HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Connect one-on-one with {0} who will answer your question

Related HVAC Questions
I replaced my honeywell S8610U 3009 module a month ago
I replaced my honeywell S8610U 3009 module a month ago because that's what we narrowed it down to and now it's doing the same thing and I have no heat. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,063 satisfied customers
I currently have an older Furnae that the control module ent
I currently have an older Furnae that the control module ent out in. The old module was a S8600M and they said it was replaced with a S8610U but when I got it and hooked it up theres nothing. Nothing … read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,969 satisfied customers
I have a lennox gas furnace (1993) and i have replace the 8660K
I have a lennox gas furnace (1993) and i have replace the 8660K module and the VR8204H gas control. Now when i turn the unit on the fan immeadietly starts running.. no spark for the pilot.… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Wiring diagram of old furnace board with a new furnace board
I have the same issue with wiring the diagram old furnace board stay 20 4057 with a new furnace board st9129u.… read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
8,257 satisfied customers
My boiler pilot light is out and I did some troubleshooting
My boiler pilot light is out and I did some troubleshooting of the L8148E controller. I have confirmed that I have 120 VAC on the incoming L1/L2 terminals, and that I also have 120 VAC on the BLK/WHI … read more
Rick
Rick
Supervisor
25,591 satisfied customers
I have a Burnham P204 natural gas fired boiler. Performed
I have a Burnham P204 natural gas fired boiler. Performed yearly startup, system worked fine. A week ago it wouldn't fire. Wasnt even trying. I have replaced the transformer/relay, and the control boa… read more
Rick
Rick
Supervisor
25,591 satisfied customers
Have a gas fired Utica direct vent boiler with electronic
Have a gas fired Utica direct vent boiler with electronic ignition. Ignition quit working, I can move the module and get the boiler to start and run but only temporarily. I replaced the module and get… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,969 satisfied customers
experienced DIY'r & electrical engineer 2.5 Ton heat pump
experienced DIY'r & electrical engineer 2.5 Ton heat pump (split system) first symptom was AC not turning on at all Found 24VAC fuse blown in air handler and replaced it turned FAN to ON and blower wo… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,969 satisfied customers
Woke up this morning and my furnace was blowing cold air with
Woke up this morning and my furnace was blowing cold air with the heat on auto. I found that the ignition module (honeywell s8600m) was not working. I replaced it with a honeywell s8610u. Now unit lig… read more
Expert
Expert
I have a Carrier WeatherMaker 8000 2 speed furnace (17 years
I have a Carrier WeatherMaker 8000 2 speed furnace (17 years old). It used to switch into high speed if it took, say more than 10 minutes to bring the room temp. up to the thermostat setting. I have n… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
Hello I have a Gas furnace NTN 6075HFG1 with a ST9120C 4057
Hello I have a Gas furnace NTN 6075HFG1 with a ST9120C 4057 timer board. When I shut down the power and restart I can make the furnace start up and run correctly with the thermostadt. The conbustion b… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,969 satisfied customers
HELP. I am trying without luck to replace a Honeywell S86H
HELP. I am trying without luck to replace a Honeywell S86H Ignition module on my residential boiler with a Honeywell S8610U. I have a damper control with an end switch that sends power through a limit… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a robertshaw control module hs780 17nl-108 its 24
I have a robertshaw control module hs780 17nl-108 its 24 v in and at the 2 wires that would go to the ignitor read at about 24v also. My problem is another company took the ignitor and went out of bus… read more
N4IEA
N4IEA
Customer Service
Associate Degree
227 satisfied customers
I have a lennox g16 series furnace with an updated honeywell
I have a lennox g16 series furnace with an updated honeywell ignition module that is reading a low voltage fault. error just started occuring recently worked fine before this. How do i go about correc… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
comfort maker fa gas furnace gnk100n16a3 sn l9850 75629
comfort maker fa gas furnace gnk100n16a3 sn l9850 75629 exhaust blower and heat exchanger blower both run costantly no heat no lite off st9120c 4040 honeywell fan control has been changed out no help… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,969 satisfied customers
1. I am converting a Honeywell S86H Pilot Ignition Module to
1. I am converting a Honeywell S86H Pilot Ignition Module to the replacement S8610U(3009). 2. MV,PV,MV/PV connections are straightforward. This leaves the 25V, 25V(2), and TH-W connectors on the S86H … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
I HAVE AN ARMSTRONG FURNACE (EG6H80DC14-1), THE THERMOSTAT
I HAVE AN ARMSTRONG FURNACE (EG6H80DC14-1), THE THERMOSTAT WILL PICKUP BUT THE BURNER WILL NOT. I TURN OFF THE POWER TO THE FURNACE A COUPLE OF TIMES AND THE BUNER WILL LITE. THE FURNACE WILL WORK A F… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
My HB Smith steam boiler (GB300-7) came with an S8610 PV/MV
My HB Smith steam boiler (GB300-7) came with an S8610 PV/MV module, which failed after a few weeks of operation. The output voltage on the PV/GND terminals was 15VAC -- not enough to open the gas valv… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,791 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x