Well, I’ve been reading to find answers in the previous

Customer Question
Well, I’ve been reading...

Well, I’ve been reading to find answers in the previous texts, but since your little face popped up below, I thought maybe I should try directly. I have a Rheem Criterion II Gas Upflow furnace that when heat is called for by the thermostat it goes through the process; exhaust fan then igniter then fan, but no flame.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Thermostat is on auto and heat and I cleaned the filter

Contractor's Assistant: Do you plan on doing the work yourself?

Would like to yes

Contractor's Assistant: Anything else we should know to help you best?

Hmm, guess that about covers it

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/11/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,693
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

This is likely a thermal rollout issue. There are high limit safety thermostats that are around the burner housing area that can trip open if they fail or the unit is overheating. Some of these have reset buttons on them that you can manually press down to reset while others do not. The ones that do not either are one time limits or are limits that are suppose to manually reset when cooled down. Now that does not always happen when they go bad so you will have to check them for continuity with an ohm meter across the two leads going to them. If you do not pwn a ohm meter you can physically bypass each rollout to make sure it is good by connecting the two wires to each rollout sensor together to see if the unit will then operate. Now once you have found the bad one you can change it out or reset it and then you should check your furnace filter for blockages and make sure you main furnace blower is running to speed. These two things can cause a unit to overheat and trip one of these rollout sensors. Mosts units have 3 of these devices and here is a link to what they can look like on your unit.

CLICK HERE

CLICK HERE

CLICK HERE

All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Customer reply replied 7 months ago
All three rollout sensors test as having continuity. Don’t see a reset button on them though. What’s next step?
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

See if you are getting 24 volts after the ignitor is glowing to the gas valve.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
OK, which leads do I test on the gas valve? there are three leads to it one green one blue and one yellow.
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

blue to yellow

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Don’t seem to get any voltage across the blue and yellow wires when the igniter is sparking. What’s the next step?
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Can you upload a pic of your wiring diagram on the unit?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,693
18,693 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I hace a Rheem Criterion RGDG-10EBRJR and the Induced Draft
I hace a Rheem Criterion RGDG-10EBRJR and the Induced Draft Blower goes on only when the main limit switch is disconnected (therefore open). … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem Criterion Model #RGDG100AUER furnace that the
I have a Rheem Criterion Model #RGDG100AUER furnace that the exhaust blower motor constantly running with no heat.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rheem Criterion II...No heat. The small fan/blower does not
Rheem Criterion II...No heat. The small fan/blower does not come on when there is a call to heat, so nothing else happens either, no igniter, nothing. But, the A/C works fine, so I know know the large… read more
type2technician
type2technician
253 satisfied customers
I have Rheem Criterion II furnace. installed in 2000 natural
I have Rheem Criterion II furnace. installed in 2000 natural gas, downflow unit. The fan runs continously whenever the power is on to the furnace. Thermostat fan switch is set to auto. doesn't matter … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Rheem Criterion natural gas furnace (with pilot light)
I have a Rheem Criterion natural gas furnace (with pilot light) - system was working fine this morning when i went to work - came home tonight and its not working - thermostat is set for 72 internal t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I Have Rheeme Criterion II Model RCBA-4882AS24. The burners
I Have Rheeme Criterion II Model RCBA-4882AS24. The burners won't light. It sounds like it is going through the motions, but the elctric pilot light does not come on? What can I do?… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
I have a Rheem Criterion II Gas Furnace. The furnace will
I have a Rheem Criterion II Gas Furnace. The furnace will not light now, it was just working yesterday. When I turn the fan to on from auto, the fan works, when the I set fan to auto and turn the heat… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a rheem criterion II gas furnace and when I set the
I have a rheem criterion II gas furnace and when I set the thermostat to heat, the ignition clicks but the burners will not light and the furnace will not produce heat. Do need to call a heating contr… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Rheem Criterion II with a programmable Aprilaire thermostat.
I have a Rheem Criterion II with a programmable Aprilaire thermostat. Problem is that I get a clearing fan and ignition and a temperary flame(about 10 seconds) then flame is gone but fan still runs th… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Hey Paul, I have a Rheem Criterion II furnace. The blower
Hey Paul, I have a Rheem Criterion II furnace. The blower works. I just replaced the pressure switch. The ignition heats up. The gas lights in one of the 3 long tubes. It stays on for about 5 or so se… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Ive got a Rheem Criterion propane gas furnace. It starts just
I've got a Rheem Criterion propane gas furnace. It starts just fine, ignites, blows flames and then after about 3 minutes the flames go away but the fan is still running.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hello. I have a criterion II gas furnace. The control panel
hello. I have a criterion II gas furnace. The control panel is showing both green lights steady, no XXXXX XXXXXght. It is only blowing cold air when i turn the thermostat to "heat" with the fan in aut… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a relatively new gas furnace (1995). The fan runs, but
I have a relatively new gas furnace (1995). The fan runs, but the heating/ignition element doesn't seem to come on to generate heat. Is the problem in the thermostat, or the fuse inside the furnace, o… read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
I have a Rheem Criterion II plus 2 two stage furnace (approx.
I have a Rheem Criterion II plus 2 two stage furnace (approx. 9 years old). Intermittently, the burners will not ignite. The electric igniter clicks and there is spark from the igniter but no flame co… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
My Rheem Criterion II furnace will not stay lit. It goes through
My Rheem Criterion II furnace will not stay lit. It goes through all the proper steps, then stops.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem Criterion Gas furnace. The blower is running
I have a Rheem Criterion Gas furnace. The blower is running but it is pumpin out cool air. We cleaned the filters but the heat does not come on. Would you change the Igniter? I tried turning the gas c… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
In my house I have a Rheem Criterion II furnace / AC. (not
In my house I have a Rheem Criterion II furnace / AC. (not the Criterion II +2. It starts up and the flames come on, then the blower starts, and the flames shut off. I heard about some ignitors, but t… read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
The furnace is a rheem criterion II . The furnace will go through
The furnace is a rheem criterion II . The furnace will go through its begining processes, the igniter key lights up and ignites the flame and as soon as the big fan comes on to circulate through the h… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x