I have a Lennox Innovator G32V5. Yesterday it quit working…

Customer Question
I have a Lennox Innovator...
I have a Lennox Innovator G32V5. Yesterday it quit working properly. Here's the scenario. Thermostat calls for heat, unit ignites the flame, ECM blower rotates back and forth but does not fully turn on. After about 45 seconds, the unit completely shuts off even to the point that my Nest controller has no power and reports a power problem. When I first noticed the problem, the indicator LEDs flashed a pattern indicating a low flame sensor. I took the sensor out, cleaned it up, put it back in. This time there were no faults reported by the LEDs but the unit behaved the same way. I'm hoping it is not a bad ECM but I do not have a tester to check it with. Any recommendations?
Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
12/4/2017
HVAC Technician: Phil, Mechanical Engineer replied 9 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,880
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, The electronics that control the ECM motor are bad, either the electronics in the end bell (most likely) or the electronics in the furnace/air handler that sends signals to the ECM motor (less likely)... or the windings in the ECM motor are bad, slight chance of that, 10% at the most.

.

Take a close up, exceedingly well focused photo of the wiring diagram glued inside the furnace/air handler door, and I will mark it up with trouble shooting instructions. Use the 'add files' link next to your send button to get the photo(s) to me.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed , after you rate this answer:

Select the 'finish and rate your expert link' near the top of your page and click on it.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally.. and with over 8,000 questions answered here since 2009, with a 98.5% satisfaction rating.

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

That said, I cannot guarantee that you will not do something unsafe, or cause damages. You take that risk.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

.

Tell me a lot about your technical background and instruments on hand so that I can coach you most effectively. We can go from here as you keep asking follow up questions without any limits …

.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
I'm not home right now but perhaps I can run home sometime soon for the picture. I have replaced the thermistor in the unit before, 5-6 years ago, so this wouldn't be the first time I've worked on it. However, if it is the problem, seems like the only thing to do would be to replace it. It's rather expensive so before doing that I wanted to make sure it wasn't the flame sensor. The fact that the LEDs indicated a problem initially with that sensor makes me think it still might be the cause. Is there anything I can do to bypass the sensor, only for test purposes of course, to rule it out of the equation?
HVAC Technician: Phil, Mechanical Engineer replied 9 months ago

Hello again, thermistors generally cost $30 to $60 at the most, unless you mean something else, if you can put a tiny check mark by it on the photo of the wiring diagram you send that will help.

There is no time limit, we can go from there

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Sorry, I wasn't very clear. I meant that replacing the whole ECM would be expensive. The small thermistor was only a couple of dollars but I'm certain that is not the problem this time because the motor does rotate back and forth as it tries to determine the direction to commutate the windings. As I see it, I replace the flame sensor or bypass it somehow for test purposes or I replace the ECM. I do not have access to a universal ECM tester. Can I bypass the flame sensor to test the rest of the system?
HVAC Technician: Phil, Mechanical Engineer replied 9 months ago

Hello again, the flame sensor operates to shut off the gas valve if there is no flame, it does not affect an ECM motor in any way.

There are 4 different types of ecm motors, so far it sounds like you have an older Gentex 2.5 model, the entire electronics end bell of that motor can be replaced for less than $200... assuming the motor windings, bearings and rotor are good (they generally are quite durable).

A Genteq brand ecm motor tester is under $100 for most models. Getting one of those would be a good idea.

click here please

The motor situation needs to be corrected before the rest of the system will operate....thats the short explanation, tell me if you want the 500 word explanation or not.

We can go from there

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Thanks. I'm back in front of it now. It ignites just fine. However, the status LEDs go from both flashing fast (heat called) to one slow one fast (low flame sensor). It does stay on for about 3 minutes but the fan does not come on. Will the fan be called if there is a flame error being reported by the system? I've just noticed that it doesn't try to rotate at all. However, when I turn the whole system off then on again, it spins back and forth.
HVAC Technician: Phil, Mechanical Engineer replied 9 months ago

Hello it sounds like a bogus flame sensor error, if the flame sensor was bad the burner would only stay on for a few seconds in most cases...

so far sounds like the blower motor controls are defective, so the blower does not come on, then the furnace keeps firing for 3 whole minutes until the high temperature safety limit switch trips.

