I have a Goodman 100-4. Igniter lit no burner. Replaced board and transformer. Ran ok for six hours. Now back to original issue

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About two weeks since heat needed noticed ignition light but that’s all after one use. Replacing parts got it working fine again only for a few hours then back to only igniter going through 3 cycles and resetting. Just like before no 24v to valve

Contractor's Assistant: Have you tried power cycling the appliance -- unplugging it and leaving it off for a few hours?

Yes

Contractor's Assistant: Do you plan on doing the work yourself?

I have done all the troubleshooting and part replacement myself. Thought I had it fixed but back to original issue. I am about ready to give up and call pro tech.

Contractor's Assistant: Anything else we should know to help you best?

It is about 13 years old and first problem. AC side works fine. Blew out burner tubes. Heat exchanger and new filter.

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/3/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,998
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

Is this a GMP or GMPN?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
GMPN
Customer reply replied 4 months ago
I did ohm test on rollout switches, tested pv switch and thermostat before replacing board and transformer. It then would fire up but cut off once the blower started up. According to the new board instructions it said if this occurred switch 24v leads. Once that was done it worked as expected for about 6 hours and a few on and off cycles. It then went back to the original problem. I swapped out the old board and no change. Could there be some reason the board would go bad or be fried that quickly?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago

in the same series as the gas valve....meaning once power is sent to gas valve it must cross a couple "bridges"...

Do you know if your unit has an auxiliary limit? If you trace the 24v wire backwards from the gas valve does it go to a limit in the blower section?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
The gas valve blue wire traces back to the 24v pigtail that includes the ground and into the board at pin #6 on the nine pin connector. I have jumped both the limit, pv and burner box switches at times during my initial system checks and all switches work. As I said earlier replacing the board and transformer got the system working so all paths thru the switches are good. It is after running it went back to the original status of three times trying to get burner to light then flashing one on the board. This is because there is no 24v trigger from the board to allow a voltage path to the gas valve to get initial ignition. I am sure that something has damaged the board or transformer as I have 120v ac into transformer but never see the 24v on the other side of the transformer, at the gas valve or at pins # 3 and 6 of the nine pin connector. If one of the switches was opening after a few cycles off heat on and off my jumping them should allow the system to run at least for awhile. Is there something that would take out the board after so short a time?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago

If no 24 on 3 and 6 then the transformer is bad. This can be because of any short in the low voltage circuit.

A transformer can run hot with a partial short to ground, bad gas valve etc. After cooling down it can work until eventually burns out. Is there a fuse on the board (yellow 5 amp)?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
There is a yellow 3 amp fuse but it is not blown. The transformer they sent me was a 120/240v ac where you pick the common and 120 or 240 voltage pin. It was hot to the touch when I went down to trouble shoot this morning. I will pickup a 120v only transformer tomorrow and see if that works. If it does is the a way to test load on the transformer while running or a way to see load on gas valve to detect a short? I maybe at the point of local help if a different transformer does not get me back up. I don't just want to replace t formers and boards a few more times.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago

Some transformers you have to watch how they wire...especially multitap...we are trained to think black as power...but the transformers (some) use black as common...

If you get a multitap just watch how it is wired..

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My unit seems to be short cycling, and the temperature
My unit seems to be short cycling, and the temperature sensor on the unit in the attic has a high temperature light on. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How to clean heat exchanger coils, filters have been clean
filters have been clean recently and I am getting an airflow alarm on the thermostat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
277 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,998 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Funky smell coming from heat exchanger outside...... repair
funky smell coming from heat exchanger outside...... repair guy said the gas not m ixing with the air properly..true? said probably just clogged … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,998 satisfied customers
Heat exchanger is a month old and heat stopped working.
Heat exchanger is a month old and heat stopped working. Three lights are blinking saying it is a limit or rollout switch … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
I have a property with a Keeprite heat exchanger installed.
I have a property with a Keeprite heat exchanger installed. I believe the filter is clogged but I don't know where it's located. The model is PGF018K040E … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
How can I clean the inside of the heat exchanger on my
how can I clean the inside of the heat exchanger on my furnace? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier heating heat exchanger is plugged. I understand
My carrier heating heat exchanger is plugged. I understand it is civered under a recall action. if bI purchase a new systeem 59mn7a080-20 what price drduction do I receive? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How much time should be allowed to change a heat exchanger
How much time should be allowed to change a heat exchanger for a 48tjf016 series 580ba and 2 men?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
I was looking into a trane tud060 heat exchanger and noticed
I was looking into a trane tud060 heat exchanger and noticed a buildup of white powder at one of the factory seams and need to know what is causing this. I attached a pic. Thanks… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,998 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x