I have a 25 year old Lennox gas heat system. It has worked great until now. It runs fine for two/three nights and the it just dies not turn on. I turn the system off via the thermostat and the flip the breaker. After 20 seconds I turn it back on and the system is fine again fir 2/3 nights. Any ideas????
Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
12/2/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,713
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Do you have a battery powered thermostat?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The battery is only for the backlight. I have replaced the batteries and tried a new thermostat as well.
Customer reply replied 7 months ago
Thanks for the heads up on the call offer!!!!
Customer reply replied 7 months ago
Air intake is clear and the condensate line is flowing. I tried to think of items that would cause a safety shut off.
Customer reply replied 7 months ago
Only other thing I can imagine is a flame detector or circuit board.
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Was a safety limit shut off?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I don’t know how to tell.
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

DOes it doe anything at all?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Lennox furnace is showing ‘system is waiting' on thermostat.
Lennox furnace is showing ‘system is waiting' on thermostat. HVAC Company was called and came out earlier today (this was after I ‘reset' the furnace via the circuit breaker and everything was working… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My boiler short cycles about two times before going through
Hello, my boiler short cycles about two times before going through a complete heating cycle. What's causing my propblem?… read more
Rick
Rick
Supervisor
24,242 satisfied customers
Have 2000 90i series HVAC. Fan running but lost heat on very
Have 2000 Bryant 90i series HVAC. Fan running but lost heat on very cold day in Boston. Getting LED light error message three green three red. Tried turning on and off by switch does not start up flam… read more
Tim Ohms
Tim Ohms
HVAC Journeyman
31 satisfied customers
I have an AS Freedom90 that was installed without intake
I have an AS Freedom90 that was installed without intake filters about 7 years ago. This year I figured out how to put a 16x20 filter in the opening and have had some ignition failures. I had a tech c… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
My Lennox Heat Pump M/N LPS13DC-024-230-01 is four years old.
My Lennox Heat Pump M/N LPS13DC-024-230-01 is four years old. It replaced a 9 year old Lennox whose compressor died. I have electric auxiliary heat. This winter when the temperature went to single dig… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have Carrier WeatherMaker 8000 gas furnace, which does not
I have Carrier WeatherMaker 8000 gas furnace, which does not have a pilot. The furnace was working until last night, and died around 8pm. The only thing that I can think of is that we had a new oven i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox model #HP26-030-7P. the power to the furnace
I have a Lennox model #HP26-030-7P. the power to the furnace was turned off while it was running - when i turned it back on it wouldn't run. The "pump" light is on the thermostat is on.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Lennox G51 series that is not lighting properly.
I have a Lennox G51 series that is not lighting properly. If I set the temp to 68 or above, it runs fine. If I lower the temp (i.e. when away or on my downstairs unit over night) then the igniter won'… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
I have a Goodman 13 Seer gas heat/A/c system (GasPack) on the
I have a Goodman 13 Seer gas heat/A/c system (GasPack) on the roof of our home. I had the unit serviced about 2 weeks ago and he said everything looked great/was running fine that day. Today it is fin… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Lennox high eff. Model g26 gas furnace 11 years old. Problem..unit
Lennox high eff. Model g26 gas furnace 11 years old. Problem..unit not running...no heat Action: - turned everythinh off (power & gas) - waited 20 minutes turned everything back on....nothing happened… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
I have an older Trane heat pump, the outside and inside units
I have an older Trane heat pump, the outside and inside units run all the time. The thermostat has two aneroid tubes in it(baystat thermostat). the top one controls the fan motor and heat pump, the lo… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a Lennox GSR14(about 20 years old) pulse furnace. Either
I have a Lennox GSR14(about 20 years old) pulse furnace. Either the spark is not sparking, or the power module to fire the ignitor is not working. When the furnace starts, I can hear the cold air moto… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I have an old American Standard Gas Boiler with Bell & Gossett
I have an old American Standard Gas Boiler with Bell & Gossett circulator pump and 3 zone valves. Boiler provides great heat 98% of the time, until the outside temperature drops and we have the coldes… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Just got home and my upstairs Heat is not working. I just
Just got home and my upstairs Heat is not working. I just had the thermostat replaced by a technician about 3 months ago. Model is White Rodgers 1F82-261. When we left the unit was working fine. We le… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
We live in Florida and have a Trane 3.5 ton unit that weve
We live in Florida and have a Trane 3.5 ton unit that we've had for approx. 6 years and has worked absolutely fine. For the past few weeks, when we use our heat on very cold nights, our heat will kick… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
i have an affinty heat pump / furnace. I just had the windows
i have an affinty heat pump / furnace. I just had the windows open to air out the house and turned the thermostat down so the heat wouldn't run while the windows were open. Closed up the windows and t… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
I ran the A/C for a few minutes last night and then switched
I ran the A/C for a few minutes last night and then switched back to heat. When I woke up this morning, the house was too cool and I can't get either the heat or A/C to work. I can't even get the fan … read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
We have Lennox furnace and heat pump, runs even when not cold outside?
We have a Lennox furnace and heat pump -- when we turned on the heat for the winter we noticed that the furnace runs with the heat pump even when the outside temperature is not very cold. Any advise?… read more
Jack Walker
Jack Walker
President
Vocational, Technical or Trade Scho
6 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x