I have a Good man GKS90 about 8 years old. I replaced a bad main control board (no power) Now I have power, solid red light/no error code.My blower just won't turn on, no heat. When I turn it on, I can hear a click/buzz but nothing else. Blower cage turns freely and it's getting power. I also replaced the blower capacitor. Same symptoms. Bypassing the thermostat doesn't help.
What next?
Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 40 minutes by:
11/30/2017
HVAC Technician: airheatman, HVAC Technician replied 4 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,977
Experience: Furnace, A/C and heat pump specialist.
Verified

Does control board have HEAT COOL and UNUSED terminals where motor wires connect?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
No AC, so there are two connected wires then a jumper wire. Motor is getting power....I'll double check when I get home.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

If the board is sending power to motor white to neutral and either black, blue orange or red to the jumpered heat/cool terminal on board, issue has to be a bad capacitor or bad motor.

If cap checks good (new does not mean good these days) then motor is bad.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
That's the conclusion I already came to. Capacitor is new. Power is going to blower,but I just get a click/buzz.
Blower turns freely. No error codes on board.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Double check wiring and voltage and dif all is good replace motor If you have further questions, please let me know.
Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.
To rate answer, please select one of the stars on the page.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I pretty much concluded it was the blower motor already. Are you going to walk me through replacing that? My furnace isn't fixed...yet.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Sure I will be happy to. I am going to send you a gen***** *****nk that will give you a good idea of exactly how to do.

Also let me know if you need help locating the motor online.

If so give me complete model number on furnace.

https://www.youtube.com/watch?v=xUTvbr1kmDk

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

The video is generic so not exactly like your furnace but will give a very good idea of replacement procedure.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok...i found it unlikely my motor was bad,despite your advice, So I direct wired the blue/heat wire to the door switch and the fan kicked right on. So you were wrong AND you almost cost me an epensive part and lots of labor for no reason.Any ideas before I rate you? Control board is new, no error code. The capacitor and the blower motor are GOOD. I STILL have no fan.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

If you got fan to run by connecting the blue wire, but not with blue connected the the board you DO NOT have 120v coming out of board between neutral and heat terminal; as you say. You told me motor is getting power.If it runs with power from door switch it would run with power from board.Take a picture of the fan wires where they are connected to board.Undoubtly you have something wired incorrectly or you are not reading voltage at correct terminals.

It is a very simple fact that if motor runs with 120v from door switch it has no choice but to run with 120v from board.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

You can attach a picture using the "add file" button

Ask Your Own HVAC Question
Customer reply replied 4 months ago
New board. It was wired exactly like the old board. Blower motor isn't bad, control board isn't bad. Anything else?
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Can you attach a photo of current wiring and show me where you are testing for 120v to motor?

What I am saying is if the board is sending power to the motor as you say, then that is absolutely no difference in the door switch sending power to motor.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Well...the blower motor and capacitor is DEFINITELY operational if I can get it to run independent of the board. As far as I'm concerned that's the only definite I have. Are you now suggesting I have a bad relay or something on the new board. You said blower motor, and it's now something I wired wrong, which didn't happen. No other options you can think of?
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

I am saying the fan has no idea where it is getting power.It runs if it has power and is good.It does not run if it is not getting power.

There is no way motor can run with power from one source but not from another source.

Since you have made motor run by directly connecting to power we know motor is good,

The only thing that would keep a good motor with a good capacitor from running is that it is NOT getting power from the board.

Just because board is new does not mean it is good.

Why are you being defensive and not wanting to send a picture showing me where you are testing for power?

I am not here to argue with you but to help you.

