My older furnace short cycles because the burner shuts off…

My older furnace short...

My older furnace short cycles because the burner shuts off before thermostat setpoint is reached

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I'm not sure but I don't think it's a thermostat problem

Contractor's Assistant: Do you plan on doing the work yourself?

I would depend on the problem

Contractor's Assistant: Anything else we should know to help you best?

There's probably a lot that I could tell you but what info would be helpful?

Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 minutes by:
12/6/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,400
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

What's the brand and model of your furnace?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The brand is Bryant. I don't know the model.

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 922
Experience: Owner at Gaztech
Verified

Hi I am Gaztech1, a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

The furnace is probably shuting off on high limit (getting to hot) then it cools down with blower fan then starts again.

Does this sound like its the case

Possible causes

  1. Cloged filter
  2. dirty blower wheel
  3. dirty AC coil
  4. restricted return air grilles (ex. furniture covering air glilles)
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 922
Experience: Owner at Gaztech
Verified
Gaztech and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 7 months ago
Could it be a bad high limit? If it is. Where would I look for the high limit sensor? I will look into all of your suggestions. Thanks.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 922
922 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My furnace double or triple cycles heating is fine and have
my Coleman furnace double or triple cycles heating is fine and have installed a new thermostat which didn't help, after a heat cycle the burner stays on and another cycle begins … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an old tempstar furnace that has a fan/limit switch.
I have an old tempstar furnace that has a fan/limit switch. When heat is called for, the burners ignite, the fan comes on at the proper temperature, and the burners will run for about 5 minutes until … read more
Rick
Rick
HVAC Supervisor
24,400 satisfied customers
I have a Honeywell RTH7600 Programmable Thermostat. I have
I have a Honeywell RTH7600 Programmable Thermostat. I have an fairly new oil furnace. The problem I have is that the thermostat keeps coming on at a 1 degree temperature change which is way to much as… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 20 year old York updraft gas furnace model # XXXXX
I have a 20 year old York updraft gas furnace model # XXXXX When I call for heat, the vent motor runs, then the burner ignites. But the blower motor never comes on and after a few minutes the burner s… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My furnace will sometimes kick on and run a few minutes and
My furnace will sometimes kick on and run a few minutes and shut off... it is inconsistent. It just shut off a minute ago but did not reach the temp set at Thermostat. Changed batteries in thermostat … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have a LP gas furnace in a mobile home, model CMF 80-PG CONV,
I have a LP gas furnace in a mobile home, model CMF 80-PG CONV, Robertshaw electronic thermostat. Problem: Furnace shutdown last night. I opened the door on the furnace pulled on switch and furnace tu… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Fridgidaire 903016F furnace. At the start of this
I have a Fridgidaire 903016F furnace. At the start of this heating season this unit has started to short cycle a lot. What it does is this: induction fan starts, then the igniter lights, after short d… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
Hi Tim, I have another question for you. I find my furnace
Hi Tim, I have another question for you. I find my furnace runs for a while and even though the tempsetting is not reached, it will shut down and restart again. Goes through 2 or 3 cycles like this be… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a honeywell RTH 7000 series programmable thermostat
I have a honeywell RTH 7000 series programmable thermostat and noticed today that the furnace seems to run properly, but the cycle time is very short. It will start up just seconds after it shuts down… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,514 satisfied customers
Hi our heat is forced air from our central heat/air unit.
Hi our heat is forced air from our central heat/air unit. The unit is a coleman but i don't know the size and it is approximately 5 years old. It wasn't used much before we moved in. When our heat com… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a Honeywell CHronotherm IV Plus that intermittently
I have a Honeywell CHronotherm IV Plus that intermittently does not heat to the requested temperature. The A/C worked fine all summer, but in the winter the heater occasionally either fails to turn be… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
768 satisfied customers
I have a Carrier HVAC ( Model 158RAV055-GC Series 100 Serial
I have a Carrier HVAC ( Model 158RAV055-GC Series 100 Serial Number 1492A03944 ) ADDITIONAL INFO 3191 04-7004. My problem is that my heater won't heat. The heater blower comes on but the hot surface f… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Wondering if anyone can help me out on this. I have a Rheem
Wondering if anyone can help me out on this. I have a Rheem oil furnace model ROBC-067LBEA controlled by a Honeywell programmable thermostat. The furnace runs fine and goes through its normal cycle wh… read more
Rick
Rick
HVAC Supervisor
24,400 satisfied customers
I have an amana 80%efficient installed approximately 1988.
I have an amana 80%efficient installed approximately 1988. It had a rotary dial, merc switch thermostat. I recently changed it to a honeywell rth6300b programmable. Since then it does two weird things… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
I have a forced hot air, gas fired furnace controlled by an
I have a forced hot air, gas fired furnace controlled by an analog thermostat, like the one posted on your web-page. When I set the temperature above what the room is at expecting the heater to come o… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have an Trane XE80 it blows cool air not warm at all I have
I have an Trane XE80 it blows cool air not warm at all I have to put the therastat on 74-76 to get the house to 70… read more
Jim Eastwood
Jim Eastwood
Lead service
High School or GED
100 satisfied customers
The furnace in my mobile home .the burner stays lit all the
The furnace in my mobile home .the burner stays lit all the time and the blower short cycles all the time and it never gets warm. what could it be?… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
I have a propane furnace with a digital programmable thermostat.
I have a propane furnace with a digital programmable thermostat. I have the thermostat set to 68 degrees but the actual temperature in the house is 60 degrees. Is there something I can do to fix the p… read more
Al
Al
Master Service Technician
Votec, College, Master Electrical S
24 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question