you can try

  1. adjust pilot flame biger with pilot adjust scew on gas valve
Ask Your Own HVAC Question
Customer reply replied 8 months ago
I only got your first suggestion, the second was blocked by the window to opt for the chat
What is your second suggestion?

2. adjust air ventury air inlet less open and try and pilot assembly and burner a little further apart so that when burner flame goes out it will not suck pilot out

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Thank you
I will try those things

2. adjust air ventury air inlet less open and try seperating pilot assembly and burner a little further apart so that when burner flame goes out it will not suck pilot out

Ask Your Own HVAC Question

Cheers!

Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified
Gaztech and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
937 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an older Reznor unit heater that has not been used
I have an older Reznor unit heater that has not been used for a few years due to main line gas pipe failure. Finally got around to replacing the gas line and have confirmed gas to main valve. but cann… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Older Modine pa 150 unit heater used in a greenhouse.
Hi. Older Modine pa 150 unit heater used in a greenhouse. Standing pilot that keeps going out when main burner goes off. I replaced the valve a year ago and pilot burner a few days ago. Why is this ha… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My 9mpd Tempstar furnace quit doing anything a month ago when water got into the smart val
My 9mpd Tempstar furnace quit doing anything a month ago when water got into the smart valve form a roof leak. I replaced the valve and it works ok most times except every other day or so it goes thro… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have threebrick propane heater, pilot light wont stay lit,
I have threebrick propane heater, pilot light wont stay lit, sometimes wii stay lit for a little while, and light goes out and heater shuts down. Then hard to relit pilot light.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 5 mantel heater. When burning on 3 or 5 mantels; it
I have a 5 mantel heater. When burning on 3 or 5 mantels; it will burn a few minutes then shut off. When I shut off910 mantel and leave pilot on : it goes out in a few minutes. Burning (1) mantel work… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
we had a laars mini therm boiler installed about a year ago,
we had a laars mini therm boiler installed about a year ago, it was working fine, its a standing pilot natural gas boiler, hot water base board heat, yesterday the unit stopped working, pilot went out… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
In my farm house I have a 30,000 BTU Dyno-glo gas heater. the
In my farm house I have a 30,000 BTU Dyno-glo gas heater. the pilot light constantly keeps going out. it will shut down even when it is kicked in to provide heat. what can be shutting this down?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Hi I have a old Bryant gas hot air heater model 75-318 serial
Hi I have a old Bryant gas hot air heater model 75-318 serial C-EF-31707 BTU 75000. Here is my ? When I turn my thermostat on for heat it will not fire up the heater at all and its a new one/wire up r… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
On my Empire direct vent, 20,000 btu propane gas heater with
On my Empire direct vent, 20,000 btu propane gas heater with Piexo igniter, when the thermostat calls for heat to open the main valve, the valve opens for a few seconds, up to as much as a minute., an… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Have a Lochinvar water heater that will not keep the pilot
Have a Lochinvar water heater that will not keep the pilot burning after it goes thru the heating cycle. I have changed the thermocouple twice. It works for a short time and then it is back to the sam… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Carrier Furnace. Model 58CS075-2 SN 201BB 1983
I have a Carrier Furnace. Model: 58CS075-2 SN: 201BB 1983 75,000 BTU/Hr There is another number on the nameplate also #58SE900141. The pilot light will light, then the main flame will come on. After a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a natural draft home heater rated at 92,000 Btu/hr.
I have a natural draft home heater rated at 92,000 Btu/hr. input. It has a standing pilot with a 24 volt GC solenoid and gas regulator which I want to replace and update. The unit is thermostat operat… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
I have a Coleman direct vent standing pilot furnace model #
I have a Coleman direct vent standing pilot furnace model # XXXXX (mobile home unit). The pilot will stay lit as long as I am holding the button to SET but as soon as I release it to PILOT the flame g… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
iam working on a bradford whitewater heater gas fired standing
iam working on a bradford whitewater heater= gas fired standing pilotm#m-1-40t-5lx-8 manuf 1995. pilot light does not stay lite changed the thermocouple. heater will cycle once then on the 2nd cycle w… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have a Janitrol furnace. It goes through spells where the
We have a Janitrol furnace. It goes through spells where the pilot light will not stay lit. We replaced the thermocouple about a month ago and it worked fine for awhile but now it is acting up again.… read more
BARRY
BARRY
owner
Associate Degree
56 satisfied customers
I have a space heater (Perfection schank) that will not heat.
I have a space heater (Perfection schwank) appox (1994) that will not heat. Pilot light is on, when I turn the control knob for more heat the main burner does not come on. The valve is set to the on p… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a rheem furnish and when thermastat cuts main valve
I have a rheem furnish and when thermastat cuts main valve off it cuts gas off to pilot light… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i am trying to repair a Rheem 21R30T gas water heater in my
i am trying to repair a Rheem 21R30T gas water heater in my grand daughter's mobile home. The pilot will not stay lit. I have replaced the thermocouple with no change in results. Now and then the pilo… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x