I have a boiler that is having issues starting, It is a

Customer Question
Good morning Contractor's Assistant:...

Good morning

Contractor's Assistant: Hi. How can I help?

Okay I have a boiler that is having issues starting, It is a ingniter type of igntion

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About a month I replaced the flame sensor as the repair shop said that they though it was that but, It still clicks It gets a call to heat and then starts a sequence to inginte the click gets louder and louder until I hear the gas valve open and the igniter is hot and gas is introduced. Then it shuts down. hence the thought of a bad flame sensor.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

This is a hydronic system so no filters, hot water thru out the house. there are 6 zones and all thermostats are working along with their respective valves. This issue is definitely in the boiler The control module has a flashing red light that blinks about the same speed as the clicking. So I am guessing that since the gas valve was opening before that it is most likely the controller that has failed.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes, have have a pretty good knowledge of electronics and electricity

Contractor's Assistant: Anything else we should know to help you best?

This is a solar heating system with back up boiler,

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
12/8/2017
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,770
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation.

What's the brand and model of the boiler?

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
how do i adjust the pressure on my hot water heating system
how do i adjust the pressure on my hot water heating system for my two story house. what should it be cause it was low now i think it is to close to the prseeure relief setting of 30 psi… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
Hi I have replaced a Sunvic SM 5203 with a Honeywell V4043H
Hi I have replaced a Sunvic SM 5203 with a Honeywell V4043H Motorised Zone Valve. Can anyone tell me which Honeywell wires correspond to the old Sunvic ones please. This zone valve is to control the h… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
how do you fix an error code 25 on a new baxi luna 3.first
how do you fix an error code 25 on a new baxi luna 3.first it was showing error code 10E they remidied that problem now there getting error code 25.the heating system is not up and running yet if that… read more
Brian
Brian
Plumbing & Heating Engineer
129 satisfied customers
I have a large hot water heat system with 8 zones using
I have a large hot water heat system with 8 zones using wired thermostats all connected to 2 Caleffi ZVR104 relay panels. Each wired thermostat is connected via 2 wires (R and W) on the ZVR's thermost… read more
hvacdave84
hvacdave84
53 satisfied customers
I can't get the boiler to ignite. The heating system has
Hi I can't get the boiler to ignite. The heating system has been operating continuously for probably 6 months now. This is unusual for me. I normally only use the system for hot water for washing etc.… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a Goodman heating system and it is not heating
I have a Goodman heating system and it is not heating properly. The burner starts for about 3 seconds and then it goes off. The blower keeps blowing air, but not warm enough. Any ideas what it could b… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
I am having a problem with my heating system, the unit will
I am having a problem with my heating system, the unit will start up and the heat will ignite and there is flame but after a few minutes the limit switch opens and shut down, is the vent blower causin… read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
The heating system seems to be on a hold for one day that I
Second opinion] The heating system seems to be on a hold for one day that I cannot chnge Help!… read more
Bill
Bill
Service Mgr
79 satisfied customers
My boiler (forced hot water heating system) has been running
My boiler (forced hot water heating system) has been running when no zones have been calling for heat. Why?… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
I own a Payne heat pump air conditioning/heating system
Hello. I own a Payne heat pump air conditioning/heating system that's been in my home for 10 years or more. I'm sure it replaced the unit originally in my home. There's an air return in the largest ro… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,682 satisfied customers
The heating system seems to be on a hold for one day that I
The heating system seems to be on a hold for one day that I cannot chnge Help! … read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
We had a new heating system put in this fall, and the
We had a new heating system put in this fall, and the contractor has been back 6 times trying to get the T6 thermos. working right. The down stairs thermo. operates a heat pump until the temp gets to … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
Heating system working but is making a buzzing type sound
Heating system working but is making a buzzing type sound every minute or so. It sort sounds like it's trying to start but it's already running. You can hear the sound at the electrical panel inside o… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an electric heating system with a heat pump, and a
I have an electric heating system with a heat pump, and a Totaline thermostat model P274-1200. I received a NEST Pro thermostat that I would like to install. I want to make sure I have the wiring corr… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 5 zone boiler heating system with 6 Honeywell
I have a 5 zone boiler heating system with 6 Honeywell 3-speed model pc3f1558iufoo/u circ. Pumps. 1 is on the main recir line, 4 on upstairs rad loops & 1 on in-floor loop. There are two auto bleeds. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a heating system that pumps hot water from the boiler
HI! I have a heating system that pumps hot water from the boiler to radiators throughout the house. I have two rooms that are lacking in heat. The pipes in the radiator in these rooms are cold but the… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
How do you pump water into a boiler heating system to get
How do you pump water into a boiler heating system to get the air out after draining system to fix a leak on the second floor… read more
Rick
Rick
HVAC Supervisor
23,770 satisfied customers
We have a hydronic heating system with a Ferroli boiler. It
Hello. We have a hydronic heating system with a Ferroli boiler. It has been intermittently failing to ignite over the last few months. Now, however, the flame will only stay on for a few seconds after… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.