I have a Goodman 100-4. Igniter lit no burner. Replaced

Customer Question
I have a Goodman...

I have a Goodman 100-4. Igniter lit no burner. Replaced board and transformer. Ran ok for six hours. Now back to original issue

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About two weeks since heat needed noticed ignition light but that’s all after one use. Replacing parts got it working fine again only for a few hours then back to only igniter going through 3 cycles and resetting. Just like before no 24v to valve

Contractor's Assistant: Have you tried power cycling the appliance -- unplugging it and leaving it off for a few hours?

Yes

Contractor's Assistant: Do you plan on doing the work yourself?

I have done all the troubleshooting and part replacement myself. Thought I had it fixed but back to original issue. I am about ready to give up and call pro tech.

Contractor's Assistant: Anything else we should know to help you best?

It is about 13 years old and first problem. AC side works fine. Blew out burner tubes. Heat exchanger and new filter.

Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/3/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 9 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,175
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

Is this a GMP or GMPN?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
GMPN
Customer reply replied 9 months ago
I did ohm test on rollout switches, tested pv switch and thermostat before replacing board and transformer. It then would fire up but cut off once the blower started up. According to the new board instructions it said if this occurred switch 24v leads. Once that was done it worked as expected for about 6 hours and a few on and off cycles. It then went back to the original problem. I swapped out the old board and no change. Could there be some reason the board would go bad or be fried that quickly?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 9 months ago

in the same series as the gas valve....meaning once power is sent to gas valve it must cross a couple "bridges"...

Do you know if your unit has an auxiliary limit? If you trace the 24v wire backwards from the gas valve does it go to a limit in the blower section?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
The gas valve blue wire traces back to the 24v pigtail that includes the ground and into the board at pin #6 on the nine pin connector. I have jumped both the limit, pv and burner box switches at times during my initial system checks and all switches work. As I said earlier replacing the board and transformer got the system working so all paths thru the switches are good. It is after running it went back to the original status of three times trying to get burner to light then flashing one on the board. This is because there is no 24v trigger from the board to allow a voltage path to the gas valve to get initial ignition. I am sure that something has damaged the board or transformer as I have 120v ac into transformer but never see the 24v on the other side of the transformer, at the gas valve or at pins # 3 and 6 of the nine pin connector. If one of the switches was opening after a few cycles off heat on and off my jumping them should allow the system to run at least for awhile. Is there something that would take out the board after so short a time?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 9 months ago

If no 24 on 3 and 6 then the transformer is bad. This can be because of any short in the low voltage circuit.

A transformer can run hot with a partial short to ground, bad gas valve etc. After cooling down it can work until eventually burns out. Is there a fuse on the board (yellow 5 amp)?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
There is a yellow 3 amp fuse but it is not blown. The transformer they sent me was a 120/240v ac where you pick the common and 120 or 240 voltage pin. It was hot to the touch when I went down to trouble shoot this morning. I will pickup a 120v only transformer tomorrow and see if that works. If it does is the a way to test load on the transformer while running or a way to see load on gas valve to detect a short? I maybe at the point of local help if a different transformer does not get me back up. I don't just want to replace t formers and boards a few more times.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 9 months ago

Some transformers you have to watch how they wire...especially multitap...we are trained to think black as power...but the transformers (some) use black as common...

If you get a multitap just watch how it is wired..

