I have a carrier model performance 93 that quit working

Customer Question
I have a carrier...

I have a carrier model performance 93 that quit working after power outage. there is a E2 flashing on thermostat. blowing running but wont ignite

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Not the thermostat

Contractor's Assistant: Do you plan on doing the work yourself?

Depends on what it is I have pool heater experience and industrial maint but no hvac

Contractor's Assistant: Anything else we should know to help you best?

What does the E2 mean

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 25 minutes by:
12/8/2017
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,347
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Russ here check the fuse on the furnace board to see if it is blown. It is a 5 or 3 amp auto type fuse. It is in blower compartment. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

1st thing is turn off power to outside and inside unit to reset faults and retry furnace. E3 is outside sensor fault. Russ

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Goodman furnace light flashing four times. Fan kicks on but
Goodman furnace light flashing four times. Fan kicks on but wont ignite … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trane hvac unit - 24 years old - AC Works - no heat - gas
trane hvac unit - 24 years old - AC Works - no heat - gas draft fan comes on when heat called for - but not igniter - or gas. Igniter tests OK, 64 ohms, glows OK with test power. Pressure switch tests… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Getting an E2 error on my Carrier programmable thermostat in
Getting an E2 error on my Carrier programmable thermostat in cooling mode. Measured voltage at the air handler and getting 27.9 volts between R & C. Error indicates low voltage situation. Bad thermost… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,347 satisfied customers
Carrier Performance 93 installed 5 years ago. Last week I
Carrier Performance 93 installed 5 years ago. Last week I had a new thermostat installed but problem has not been resolved. Here is the pattern since then: New thermostat installed Wed March 9th and p… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Have a Carrier Performance 93 furnace that will not fire up.
Have a Carrier Performance 93 furnace that will not fire up. Was working fine this morning. I checked the main breaker box, pulled the panel to check the fuse and fine. The led it YELLOW.. .not blinki… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm ***** *****. I have a Carrier Performance 93 that seems
Customer: I'm ***** *****. I have a Carrier Performance 93 that seems to be having a problem when it goes into Stage 2. The voltage to the thermostat drops to 0, and then the unit shuts down. After a … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier Performance 93 HVAC system. The control
I have a Carrier Performance 93 HVAC system. The control board was just replaced by factory technician 2 week ago. Right now the furnace will not come on. Looking at the Honeywell panel, the yellow pu… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,347 satisfied customers
Carrier Performance 93. Holding the house at around 63, even
Carrier Performance 93. Holding the house at around 63, even though set at 74. Thermostat is relatively new. LED code 3 short, 2 long. Sometimes gives warmish air, sometimes cold. Tried turning off an… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have a Carrier Model# ***** furnace flashing code 12 Blower
Have a Carrier Model# ***** furnace flashing code 12 Blower on after power up - Blower runs for 90 seconds if unit is powered up during a call for heat. (R-W closed) I replaced the control board in th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
There was a power outage in Riverside, CA and now the AC does
There was a power outage in Riverside, CA and now the AC does not work. We had a technician come out but they told my tenant is was a short in the wires and then tried to price gauge her. Is this some… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
My carrier gas heater model 58ssb will not ignite. I can hear
My carrier gas heater model 58ssb will not ignite. I can hear the blower fan and the the click to ignite - but no ignition.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Error E2 on the thermostat (Carrier rooftop heater / air conditioner
Error E2 on the thermostat (Carrier rooftop heater / air conditioner unit). We set the stat at 70°F on Hold. Next morning it was 50°F with E2 error code. We powered on / off and this reset the stat an… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have issue with my YORK. some time fan continue work aft
I have an issue with my YORK. Sometimes fan continues to work after gas/heat shots down. This could continue for over an hour before stoping. I called for service and diagnostic specialist find no pro… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I installed a Honeywell RTH6450 thermostat. I have two questions -
I installed a Honeywell RTH6450 thermostat. I have two questions: - are the batteries only used for the clock/calender so they work even during power outages, or are the batteries also used to run the… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,347 satisfied customers
I have a Carrier central heating and air conditioning unit
I have a Carrier central heating and air conditioning unit model # XXXXX Ocassionally it displays an "E2" message in the display window on the control panel in the house. The manual does not indicate … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Carrier Performance 93, installed in July 2008. The
I have a Carrier Performance 93, installed in July 2008. The problem with the furance is that about 30% of the time the unit will not automatically turn on, requiring that I do a power reset to get th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Carrier Gas Furnace 9200-58MXA. Sometime in the night
We have a Carrier Gas Furnace 9200-58MXA. Sometime in the night after Daylight Savings time change the furnace quit running on auto and when we turned it to ON it runs but only blows cold air, The the… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a carrier 48ss heat/air unit, the fan wont quit blowing
i have a carrier 48ss heat/air unit, the fan wont quit blowing and the heater will only blow cold air the red led is flashing 8 times can you help with a diagnosis?… read more
Robert
Robert
Associate Degree
161 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.