S valve will shut down then the startup procedure starts…

Customer Question
S valve will shut...

S valve will shut down then the startup procedure starts again red light is on solid new gas valve and flame senser so dont know what is causing this problem

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

A month or two

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

All safety circuits are working so thats why i am so confused as to why it goes out when fan is about to turn on. I also have installed a new circuit board last year.

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 hours by:
12/7/2017
HVAC Technician: Regan Land, HVAC Technician replied 7 months ago
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Hi, my name is ***** ***** I'll be assisting you with your question. I apologize for the extended wait time you experienced, I've only just come online now and would like to assist you with your question if you still need help. Can you please let me know if you still need help with your question?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
yah i sure do
Customer reply replied 7 months ago
I payed for a phone call. When can I expect the HVAC Technician to give me a call?
HVAC Technician: Regan Land, HVAC Technician replied 7 months ago

Before we proceed with the phone call, can you please provide the full make and model # of the furnace? It will be on a tag on the inside of the panel in the burner compartment.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
ok mate its a goodman modle gmtho45-38 serial number###-##-####its a small one goes right through its cycle to the point gas is lit but as soon as igniter cools down gas valve cuts out
HVAC Technician: Regan Land, HVAC Technician replied 7 months ago

Okay, thank you! Hopefully we can solve this quickly without you needing to spend the additional money on the phone call - If you look at the burners you should see a flame sensor in the direct path of the flame on the opposite side of the burners of the igniter. Remove that sensor and clean with steel wool, then reinstall and try again. If it works then you're good to go! If not, we can proceed from there.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I wish it were that easy mate. I have bought a new flame sensor even cleaned that one and still furnace shuts down right before the fan kicks in. The other mystery is there are no blinking lights to indicate a problem. I have replaced most of the parts that would cause this happening, gas valve, flame sensor, even a new circuit board. I have done a physical inspection to make sure there are no cracks and there are none. I have jumped the connection to the blower to make sure it works and it does. I have done a meter test to the circuts and to my knowledge they seem to be giving off the right voltage.
HVAC Technician: Regan Land, HVAC Technician replied 7 months ago
does the fan kick in immediately when the flames shut off? Or does it never come on unless jumped? Check the wire beween the sensor and board closely - do a continuity check on it as well. Also, the furnace verifies flame through ground, so make sure the furnace is grounded properly and ground connection is tight.
Ask Your Own HVAC Question
Customer reply replied 7 months ago
I will check that and get back you by today.
HVAC Technician: Regan Land, HVAC Technician replied 7 months ago

Sounds good, thanks

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Regan Land Your Own Question
Regan Land
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
768 Satisfied Customers
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist

Regan Land is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My gas furnace Model 80+AFUE runs for a few days and then
my gas furnace Model 80+AFUE runs for a few days and then quits igniting. All the switches and sensors seem to be functioning. When the thermostat calls for heat, everything starts up okay. The ignigh… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We are dealing with a hydrotherm 175,000 BTU boiler about 4
We are dealing with a hydrotherm 175,000 BTU boiler about 4 years old. It has a history of occasionally having the pilot light go out with the last incident resulting in $75,000 water damage. To allev… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My 20 year old rheem criterion 11 furnace finally had a
My 20 year old rheem criterion 11 furnace finally had a problem. I turn the thermostat on and everything fires and cycles in sequence. Once the room gets to the set temperature the exhaust blower and … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to test run a gas furnace using a Honda eU2000 portable
I'm trying to test run a gas furnace using a Honda eU2000 portable generator. When I plug the power cord for the heater (blower and thermostat) and turn the AC off and the heat temp to 81 degrees, the… read more
Expert
Expert
i have the rheem classic series,super quiet 80.every time i
i have the rheem classic series,super quiet 80.every time i turn it on it fires up ,but then the flame goes right out and the fan kicks on ,no blinking lights just the two solid green.the third turns … read more
rpen7111
rpen7111
119 satisfied customers
I have a Luxaire TG85080B12MP11A with a wireless thermostat.
I have a Luxaire TG85080B12MP11A with a wireless thermostat. Once in a while (once every couple of weeks), the furnace will reach the programmed temperature. It drops the heat (like it should) but the… read more
rpen7111
rpen7111
119 satisfied customers
My 3 y old York furnace, the fan spools up but wont stay on.
My 3 y old York furnace, the fan spools up but won't stay on. The heat in the house is dropping.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
What is the little red circuit breaker thing in the middle
What is the little red circuit breaker thing in the middle of the IFC on a Ruud Silouette II model # XXXXX… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a bryant, the fan motor keeps running and will not shut-off
I have a bryant, the fan motor keeps running and will not shut-off by thermostat, I have had the curcuit board and the transformer replaced but its still doing the same thing blowing cold air. I was r… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Coleman Evcon Furance in a moble home . Model # dlaso75bdd.
I have a Coleman Evcon Furance in a moble home . Model # XXXXX When we check it out the furance would light and burn for while, then go out, then the fan kept going on and off so we bumped the circuit… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello, I have an Tappan furnace that is not functioning properly.
Hello, I have an Tappan furnace that is not functioning properly. Propane model FG6R6C100C-16. It was installed in 2004. Is there a known issue with the control board on this model? Thermostats call f… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, Have a TRANE XR90 that fails to open the gas valve.
Hello, Have a TRANE XR90 that fails to open the gas valve. After startup proceedure, glowplug gloes and the circuit "clicks" to open the gas valve but the gas valve does not open, no power to the valv… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
hi im working on a 105e combi boiler has just had curcuit boardand
hi im working on a 105e combi boiler has just had curcuit boardand diaphram to the hot water section of diverter .hot water works fine heating side pump runs micro makes goes to ignition fires for 2se… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
I have a Miller branded Nordyne furnace modle m1mb 077a aw.
I have a Miller branded Nordyne furnace modle m1mb 077a aw. The flame will not stay lit. The igniter is working, the gas valve opens, the flame starts but then within less than a minute it goes out. T… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a model KG6RA120C-20 gas furnace that short cycles.
I have a model KG6RA120C-20 gas furnace that short cycles. I have checked all 3 safety / limit switches and even eliminated them and it made no difference. I have bypassed the pressure switch and it s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I went to service an older nordyne mobile home furnace today
I went to service an older nordyne mobile home furnace today and had some trouble figuring out the problem. I replaced the thermocouple, lit pilot, then called for heat. The burner started then in abo… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a rheem classic 90 plus, it is 3 years old. It is a
I have a rheem classic 90 plus, it is 3 years old. It is a gas furnnse. It is turning off and on, sometimes it does not fire up, and just blows cold air. Othertimes it runs like a champ.… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
I have a FRIDGIDAIRE FG6RC 080c-16b gas furnace. It wont
I have a FRIDGIDAIRE FG6RC 080c-16b gas furnace. It won't light (hot shoe won't even come on), but gives error codes alternating between "false flame / gas valve relay shorted", "pressure switch is op… read more
hvacmrfixit
hvacmrfixit
disabled
Vocational, Technical or Trade Scho
118 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.