Your test on spinning the blower wheel also points failed electronics ... you need the tester to discover what exactly.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,880
9,880 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,880 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Lennox CBX32MV with ECB40 giving me a .E201 code.
I have a Lennox CBX32MV with ECB40 giving me a .E201 code. What does the unit think is going on? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am looking at a Ruud furnace Model ugra06emaes. when the
I am looking at a Ruud furnace Model ugra06emaes. when the unit first Powers up there is a five-second delay the combustion blower starts and 2 seconds later the indoor fan starts and they both contin… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Nordyne M1MB 090A BW Furnace that had a bad
Hello, I have a Nordyne M1MB 090A BW Furnace that had a bad ignightor that was replaced two years ago with a universal type unit. It went out again yesterday and I replaced it again with another unive… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rick I talk to you this morning about the lennox heater
Rick I talk to you this morning about the lennox heater burners turning on for a few seconds and then shutting down, I try a new board and did not fix the problem any suggestions?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a G60UHV-36B-090-02 when i Start the heat cycle, it
I have a G60UHV-36B-090-02 when i Start the heat cycle, it ignites and the heater blower runs, but after the unit fires the heater and supposed to start the main blower, the main blower only runs in s… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I HAVE A LENNOX G26 PUT IN 1997 BURNERS KICK ON RUNS FOR
I HAVE A LENNOX G26 PUT IN 1997 BURNERS KICK ON RUNS WHILE SHUTS DOWN NO BLOWER COMES ON REPLACED MOTOR LAST YEAR REPLACED FLAME SENSOR WITH GENARIC ONE… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an American Std UY120R9V5V . The zone controller is
I have an American Std UY120R9V5V . The zone controller is calling for heat, but there is no ignition or blower activity. The vent fan runs continuously which is not normal. It was running fine yester… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox slv98 furnace. Last night it would not run
I have a lennox slv98 furnace. Last night it would not run and gave the error code E210 - No communication with blower. Afrer powering on and off a number of times and finally banging around a little … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a coleman evcon furnace modal #dgat070bdd with the deluxe
I have a coleman evcon furnace modal #dgat070bdd with the deluxe blend air II. The problem I'm having is when the thermostat calls for heat most times it will not stay lit. The igniter glows for about… read more
hvacdave84
hvacdave84
53 satisfied customers
I have a Lennox G32V5 about 10 years old. No heat this morning
I have a Lennox G32V5 about 10 years old. No heat this morning so I went to check on it. Set the thermostat to call for heat. Furnace started up, induction fan started, flame started, but the fan woul… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Lennox LF24 garage heater that attempts to start up
I have a Lennox LF24 garage heater that attempts to start up but quits. LED flashes 2 times. Gas and power are fine.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Could somebody help with RUUD Gas/Electric package rooftop
Could somebody help with RUUD Gas/Electric package rooftop unit? The 4 units SKNL-B150NL21 with the same symptom: - Thermostat calls for heat - One Inducer starts purge - After 30 seconds igniter come… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Lennox G26Q4/5-100 furnace. Burners are not starting
I have a Lennox G26Q4/5-100 furnace. Burners are not starting at times and turn off during heat demand on other occations. If the induction blower starts on heat demand the burners will light. If the … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
A repair tech just told me that I need to have the blower motor
A repair tech just told me that I need to have the blower motor replaced in my g32v5-125-1. Is this a normal repair/replace for a 10 yr old system? What motor is in it (HP/model)? They quoted ~$1150 f… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I HAD A LENNOX PULSE 21 MODEL G21Q3-80-1 INSTALLED IN 1994
I HAD A LENNOX PULSE 21 MODEL G21Q3-80-1 INSTALLED IN 1994 AND EVER SINCE IT WAS INSTALLED, THE FURNACE WILL IGNITE FOR A FEW SECONDS AND THEN QUIT. IT DOES THIS ABOUT THREE TO FIVE TIMES BEFORE IGNIT… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,880 satisfied customers
I have a Lennox Innovator Series furnace model G32Q3-75-2.
I have a Lennox Innovator Series furnace model G32Q3-75-2. Here in the midst of the Chicago blizzard, it has stopped producing heat. Power to the furnace is fine as is the thermostat. I have checked b… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Lennox 80MGF 4/5-120A-1 furnace. Same symptoms as
I have a Lennox 80MGF 4/5-120A-1 furnace. Same symptoms as asked back 300 days ago by a different customer. Just need a little help with diagnosis. I'm able to troubleshoot with you. I have a Lennox M… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I had a question about the differance between a ignition control
I had a question about the differance between a ignition control module and a control board on a residential furnace, what application does a module serve and what tpe of furnaces are they used on?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x