I get 7 flashes on my luxaire residential unit. I checked…

Customer Question
I get 7 flashes...

I get 7 flashes on my luxaire residential unit

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

I checked the filters are slightly dirty the thermostat has a click sounding as soon as we increase the set point

Contractor's Assistant: Do you plan on doing the work yourself?

I checked the lame sensor and it is clean not a lot carbonation checked ingnitor looks continuos did not check for continuity the exhaust flue is not obstructed and the system resets upon cycling power to the unit yes i plan to work on it

Contractor's Assistant: Anything else we should know to help you best?

Normally you can smell if bad inducer motor, or you can see a broken ignitor or bad flame sensor. afte cycling the power it works for a while then it has the seven flashes any suggestions

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
12/8/2017
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,398
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

If the unit fires up then goes out in seconds you need to clean the flame sensor as a first step. It's not carbonation but oxidation on the sensor that causes a weak flame signal (among other things). If the unit doesn't fire up then you need to look more closely at the igniter. An ohm meter test is the best method but a visual inspection can also work. Even the tiniest flaw is cause to replace it. A little white powder is ok.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
After system reset the furnace will go through more then several cycles before the error code comes back so it is intermitten
But I will ohm the lgnitor
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Intermittent issues could be either the flame sensor or the igniter. Could also be a gas vale problem. The only way to pin it down if cleaning the sensor and testing the igniter prove unsuccessful, is to catch it when it happens.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I go through the check down and hopefully it is not the gas valve
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

It would be the gas valve if you have a glowing igniter and power to the valve but no main burner ignition. This is one you'll need to catch in the act.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Rheem furnace year 2011 have a code 12 low flame sense,
I have a Rheem furnace year 2011 have a code 12 low flame sense, code 45 low pressure switch open-inducer on high, code 46 low pressure switch open- inducer on low. we have had rain/snow for the past … read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Coleman CP9C 080 error code RED 5: roll out switch or pressure
Coleman CP9C 080 error code RED 5: roll out switch or pressure sensor open. I have shorted across the roll outs (although they read zero ohms with no difference. The pressure switch appears to actuate… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have RUUD Silhouette heater, Model # ***** 10NBRJR When
I have RUUD Silhouette heater, Model # ***** 10NBRJR When I turn the heater on the inducer motor starts running. After a few seconds the fan starts but the ignitor never glows, the gas doesn't come on… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Billy Same question, although yesterday, the diagnostic told
Billy Same question, although yesterday, the diagnostic told me to replace the flame sensor. I replaced it, now both LED's flashing fast, but the ingnitor now does not light, but did yesterday when de… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
G32Q3/4-100-3 pilot lights out and no indicator light is on
G32Q3/4-100-3pilot light is out, and there are no indicator lights on. I checked the breaker, and it's fine. Do you have any ideas?… read more
V12Tech
V12Tech
252 satisfied customers
I have a Laars Endurance gas furnace. It periodically shuts
I have a Laars Endurance gas furnace. It periodically shuts off, displaying LO (lockout) in the readout area. There does not seem to be any rhyme or reason as to what causes this to happen. It could b… read more
V12Tech
V12Tech
252 satisfied customers
Good morning. I have an American Standard Freedom 90 furnace
Good morning. I have an American Standard Freedom 90 furnace that's no more than ~4 years old or so. I have an error code blinking (two red blinks), and the furnace blower is running constantly, but t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I HAVE AGOODMAN FURNACE GMP 100.THE BLOWER COMES ON BUT THE
I HAVE AGOODMAN FURNACE GMP 100.THE BLOWER COMES ON BUT THE FLAME WON'T COME ON.I HAVE TRIED CHANGING THE SENSOR.… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I just purschased a new luxaire 80% 80,000 btu upflow natural
I just purschased a new luxaire 80% 80,000 btu upflow natural gas furnace. However, upon installation the burner will not ignite. Any help would be appreciated.… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
HVAC Question Trane Model XE 70 with a White Rogers Model
HVAC Question: Trane Model XE 70 with a White Rogers Model 50E47-060 Ignition Control Board. Opened front panel and found board with a continuous blinking red light. Unplugged power and plugged back i… read more
Shane D
Shane D
HVAC Service Manager
32 satisfied customers
i have a 2005 luxaire 80% gas furnace . i just purchased this
i have a 2005 luxaire 80% gas furnace . i just purchased this home with it installed forclosure .no prev.owner info . I get no heat blower kicks on 30 + seconds , Ignitor lights up , thermostat is set… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
OK, I have a Trane XE 78 with a couple of issues. First, the
OK, I have a Trane XE 78 with a couple of issues. First, the other day, it stopped blowing warm air. So I figured the ignitor went bad (like it has done in the past). Replaced the iginitor and now it … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a amana air command 80 sse, blows cold air, cleaned
i have a amana air command 80 sse, blows cold air, cleaned flame sensor, nothing? thanks Jim… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a york heater in a rental. Sorry, dont know the model,
I have a york heater in a rental. Sorry, don't know the model, etc. Twice, it has stopped heating but the blower fan works. The LED blinks 7 times. I have been doing some remodeling there and I have h… read more
Zev Simfukwe
Zev Simfukwe
High School or GED
23 satisfied customers
My Trane xl90 will start up, heat up, then the gas goes off
My Trane xl90 will start up, heat up, then the gas goes off, the main blower stops but the smaller return air / exhaust motor will keep running till you turn off the furnace. If I reset it, most of th… read more
Dan Linger
Dan Linger
Lead Technician / Energy Consultant
Bachelor's Degree
62 satisfied customers
I have a Carrier 58MTB furnace that will fire only occasionally.
I have a Carrier 58MTB furnace that will fire only occasionally. Inducer starts at high speed, ignitor lights, gas valve opens but no ignition. After 4 tries of course error 14 appears. With the burna… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our furnace isnt working. The LED indicator light blinks 3
Our furnace isn't working. The LED indicator light blinks 3 times indicating the pressure switch is stuck open. I'm not at all handy and some posting I found on line said the furnace could blow up or … read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
York Stellar Furn/AC, Mod P3UCD12N07601A. No Heat. Controller
York Stellar Furn/AC, Mod: P3UCD12N07601A. No Heat. Controller set to 72 degrees, I keep the fan on 24-7, for house air circulation. Heat cycles on and off as required. This morning, the fan is runnin… read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x