Have installed a Honeywell programmable thermostat.

Have installed a Honeywell...

Have installed a Honeywell programmable thermostat. Connected the red and white wires. When the thermo was set the valve to my boiler opened but when I reset the thermo to a lower temp it does not close. What can I do?

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I assume the thermo stat. The boiler was working fine with the older thermo.

Contractor's Assistant: Do you plan on doing the work yourself?

Trying to

Contractor's Assistant: Anything else we should know to help you best?

Not that I know of.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
12/9/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,609
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

Are you saying you turn down the thermostat and the burner doesn't shut down? Do you have more than 1 thermostat?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
3 thermos for 3 different zones. All the others in the house have been turned done.

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

So burner doesn't shut down? What brand zone valves?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
2 white rodgers and one honeywell. The white rodgers is the one in question. I cannot get the honeywell to work at all.
Customer reply replied 8 months ago
I have the red wire connected to the R connector and white wire connected to the W connector. Is that right?
Customer reply replied 8 months ago
The old thermo had 3 wires connected. There is a green wire as well.

Ok, as a general rule all your zone valves should be the same brand. But here I suspect you have a bad zone valve that's keeping the boiler energized. What model zone valve? If it's a 3 wire valve then you installed the wrong thermostat. No Honeywell valve is compatible with a 3 wire White Rodgers. You have a 2 wire thermostat.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
The valve works with the older thermo. These valves have been in the house for 20 years.
Customer reply replied 8 months ago
How can I tell if it a 2 or 3 wire wire valve?
Customer reply replied 8 months ago
What type of thermo should be used?
Customer reply replied 8 months ago
My Honeywell valve is connected to a 2 wire thermo. The old dial type. The WR thermos are connected to WR thermos.
Customer reply replied 8 months ago
The WR valves are connected to WR thermos.

Since you have 3 wires connected to the old stat you have a 3 wire valve. Here's some info on White Rodgers stats. Note the top 4 in the table are compatible with a 3 wire zone valve
http://s3.supplyhouse.com/product_files/WhiteRodgers-1F83C-11PR-ProductOverview.pdf

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Should the Honeywell prog thermo I have work with the Honeywell valve?

Yes

Ask Your Own HVAC Question
Customer reply replied 8 months ago
just connect red to R and white to W?

Yes for the Honeywell

Ask Your Own HVAC Question
Customer reply replied 8 months ago
ok I will try that. Thanks for your help.

You're welcome. I'd appreciate a favorable rating.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
No problem

Thanks

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,609
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,609
24,609 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a rodgers 1311 zone valve connected to an old mercury
I have a white rodgers 1311 zone valve connected to an old mercury thermostat. Trying to connect to an Emerson 1F85U-42PR programmable thermostat. 2 things. 1. When I discoonect the old thermo the hea… read more
Rick
Rick
HVAC Supervisor
24,609 satisfied customers
I am trying to see what I can find out about my thermostat
Hi, I am trying to see what I can find out about my thermostat causing short short- cycling. … read more
Rick
Rick
HVAC Supervisor
24,609 satisfied customers
I have a TACO control box zvc403 which turns on my
I have a TACO control box zvc403 which turns on my tripletude boiler. I just replaced a thermostat which was hooked into the control box. There were two wires coming out to the thermostat black and re… read more
Rick
Rick
HVAC Supervisor
24,609 satisfied customers
have zvc403 board, with lockinar boiler. Replaceing 2 wire
have zvc403 board, with lockinar boiler. Replaceing 2 wire thermostat with Honeywell w/wifi. ran new 5 wire. Hooked r&w as before, used new Y wire as C connected to white of 24v. New thermo powers on,… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am trying to replace a White Rogers 1f80-361 with a Honeywell
I am trying to replace a White Rogers 1f80-361 with a Honeywell rth6350d. I have single stage heating (gas furnace, hot water heat) A/C system. The WR had the following wires: red to rc with a jumper … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I recently installed a Honeywell RTH2310 theromostat in my
I recently installed a Honeywell RTH2310 theromostat in my home. The existing thermostat had three wires, R, G, and W. The wire colors and labels at the existing terminals all matched (terminal G had … read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I am hooking up a new honeywell rth2300 programmable thermostat
I am hooking up a new honeywell rth2300 programmable thermostat to the existing wires the old honeywell rth2300 was hooked up to and boiler will not fire. I'm not sure how the two wires (one red and o… read more
Rick
Rick
HVAC Supervisor
24,609 satisfied customers
Hello, I have a 3-zone SlantFin furnace (about 15 years
Hello, I have a 3-zone SlantFin furnace (about 15 years old) - one used for water and 2 used for the two floors of the house. The thermostats are White-Rogers brand. I noticed yesterday that the my fi… read more
Rick
Rick
HVAC Supervisor
24,609 satisfied customers
Just getting new boiler installed. We have open vented system
Just getting new boiler installed. We have open vented system so have EcoTEC 428 boiler with S-plan for CH/DHW (2 zone valves), Timer 140 fitted in boiler fascia, honeywell cyl stat, Grundfos pump, an… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
I need a wiring diagram for a LP522 used in conjuction with
I need a wiring diagram for a LP522 used in conjuction with a Glow worm HXI 15. The system is fully pumped mid position with pump over-run. A Siemans Flow minder,Honywell T6360B room stat and Poterton… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
Hi I have replaced a Sunvic SM 5203 with a Honeywell V4043H
Hi I have replaced a Sunvic SM 5203 with a Honeywell V4043H Motorised Zone Valve. Can anyone tell me which Honeywell wires correspond to the old Sunvic ones please. This zone valve is to control the h… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
Ive got an ancient oil boiler thats been converted to a gas
I've got an ancient oil boiler that's been converted to a gas boiler sometime in the past. It's in a 2-family victorian. It has a 180 degree set point and 15 lb pressure. It is a hot water boiler and … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I am not sure if you can help but I just installed a new boiler.
I am not sure if you can help but I just installed a new boiler. I am trying to hook up my thermostats to the boiler. I have 5 thermostats and and five zone control valves. The thermostats are run wit… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have an Honeywell Magicstat 3200 thermostat that seems to
I have an Honeywell Magicstat 3200 thermostat that seems to have a mind of its own.No problems with it over the past 4 years but in the past couple of days it will run the temperature up to 77 when it… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
My Honeywell TH8110u1003 programmable thermostat has a mind
My Honeywell TH8110u1003 programmable thermostat has a mind of it's own. When I program heat at 62 it maintains at 72. When I turn off the heat from the thermo, it keeps calling for heat. Should I cle… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I installed your CT87K (Heat Only Thermostat) today and when
I installed your CT87K (Heat Only Thermostat) today and when I turn the dial to 80 degrees, the furnace does not kick on. There are 2 wires in the wall...a black and a white. I put the black in the re… read more
Mike
Mike
Service Tech/ Installer
High School or GED
149 satisfied customers
Hi, I have an older Burnham oil burner for heating and hot
Hi, I have an older Burnham oil burner for heating and hot water, I replaced teh thermostat, seemed to still be heating when set point was set lower,(valve not closing?) can feel some heat from radiat… read more
Rick
Rick
HVAC Supervisor
24,609 satisfied customers
I am trying to replace a White-Rodgers 1E35-910 thermostat,
I am trying to replace a White-Rodgers 1E35-910 thermostat, connected to a White-Rodgers 1311-102, with a Honeywell RTH2310. The current thermostat has 3 wires: Red, White, Green. Red is connected to … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x