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a rudd deluxe 90 plus furnace (ugeb-06ec-fs) and the
i have a rudd deluxe 90 plus furnace (ugeb-06ec-fs) and the pilot lights but the burners never ignite. I was told it might be the flame sensor so I purchased one but i cannot locate the part on the fu… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have replaced both the pilot assembly and the S6810U
we have replaced both the pilot assembly and the S6810U controller, the pilot lights, we have 24v in all the appropriate places, but the main burner never lights… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,175 satisfied customers
My Series '2A' Burnham Low Pressure Boiler is having trouble
My Series '2A' Burnham Low Pressure Boiler is having trouble igniting. I hear it 'click' every couple seconds, and I see a flame for a split second, but it won't start the burners. It worked for about… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Rheem mod.# rgla 100A-AR. The pilot lite is lit and
I have a Rheem mod.# ***** 100A-AR. The pilot lite is lit and when I turn the thermostat up the fan goes on but the burners do not lite.Can you help me… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a goodman condenser unit that keeps blowing my transformer.
I have a goodman condenser unit that keeps blowing my transformer. I clipped a burned wire on the 240v going into the contactor from the disconnect because it kept tripping my breaker. Now my transfor… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,175 satisfied customers
HI KEN I think I blew the transformer on my AC units (3) when
HI KEN I think I blew the transformer on my AC units (3) when changing stats. they are the new wifi honeywells. 2 were working fine for a while. When I changed the 3rd, I got no power. I switched them… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My Coleman Evcon furnace keeps giving me ignition failure code.
My Coleman Evcon furnace keeps giving me ignition failure code. Technician replaced the board and the flame sensor 2 days ago and the problem persists. Today, a couple of times the ignitor glowed but … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have replaced the mother board and the heat igniter. I have
I have replaced the mother board and the heat igniter. I have checked transformer-24v. The vent fan comes on when the thermostat calls for heat and then the igniter comes on. No propane to light! I tr… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My friend has an Armstrong furnace that will not light. The
My friend has an Armstrong furnace that will not light. The pilot light is on but it won't ignite the burners...what could cause that?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I Have a goodman GMNT100-4B that wont ignite. Ignitor glows
I Have a goodman GMNT100-4B that won't ignite. Ignitor glows but no gas valve opening. I've test all switches and have max .5 ohms through each. I have 24v to the pressure switch and continuity throug… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hi, I have an older (maybe 20 year old now) Rheem Criterion
Hi, I have an older (maybe 20 year old now) Rheem Criterion heat-cool unit, circuit drawing number 90-22886-01 rev 18, and has been working fine until the other day. When I got into the IIBC box and f… read more
R G
R G
44 satisfied customers
I cleaned some soot from my ducts , from the chimney and into
I cleaned some soot from my ducts , from the chimney and into the heating unit, after smelling soot as my heat want on. Now, my heat will come on, but, the blower will only come on for 30 seconds or l… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an older HQCO furnace that ignites fine, will heat the
I have an older HQCO furnace that ignites fine, will heat the air in the chamber for a minute and the shuts down the second the blower comes on. The blower will then stop once the heated air is distri… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Bryant gas furnace - burners ignite for about 4 seconds then
Bryant gas furnace - burners ignite for about 4 seconds then go out, repeats about every 10-15 seconds. The blower never comes on. Model 394GAW - with electronic ignition (spark). pilot ignites fine a… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,175 satisfied customers
TRANE XR90 NO POWER CHECKED WITH VOLT METER... NATA...MAIN
TRANE XR90 NO POWER CHECKED WITH VOLT METER... NATA...MAIN BOARD NO POWER... RELAY BAD??? FUSE OK...I PUT NEW SERVICE IN 5 MONTHS AGO... LOOKS LIKE I BLEW BOARD.. YES??? BOARD # XXXXX… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Goodman Furnace GMNT-040-3 When the Power first is
I have a Goodman Furnace GMNT-040-3 When the Power first is reset. The gas ignites and looks OK. after about 30-45 seconds the gas shuts off and the flame dies. The trouble shooting light blinks once … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Model RCDC10NCBJR Forced Air Unit in my home. REcently
I have a Model RCDC10NCBJR Forced Air Unit in my home. REcently I had a electrical Utility issue where the incoming power 'single phased" so there was only 240volts to all circuits. The Utility Compan… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,175 satisfied customers
I have a goodman furnace from 1989 and it just stopped working.
I have a goodman furnace from 1989 and it just stopped working. when you comand the heat on the pilot clicks on and lights the pilot nothing else happens help… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question