Goodman mbvc2000aa-1ae 24v 3A fuse keeps blowing. Few dats…

Customer Question
Goodman mbvc2000aa-1ae 24v 3A...

Goodman mbvc2000aa-1ae 24v 3A fuse keeps blowing

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Few dats few days

Contractor's Assistant: Do you plan on doing the work yourself?

Trying to

Contractor's Assistant: Anything else we should know to help you best?

Replaced an old thermostat w/ new one. originally thought that was the prob

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Thermostat is new Lux tx9600ts. all wiring to thermostat to blower to outside unit no shorts. all Tstat wiring is good.

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
12/8/2017
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello,

If this began after you installed the Lux, then there is most likely a wiring error, remove one wire at a time from the thermostat terminal strip in the furnace until the fuse ceases to blow. Tell me which wire when removed allowed the fuse to remain in tact.... leave the Red wire attached to the R terminal for last however.

We can go from there without a time limit

Ask Your Own HVAC Question
Customer reply replied 7 months ago
no, this happened before the new tstat. old tstat was failing. display was going away, could only see partial
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

was the 3 amp fuse blowing at that time with the old thermostat? If not, then there is a wiring error most likely causing the 3amp fuse to blow.

Follow my instructions to remove one thermostat wire at a time until the fuse ceases to blow, that will tell us which circuit the short is in.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
fuse was blown w/ the old tstat
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

Thanks

remove one wire at a time from the thermostat terminal strip in the furnace until the fuse ceases to blow. Tell me which wire when removed allowed the fuse to remain in tact.... leave the Red wire attached to the R terminal for last however.

,

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
it will take a few minutes
4
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

take your time, I am here for another 7 hours today... then back all day tomorrow

Ask Your Own HVAC Question
Customer reply replied 7 months ago
removed O - blew, removed G- blew, no more fuses
Customer reply replied 7 months ago
would need to drive ~45 minutes to get to autozone for more fuses
Customer reply replied 7 months ago
any comments. I don't want to drive to autozone
Customer reply replied 7 months ago
theme music of jeopardy.....................................................
Customer reply replied 7 months ago
DUM DUM DUM DUM ..DUMMMM DA DA DA DAAAA HELP ME PLZ
Customer reply replied 7 months ago
OK wait time is getting ridiculous. how do I stop this w/o you sucking my bank account dry?
Customer reply replied 7 months ago
As Pink Floyd immortalized......Is There Anybody Out There?
Customer reply replied 7 months ago
really, I'm trying to end this and give a 1 rating, but it wont let me. how the hell do we end this??????
Customer reply replied 7 months ago
rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off rip off
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

I will submit this to customer service they will arrange a suitable solution for you I am sure.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I installed a new thermostat with the help of honeywell
I installed a new thermostat with the help of honeywell technical support and now my new one isn't working, they think it might be a blow fuse in the air handler. I have attached pics of the thermosta… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have a Goodman GSZ140301 with heat pump. It was installed
I have a Goodman GSZ140301 with heat pump. It was installed last year but the thermostat only allowed heat or cooling. I had the thermostat switched so that it could go between heat and cooling by a s… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
New goodman GSZ160601BA w/ a MBVC2000aa-1ae. 1 1/8 & 3/8 30
new goodman GSZ160601BA w/ a MBVC2000aa-1ae. 1 1/8 & 3/8 30 ft lineset. High voltage to contactor 240V. hooked up yellow low voltage on the GSZ to yellow on the MBVC. left GSZ purple unhooked. I am ge… read more
Kcrand36
Kcrand36
Technician/Owner
Vocational, Technical or Trade School
72 satisfied customers
I live in amobile home. furnace is intertherm e2-eb 012ha.
i live in amobile home. furnace is intertherm e2-eb 012ha. ac works fine but when switching to heat small 5 amp fuse blows … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
RUUD Gas Furnace Model# UGVC-07EAAER, shorts out transformer
RUUD Gas Furnace Model# ***** shorts out transformer in Cool mode, runs fine in Heat mode.I disconnected the (2) Tstat wires that go to the outside unit, set Tstat for cool, it blew the 5 amp inline f… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Heat pump based heating system died overnight. Robertshaw
heat pump based heating system died overnight. Robertshaw stat said -AC. No power at stat. Checked 24v transformer - good. Found blown fuse on control board and replaced. Still won't fire up… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I just installed a 2 stage Goodman furnace. GMEC1205DNA The
I just installed a 2 stage Goodman furnace. GMEC1205DNA The induced draft blower comes on even with no call for heat. I disconnected all thermostat wires at circuit board to rule out mis-wiring or a s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a braeburn 3000 thermostat and had my son replace it
I have a braeburn 3000 thermostat and had my son replace it with a lux tx9600ts but he did not make note or wiring colors. Now the lux does not come on and when we put the braeborn back on it does not… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox 21j7101 tstat. I am replacing with a Pro1
I have a Lennox 21j7101 tstat. I am replacing with a Pro1 IAQ T715. Need wiring directions… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
, I am replacing a Trane TAYSTAT570 wit a LUX TX9600TS. The
Hi, I am replacing a Trane TAYSTAT570 wit a LUX TX9600TS. The Trane wiring has; Left Side G B R Y Right Side F - not used W X2 O The LUX has G B O Y RC RH W2 A W1 C Can you give me the magic match of … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
trying to install new thermostat,lux tx9600ts, old bryant programmable
trying to install new thermostat,lux tx9600ts, old bryant programmable fail, won't even approach the set temp. have 2-zone heat & cool, lennox pulse furnace from 1987 and bryant control board... 4 the… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Were switching our old White-Rodgers 4 wire thermostat to
We're switching our old White-Rodgers 4 wire thermostat to a Honeywell Wi-Fi Thermostat and having problems getting the A/C compressor outside to initiate and come on. We have heat however when the Ho… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier Infinity 96 furnace flashing code 24. the
I have a Carrier Infinity 96 furnace flashing code 24. the 3 A fuse keeps blowing. Is there something that often shorts out on their 24 V system?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a heat pump unit model eabd f030sb which connects to
I have a heat pump unit model eabd f030sb which connects to a goodman a36-10 air handler and a Lux tx9100e thermostat i need to know what wires connect to the air handler and then to the thermostat. i… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Lennox ac system fuse blows when system starts. Why?
I have Lennox ac system and the fuse #3 amp in blue wire keeps blowing. If jumped system would start and function fine. Now even a 5 amp fuse blows when system starts. Model #CB29M-41-2P AIR HANDLER.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
the indoor unit is trane and the outdoor unit is goodman a
the indoor unit is trane and the outdoor unit is goodman a 3 tons unit the nominal freon charge is 188 oz the white cable coming from the tstat to the indoor blower is not connected to the outside uni… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an older Ruud heat pump unit and it is shorting out
I have an older Ruud heat pump unit and it is shorting out the control transformer 24v side. What would would be the problem. Also the thermostat is old and has mercury tubes in it and I would like to… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I just tried to relocate my thermostat. I cut the wire in
I just tried to relocate my thermostat. I cut the wire in the attic. It had 6 wires. Only 3 wires are connected to the thermostat. After I reconnected the 3 wires, I see the LED flashing that I should… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less