Ive got a laars mini-therm induced draft jvi . the problem is the burners go out but the system still runs. sometimes the reset on the flame roll out works if not I shut off power for 15 min power back system runs if not reset button will fier it up. just replaced the high limit switch , ihave it set at 180 deg.. runs great for awhile locks out with no warning the system still runs just no fire

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Two weeks one week waiting for a new high limit switch

Contractor's Assistant: Do you plan on doing the work yourself?

Yes I worked hvac retired now

Contractor's Assistant: Are you an HVAC professional?

Retired installer

Contractor's Assistant: Anything else we should know to help you best?

Not at this moment

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
12/11/2017
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,602
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

What reset button? on the burner flame rollout sensor?

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

Then you have a dirty heat exchanger possibly a bad rollout sensor (not likely). A dirty (with soot) heat exchanger is an indication of inadequate air for combustion. The unit will have to be pulled apart and the heat exchanger cleaned.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a carrier furnace 58mca120 16-120 error code 33
I have a carrier furnace 58mca120 16-120 error code 33 followed by error code 13. replaced both the high limit and roll out switch and still have the error code. There are no other switches in the cir… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Laars JVi mini therm (surface heat ignition version)...it
I have a Laars JVi mini therm (surface heat ignition version)...it constantly will not light the main burner, seemingly after it gets really cold. I've tested out the voltages throughout the system an… read more
jhvac
jhvac
2 satisfied customers
G32Q3/4-100-3 pilot lights out and no indicator light is on
G32Q3/4-100-3pilot light is out, and there are no indicator lights on. I checked the breaker, and it's fine. Do you have any ideas?… read more
V12Tech
V12Tech
252 satisfied customers
I have a Carrier WeatherMaker 8000 2 speed furnace (17 years
I have a Carrier WeatherMaker 8000 2 speed furnace (17 years old). It used to switch into high speed if it took, say more than 10 minutes to bring the room temp. up to the thermostat setting. I have n… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Laars Mini-Therm II, Model JV, installed new 10 1/2
I have a Laars Mini-Therm II, Model JV, installed new 10 1/2 years ago when we built our home. Last September we replaced a 14 month-old electronic ignition -- a refit intended to solve the problem of… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
We have a Laars Mini-Therm JVi. It stopped heating last night.
We have a Laars Mini-Therm JVi. It stopped heating last night. The fan is running constantly but the ignition switch (JVH) will not light the boiler. I tried contacting our local distributer but they … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier model 58PAV135-20 furnace. It wont start
I have a carrier model 58PAV135-20 furnace. It won't start and the LED appears to be flashing a code (2 short flashes followed by 4 long flashes). Is there a place online that describes these codes?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a Laars Teledyne JVS mini therm boiler 14 years old. Unit
Have a Laars Teledyne JVS mini therm boiler 14 years old. Unit starts and runs fine but every so often the system doesn't function. I have to press the reset button on the flame roll out switch for th… read more
Al-Moderator
Al-Moderator
High School or GED
Intermittent problem with gas furnace. 3 to 5 times a week
Intermittent problem with gas furnace. 3 to 5 times a week the blower will continue to run and the house temp will keep dropping unless you shut the blower off on the thermostat then turn it back to a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem Furnace Model - FGPJ-10EBRJR Serial - EB5D307F199900304 I
I have a Rheem Furnace: Model - FGPJ-10EBRJR Serial - EB5D307F199900304 I have replaced the igniter, flame sensor, and the IFC board. Furnace will still not heat. Induced draft blower motor starts, 5 … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Carrier 58sta/stx 6 years old. found code 33. starts up fine.
Carrier 58sta/stx 6 years old. found code 33. starts up fine. inducer and flame kick off and blow runs for 2-3 minutes and then it starts rigth back up. had stupid tech come out and he cleaned the fla… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a amana air command 80 sse, blows cold air, cleaned
i have a amana air command 80 sse, blows cold air, cleaned flame sensor, nothing? thanks Jim… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Ive got a Teledyne Laars Induced Draft mini therm JVi the
Ive got a Teledyne Laars Induced Draft mini therm JVi the problem I'm having is the automatic pilot light does not light. it doesn't even try (tick, tick,tick). I ran out of propane a few days ago and… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I HAVE GOODMAN CETRAL HEATING MODEL NUMBER GMP100-4. ONLY BLOWER
I HAVE GOODMAN CETRAL HEATING MODEL NUMBER GMP100-4. ONLY BLOWER RUNS BUT NO HEAT. I TURNED OFF ELECTRIC CURRENT FROM THE BREAKER, AND TURNED ON, SAME THING. HOW DO I FIND WHAT PART IS BAD? DRAFT INDU… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hi there, I have a Carrier Weathermaker 8000. From 1994.
Hi there, I have a Carrier Weathermaker 8000. From 1994. My LED diagnostic light is blinking but I do not have an error code legend on my furnace, so I do not know what the flashes mean. Help!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rheem Criterion Gas Furnace Model RGDG-05NAUER. Ignitor lites
Rheem Criterion Gas Furnace Model RGDG-05NAUER. Ignitor lites up Burners go on then after 10 min. or so Burners shut off and the whole cycle starts up again. Changed the filter and installed a new dig… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
my Bryant heater is not working - the led code is #21 - what
my Bryant heater is not working - the led code is #21 - what is involved and what is the cost to fix that problem?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carirer furnace model #58sta. When the t-stat callss
I have a carirer furnace model #58sta. When the t-stat callss for everything works like it should, but after its been on for about 3 min. the gas shuts off and it starts blinkig error code 33, and the… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x