But to say motor is getting power from board but does not work but motor is getting power from door switch does not make sense. I can request a refund of your deposit if you would like rather than keep going back and forth here. Just let me know.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I told you I tested for power. I don't have to PROVE it to you with a picture. You'll have to take my word for it, like I have to take YOUR word even though you would have cost me 150$ and a hour of my labor if I had.Taking a picture while I hold a flashlight two test leads on isn't easy to do. If that's all you have, then yes I'd like a refund.
Customer reply replied 4 months ago
Never mind. I'm calling in s professional to troubleshoot the old fashioned way.
Was this answer helpful?
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,977
8,977 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I want to power a single speed circulator pump from a 120ac
I want to power a single speed circulator pump from a 120ac gfi outlet through a honeywell r8285a control center and a honeywell ct33a thermo- … read more
Dales-Electronic
Dales-Electronic
1,032 satisfied customers
We have a Rheem Model RTGH-95DVLN, it has been in use for 13
We have a Rheem Model RTGH-95DVLN, it has been in use for 13 months with no issues,. the P1 error code was flashing and the burner not firing up. I flushed the system with vinegar and cleaned the smal… read more
canuck the pro
canuck the pro
253 satisfied customers
I have an A.O. 50 gallon natural gas promax hot water
I have an A.O. Smith 50 gallon natural gas promax hot water heater. After running 15 or 20 minutes the gas valve iidicats excessive exhaust back pressure and shut the burner off. I checked the intake … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Honeywell T3 thermostat and a heat pump. The heat
I have a Honeywell T3 thermostat and a heat pump. The heat comes on no matter what the setting is. I need help. … read more
hvacdave84
hvacdave84
53 satisfied customers
How to hook up Honeywell pro 3000 series thermostat to ruud
how to hook up Honeywell pro 3000 series thermostat to ruud rqpm 14 seer 2-4 ton series … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Your answer to my pilot light problem was that my flame
Your answer to my pilot light problem was that my flame sensor rod was dirty. Do I need to remove the burner assembly to clean this rod?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Is this a refrigerant leak on my outdoor a/c unit? When I
Is this a refrigerant leak on my outdoor a/c unit? When I click the thermostat to Cool /Auto the outdoor unit clicks one time and then does nothing (no humming sound or anything)and warm/room temp air… read more
Bill
Bill
Service Mgr
82 satisfied customers
Live in apt bldg. central air Heat pump FHP MFG EC060-1HZC.
Hi. Live in apt bldg. central air Heat pump FHP MFG EC060-1HZC. Had TH8100U1003. Could no longer adjust temp as if right side of screen died. Replaced with RTH8500D. Wired same as old one. Red to R Bl… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Lennox G40UH furnace and there is no power
Hi there! I have a Lennox G40UH furnace and there is no power registering at the thermostat and furnace at this time. I checked the circuit breaker and re-checked the wire connections in the thermosta… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,690 satisfied customers
Do I need an app to my wifi thermostat. Linksys. I can
Do I need an app to my wifi thermostat JA: Who makes your router? Customer: linksys JA: What have you tried so far? Customer: I can connect but not control or program JA: Anything else you want the Ne… read more
Sheri
Sheri
Bachelor\u0027s Degree
413 satisfied customers
I have a 116B and wondering if the nest thermostat is
Hello, I have a Bryant 116B and wondering if the nest thermostat is compatible? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,690 satisfied customers
We have a gas burner that will not run. It fires, rumbles
We have a gas burner that will not run. It fires, rumbles and goes out. We can do this all day. The gas water column is correct. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The furnace is Lenox, Model G20Q3E-75-4, Serial number
The furnace is Lenox, Model G20Q3E-75-4, Serial number 5894M35521. This was in a foreclosed house so I don't know the history. The blower comes on but the burners don't come on.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Blower Motor runs all the time even when thermostat is set
Blower Motor runs all the time even when thermostat is set above/ below set point. Condenser cycles on/off when set point is reached. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Are permanent furnace filters a better option than the one
Are permanent furnace filters a better option than the one you need to replace every 3 months?I have been using the 3M Filtrete filters for a while, but recently I was told that electromagnetic filter… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,690 satisfied customers
Installed TRH3100C per instructions - seems to be OK on heat
installed TRH3100C per instructions - seems to be OK on heat setting, unfortunately I also get heat on the cool setting. Help! … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
My pump has stopped working does it have a reset button. My
Hi My pump has stopped working does it have a reset button … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,690 satisfied customers
I have a Dayton 6K778K motor that acts like the starting
I have a Dayton 6K778K motor that acts like the starting capacitor is out. It will hum when power is applied but when I give it a good spin it kicks off and runs like it should. The motor is less than… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x