I have a utica hot water gas boiler that has a pilot light…

Customer Question
I have a utica...

I have a utica hot water gas boiler that has a pilot light and some new parts such as a pilot ignitor, thermocouple and now a new aquastat l8148e 1265. My issue is boiler will not fire up. It only does when i jump power 24 volts from aqua stat to gas valve

Contractor's Assistant: How long has this been going on? And how severe is the problem?

Started after install of aquastat.

Contractor's Assistant: Do you plan on doing the work yourself?

We already did. The problem seems to be the power output for the gas. It keeps moving from 12 to 24 volts

Contractor's Assistant: Anything else we should know to help you best?

If we switch to a different power supyly it fires right up.

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
12/2/2017
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,784
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation. What's the model number of your unit?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Aquastat L8148E
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

That's the aquastat relay not the boiler model. The boiler model is on the rating tag which also has the BTU input

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Utica Gas boiler Model MGB150HD
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

Ok, give me a few to pull the specs.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

Ok, do you have 24 volts at B1 & B2 on the L8148?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
23 vac
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

Ok which terminals at the gas valve are you probing? Is the pilot lit. I'm assuming you have electronic ignition.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I took off the plugs at the gas and metered there. Pilot is lite. If i switch to diffrent power supply it fires up.
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

You didn't answer my questions. Which terminals? elctronic ignition?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
TH/TR manual ignition
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

Then if you have 24 volts at B1 & B2 but not at the gas valve jump out the flame rollout switch just above the burners, it has 2 wires attached. If the unit doesn't respond then jump out the blocked vent switch which is under the draft diverter (the open box below the damper.) Either one of these devices is faulty or you have a bad connection between the gas valve and the L8148

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I think it a bad Aquastsat. If i remove the power output wires from the Aquastat and hook up an external 24vac power supply the unit fires up.
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

Not a bad aquastat if you have 23/24 volts at B1 & B2. You have to check what I described in my last post.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
The external power supply actually outputs 26 volts and this appears to make the difference to open the gas valve and fire up the boiler
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

The gas valve will open at volatges as low as 20 volts.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
ok i will try jumping both switches one at a time
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

No 1 at a time or you won't know which is bad if that's the problem.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Bypassed switches 1 at a time and unit did not fire.
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

Then you have a bad connection between B1 & the gas valve. You can verify this by disconnecting the lead at B1 and run a line diret from B1 to the gas valve. Wiring diagram shows B1 connects to TR gas valve terminal. Double check to be sure. Those switches are in series between B1 & the valve TR

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ran new wires and still same issue.
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

Check B2 rewire if necessary. The only explanation for a volatge drop between B1 & B2 and the gas valve is a bad connection.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ran new wires to both. We just tried the different power supply again and it fired up.
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

Then what you're telling me doesn't add up. 23 volts at B1 & B2 and all new direct wiring to gas valve the gas valve should open. What do you read at the gas valve end of the new B1 & B2 leads?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
If connected 0. Disconnect and test wire directly 23vac
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

not possible, you don't lose the voltage if you conect the leads

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I can only tell you what i am seeing. But that is what is happening.
HVAC Technician: Rick, HVAC Supervisor replied 4 months ago

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Munchkin boiler not firing. Goes through blower cycle and
Munchkin boiler not firing. Goes through blower cycle and stope with water temp on doisplay. No error codes reported. Unplugged all sensors one at a time and made sure proper error code reported. Al f… read more
Bill
Bill
Service Mgr
82 satisfied customers
I have a Crown wall hung boiler with a Wilocirculator that
I have a Crown wall hung boiler with a Wilo(###) ###-####circulator that has failed. would like to buy just motor cartridge if possible. is there a part number for that , or what other model pump woul… read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
I need a blower for a Burnam Alpine boiler. It seems to be
I need a blower for a Burnam Alpine boiler. It seems to be discontinued. Can you advise? … read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
Regarding steam boilers wiring to pressure controls and
Regarding steam boilers wiring to pressure controls and switches … read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
Having a problem with my Weil Mclain boiler. It's hot but no
having a problem with my Weil Mclain boiler. It's hot but no heat to radiators … read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
140M boiler goes to F09 the ignitor was replaced. Does the
140M boiler goes to F09 the ignitor was replaced. Does the rectifier need to be replaced too? … read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
Buderus GB142 wall hung boiler with in concrete floor
Buderus GB142 wall hung boiler with in concrete floor radiant heat. Boiler Temp is set at 135, the attached AM10 has the target temp point set at 135 as well and the base temp point at 110. On cold da… read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
I have a Lochinvar boiler that is not running. Sticker on
I have a Lochinvar boiler that is not running. Sticker on panel says do the reset switch but I can't find the reset switch. Where is it? … read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
My boiler is not lighting. I can see that the pilot is
My boiler is not lighting. I can see that the pilot is burning. I have tried switching power off, and the system makes a noise like it is trying to light but does not. Noticed this this am as I was ch… read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
I have a burnham boiler date on it is 2006, no sign of
I have a burnham boiler date on it is 2006, no sign of leakage but need to fill every 3-4 days. … read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
My boiler has leak at the top... is that possible to fix
Hi.. my boiler has leak at the top... is that possible to fix this or better cal to the local HVAC specialist..?… read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
I have a cg5 boiler for my home. The boiler ignites and runs
I have a cg5 boiler for my home. The boiler ignites and runs for 10 seconds or so, turns off for 1 or 2 seconds and then reignites, that happens over and over again for 30 minutes or so and then shuts… read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
Crown boiler model # AWI128SNSTPSU NATURAL GAS. Boiler shut
Boiler shut down last night , how do I relight it ? … read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
EcoTecplus 428 boiler,after reset boiler not coming on,but
ecoTecplus 428 boiler,after reset boiler not coming on,but pcb has power. … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
Can you refer me to a Weill McLain boiler repairman? Boiler
Can you refer me to a Weill McLain boiler repairman? … read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
Im getting an error code #65 on my pennco boiler. Boiler.
im getting an error code #65 on my pennco boiler JA: What device or product does this involve? Customer: boiler JA: What's the brand and model of your product? Customer: pennco JA: What have you tried… read more
David Bowden
David Bowden
Owner
760 satisfied customers
My crown boiler boiler model no. AWR070ENST2PSU runs for a
My crown boiler boiler model no. AWR070ENST2PSU runs for a short time, shuts down, then takes a long time on start running again. We change the control. the pump, and the gas valve, Don't appears to h… read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick
Rick
HVAC Supervisor
23,784 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x