I have a utica hot water gas boiler that has a pilot light…

Customer Question
I have a utica...

I have a utica hot water gas boiler that has a pilot light and some new parts such as a pilot ignitor, thermocouple and now a new aquastat l8148e 1265. My issue is boiler will not fire up. It only does when i jump power 24 volts from aqua stat to gas valve

Contractor's Assistant: How long has this been going on? And how severe is the problem?

Started after install of aquastat.

Contractor's Assistant: Do you plan on doing the work yourself?

We already did. The problem seems to be the power output for the gas. It keeps moving from 12 to 24 volts

Contractor's Assistant: Anything else we should know to help you best?

If we switch to a different power supyly it fires right up.

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
12/2/2017
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,378
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation. What's the model number of your unit?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Aquastat L8148E
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

That's the aquastat relay not the boiler model. The boiler model is on the rating tag which also has the BTU input

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Utica Gas boiler Model MGB150HD
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Ok, give me a few to pull the specs.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Ok, do you have 24 volts at B1 & B2 on the L8148?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
23 vac
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Ok which terminals at the gas valve are you probing? Is the pilot lit. I'm assuming you have electronic ignition.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I took off the plugs at the gas and metered there. Pilot is lite. If i switch to diffrent power supply it fires up.
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

You didn't answer my questions. Which terminals? elctronic ignition?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
TH/TR manual ignition
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Then if you have 24 volts at B1 & B2 but not at the gas valve jump out the flame rollout switch just above the burners, it has 2 wires attached. If the unit doesn't respond then jump out the blocked vent switch which is under the draft diverter (the open box below the damper.) Either one of these devices is faulty or you have a bad connection between the gas valve and the L8148

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I think it a bad Aquastsat. If i remove the power output wires from the Aquastat and hook up an external 24vac power supply the unit fires up.
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Not a bad aquastat if you have 23/24 volts at B1 & B2. You have to check what I described in my last post.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The external power supply actually outputs 26 volts and this appears to make the difference to open the gas valve and fire up the boiler
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

The gas valve will open at volatges as low as 20 volts.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
ok i will try jumping both switches one at a time
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

No 1 at a time or you won't know which is bad if that's the problem.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Bypassed switches 1 at a time and unit did not fire.
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Then you have a bad connection between B1 & the gas valve. You can verify this by disconnecting the lead at B1 and run a line diret from B1 to the gas valve. Wiring diagram shows B1 connects to TR gas valve terminal. Double check to be sure. Those switches are in series between B1 & the valve TR

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ran new wires and still same issue.
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Check B2 rewire if necessary. The only explanation for a volatge drop between B1 & B2 and the gas valve is a bad connection.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ran new wires to both. We just tried the different power supply again and it fired up.
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Then what you're telling me doesn't add up. 23 volts at B1 & B2 and all new direct wiring to gas valve the gas valve should open. What do you read at the gas valve end of the new B1 & B2 leads?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
If connected 0. Disconnect and test wire directly 23vac
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

not possible, you don't lose the voltage if you conect the leads

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I can only tell you what i am seeing. But that is what is happening.
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Taco SR503-EXP, 3 Zone Switching Relay with
I have a Taco SR503-EXP, 3 Zone Switching Relay with Domestic Hot Water Priority which is blowing the 1Amp Fuse on it's control board. My boiler is a Burnham V8 oil fired with a Burnham Indirect Water… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
My l8148e acquastat won't work, Now, If possible, No
My l8148e acquastat won't work JA: I'll do all I can to help. How long have you been dealing with this? Customer: Now JA: Do you plan on doing the work yourself? Customer: If possible JA: Anything els… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Repco boiler wont turn on when I put the aquastat on auto
I am looking at a Repco LA75C boiler. When I put the aquastat on auto the boiler will not turn on. It turns on when I put it on manual. I changed the thermostat and it is still doing the same thing. W… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Need help wiring a honeywell L6006 aquastat, the boiler
need help wiring a honeywell L6006 aquastat, the boiler control, circ pump, and tstat to a honeywell RA832A relay … read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Phil, I have an old "national US radiator" boiler. I have
Hi Phil, I have an old "national US radiator" boiler. I have replaced the gas valve and the thermocouple, but the pilot light keeps going out. Any ideas on what may be the cause?… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
HAVE A UTICA BOILER, TRIED TO FIRE IT FOR THE FIRST TIME THIS
HAVE A UTICA BOILER, TRIED TO FIRE IT FOR THE FIRST TIME THIS YEAR. THERMOSTAT IS WORKING, WATER CIRCULATOR IS ACTIVATING, PILOT ON. GET 24 VOLTS AT HONEYWELL SWITCH, NO VOLTAGE AT GAS VALVE.… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Hi, I need a replacement for an WR Aquastat: 8E42A:6 for a
Hi, I need a replacement for an WR Aquastat: 8E42A:6 for a residential boiler. Is there a cross reference replacement? thanks… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
what is the correct aquastat replacement for a Honeywell L8148E
what is the correct aquastat replacement for a Honeywell L8148E 1000-1 for a HB Smith g200 gas boiler?… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have an older Gas fired boiler. When I attempted to get the
I have an older Gas fired boiler. When I attempted to get the system started, I lit the pilot, then turned the electricity on to the system. The circulating pump started immediately, but the furnace n… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I need help wiring an Aquastat L8148A controller. w/ Bonus
I need help wiring an Aquastat L8148A controller. w/ Bonus Another Just Answer expert helped me Friday to diagnose a possibly bad Aquastat. I decided to pick up a new Aquastat as it appeared the origi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Why we we have 24V coming in and only 12v coming out going
Why we we have 24V coming in and only 12v coming out going to the gas valve? All wire continuity checks out --- all connections are correct… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have a Utica series M-AGB natural gas fired boiler with a
I have a Utica series M-AGB natural gas fired boiler with a aquastat relay L8148E. the circulator pump is running All thermostats are set for heat, but the main burner does not light. Replaced the the… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
HI I have a Model MGB75HID Utica boiler ( Ser# DV07021 )that
HI I have a Model MGB75HID Utica boiler ( Ser# XXXXX )that I need a aquastat for. The honeywell model number that is on the stat is L8148e-1257. But I have odered 2 of these from a local company and n… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
replacing 2-wire to 3-wire type 1311 zone white-rodgers. Stat
replacing 2-wire to 3-wire type 1311 zone white-rodgers. Stat will open and close on demand ,but will not fire gas hot water boiler.I have 24 volt at aquastat model L8148e 1265… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Slant Fin S-90 DP Erratic boiler firing First The boiler
Slant Fin S-90 DP Erratic boiler firing? First The boiler can be jumped started by turining off the power supply and turning down the aqua stat. Return power to boiler switch the aqua state up to 180 … read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Pilot is lit, but when thermostat is turned on nothing else
Pilot is lit, but when thermostat is turned on nothing else happens. I've had the low water cut-off replaced and now it doesn't seem to fire up anymore. What could be possible problems? Boiler Model# … read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
My steam boiler from time to time doesnt kick in. I have replaced
My steam boiler from time to time doesnt kick in. I have replaced the thermostat twice with the same results. It works fine for a couple days then wont kick in. For me to get it to kick in i need to l… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have an American Standard Empire 4-GA-E gas fired boiler.
I have an American Standard Empire 4-GA-E gas fired boiler. Can't get the burners to fire. I tried to manually actuate the Detroit Lubricator V-574 to no avail. Is there a way to test this valve or th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x