I'm replacing an old model Honeywell thermostat with a new T3 programmable thermostat. The old thermostat was connected with four wire; green, red and two whites. There is a fifth (unused) red wire in in the bundle. I'm confident about the locations of the red, green and one of the white wires on the new thermostat. The other white wire was connected to a terminal that was either orange or yellow. Should the second white wire be connected to the orange or yellow terminal. Does the second red wire that was previously unconnected have a function?

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

We had a technician check out the furnace when the problem first arose about 4 weeks ago. He said the furnace was fine. Furnace stopped working again so assumed but not absolutely certain the problem is the thermostat.

Contractor's Assistant: Do you plan on doing the work yourself?

Replacement of the thermostat appeared to be relatively simple and I have a fair amount of experience with electricity and mechanics so I started on the job myself.

Contractor's Assistant: Anything else we should know to help you best?

Can't think of anything else. Ask if you have questions.

Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
12/6/2017
HVAC Technician: Rick, HVAC Supervisor replied 9 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,848
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

Did you label each white wire? Thermostat terminal designations are not color referenced although they can correspond with the first letter of a wire color. Typically the 4th terminal of a 4 wire heat/AC config would be the Y terminal.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a TRANE XV90 that I am attempting to plug a new
Hi, I have a TRANE XV90 that I am attempting to plug a new Honeywell WiFi thermostat to replace a failed thermostat. I have a six wire bundle that goes between the furnace and the termostat. The Red, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Installing a honeywell 9450 Wi-Fi Thermostat. Current
installing a honeywell 9450 Wi-Fi Thermostat. Current wiring: Thermostat: G - Green wire Y - Blue W - White RD - Red Heating Unit Circuit Board: W2 - No Wire Y1 - Blue BHUN - No wire G - green wire CO… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi. I am replacing an old Trane XT300 thermostat with a new
Hi. I am replacing an old Trane XT300 thermostat with a new honeywell wifi model. Basic heat/AC system no heat pump. The wiring on the current thermostat has white wire to W, yellow wire to Y, red to … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hi. I am trying upgrades old Rodgers1E30W Thermostat to NEST
Hi. I am trying have and old White Rodgers 1E30W Thermostat with no W-R labelling and am trying to determine which set of wires go to the a new programmable thermostat (Nest). There are two bundles of… read more
Expert
Expert
I installed a Honeywell RT8580 WiFi thermostate in place of
I installed a Honeywell RT8580 WiFi thermostate in place of an old Rite-Temp thermostat this past fall. I have a conventional gas fired furnace (Older model Consolidated Systems) in the attic and a Yo… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
1. Have hydroheat combined AC/cooling; heat not working b/c
1. Have hydroheat combined AC/cooling; heat not working b/c fan will not start in AUTO setting -- WILL work if turned "ON"/off manually when set on hear (A/C working fine -- so doesn't seem to be prob… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Good morning... I just purchased a Honeywell RTH8580WF and
Good morning... I just purchased a Honeywell RTH8580WF and according to the instructions, needs a "C" wire - 24 VAC. I've examined the wiring at both the Thermostat and Terminal Block at the unit in t… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
I am replacing a White Rodgers 1F89-211 thermostat on a heat
I am replacing a White Rodgers 1F89-211 thermostat on a heat pump unit with a programmable Honeywell RTH6350. Do you have a terminal cross reference for the two units? Thanks.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a TH61101D1006 thermostat and it has just gone blank,
I have a TH61101D1006 thermostat and it has just gone blank, obviously no AC/Heat control. So, I do what?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a standard AC/heating system without a heat pump. I
I have a standard AC/heating system without a heat pump. I got a programmable thermostat honeywell 4210D1005 that apparently is meant to be used with a heat pump. Can I still use this with a regular A… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Problem; I have a trane heat pump system. Model # XXXXX
Problem; I have a trane heat pump system. Model # XXXXX with auxilliary/backup. Previously I had a honeywell thermostat, I Guess T8011R 1014 (2).this is all I find on it. I fell and hit this and every… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am trying to wire a Honeywell RTH7500 to run a Trane heat
I am trying to wire a Honeywell RTH7500 to run a Trane heat pump A/C. The wires that were hooked up to the Trane non programmable thermostat do not match up to the terminal labeling on the Honeywell. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am wanting to replace a luxpro PSDH121a thermostat with a
I am wanting to replace a luxpro PSDH121a thermostat with a wire configuration of c (blue wire), e (brown), y (yellow), O (orange), w2 (white), r (red), g (green) and b that is unused, the replacement… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Good Afternoon I am upgrading from an old Honeywell T841A1068
Good Afternoon I am upgrading from an old Honeywell T841A1068 thermostat, to a Honeywell TH3210D. The terminals for the T841A1068 are B, W, F, X2, G, Y, R, O, T * only the W and F terminals did not ha… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a heat pump with 2-stage heat.... 1-stage cooling. The
I have a heat pump with 2-stage heat.... 1-stage cooling. The original thermostat is bad, it is a Coleman Evcon The terminals on the thermostat are as follows: E G B O Y R X L W2 The wires coming out … read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
We currently have a Honeywell T841A1746 Heating-Cooling Heat
We currently have a Honeywell T841A1746 Heating-Cooling Heat Pump Thermostat, and we bought a Honeywell RTH110B Non-programmable Electronic Thermostat to replace it. The problem we have run into is th… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
I just installed a new Honeywell digital thermostat and my
I just installed a new Honeywell digital thermostat and my heat is not working. The old thermostat had the following labels for the wires: C G W Y R 4. The honeywell wire chart showed that the 4 wire … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I just bought a Honeywell RTH2300B programmable thermostat
I just bought a Honeywell RTH2300B programmable thermostat to replace a round Honeywell T86A thermostat. To which terminal do I hook the green and yellow leads and where do I hook the black and red le… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.