We have a Westinghouse/Nordyne FS4BI-036K 23 SEER system and lately at night when it gets colder outside (we are in central Florida) we get the "RSOD" (red screen of death) on the thermostat and low pressure switch fault on the display. Our tech came out a couple of weeks ago and said it was definitely low on freon, injected the sealant/dye into it and it worked for about 10 days or so, but, now the problem is happening again. It will run just fine during the day

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Just reporting what I saw on the thermostat, definitely a problem elsewhere.

Contractor's Assistant: Do you plan on doing the work yourself?

Nope.

Contractor's Assistant: Anything else we should know to help you best?

The unit works during the day when it is warmer outside so in my mind that tells me it isn't a simple low pressure switch failure (because it wouldn't "chose" to only fail at night) and the fact the tech already had to top off freon.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
11/30/2017
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,371
Experience: Furnace, A/C and heat pump specialist.
Verified

If tech did not find and repair leak it is probably low again.Just recharging does nothing but buy time until leak can be found and repaired.

The reason for it only doing it late in the evening or overnight is that the system holds about 10.5 lbs of refrigerant.It is probably only leaking a lb or so when this happens.

During the day with a load on the structure the suction pressure might be borderline but just high enough to prevent lockout, but in the evening when it gets cooler, the load is reduced, thus dropping pressures and allowing low pressure lockout.

This should be a warranty issue and I suggest you demand they locate and repair leak, nt just keep topping it off.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
We have the same unit over at our offices and about 18 months ago it, too, had the same problem. A single visit with the dye/sealant fixed that one and as he said at the time, "Putting in the sealant and the dye will either fix the problem or help me diagnose where the leak is, if it doesn't fix it." That one still works fine.But, this one clearly still has a problem so he is scheduled to come back tomorrow.Over the phone he said it is obviously still leaking, could be a range of things and wouldn't know until he came back.He also surmised that since the house was built in 2002 and originally had an R22 system in it before we upgraded to the Westinghouse in 2008 or so, that if the installers just reused the copper that was there originally that copper could have develope leaks along the lines.I was hoping for some more specific stuff to be armed with when he comes back.(BTW, I do trust him and he has done well by us but I figured it would be nice to have extra info.)
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

I understand. Let me address a couple of the issues.

1. Using the same tubing is fine as long as they flushed it with R11 to remove any mineral oil residue.Not impossible but unlikely for older copper to develope a leak unless rubbing against something.

2.The copper used in these newer units however is almost all imported from China a stress cracks are way to common due to the quality of the material and high operating pressures of the R410A.

3.The dye on rare occassions will seal a leak but not designed to This is one of the drawbacks of the dye is that it can seal small leaks and therefore can also clog up the tiny oriifices in the metering devices.

4.Since he has already added dye, it is also possible that you may no longer have a leak but now are getting a low pressure cut out due to the dye clogging a metering device.However that is not as likely since it only does it when load is reduced at night.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
About 3 feet of the copper tubing is run underground outside (from the compressor to the wall of the house then through the concrete block and up the inside wall of the garage into the attic and about ten more feet to the air handler).The stuff he used (and I read the package stuff while he was using it but can't for the life of me remember the brand) was definitely sealant and dye, not just dye.He said once his dad started using this stuff several years ago their replacement of coils and other stuff went down drastically but they were fine with that since customers loved the lower repair cost (and that was our experience at our offices as I mentioned).Since (relatively speaking) AC systems are pretty simple (compressor outside, tubing running to coil inside and then the coil itself) the leak is "somewhere" (duh!) and the task now will be lighting it up and watching for the glow.I guess I was hoping for something more reassuring like, "Well, most of the time with these sorts of low pressure switch issues, the problem turns out to be... or..."
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

I understand. Just being honest most of the time with these sorts of low pressure issues, the cheap imported crap we are getting dumped on from China is the culprit.

Now it is not out of question that the actual pressure switch could be out of calibration as if you look on these parts you will also see an imported from Mexico or China on them.

To accurately diagnose of course I would have to be onsite with gauges and test equipment and catch the unit in this troublesome mode.

As for the dye/ sealant, I am not knocking your tech as it appears you have a lot of trust in him, but personally only use spectroline bye on which has no sealing properties. The reason is, as stated earlier, if it can seal a leak it can clog a tiny orifice in metering device and cause us to lose a compressor.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
It seems to me that the pressure switch most likely isn't the problem (since I would presume if it was out of calibration it wouldn't have worked after the unit was filled with freon to the proper pressures and worked for 10 days or so and just like prior to "topping off"/"refilling" only have the problems at night now that the problem has come back).I was just in the attic (pull down ladder on this side of the house where the air handler is located) and pulled the "front" off of the air handler.I do have a "party" black light (yeah, I am that old...) and turned off the lights in the attic with that light in one of those protective cages and though with the lights on I did see rust where the galvanized sheet metal met all of the copper tubing of the coil with the lights off and just the black light on I didn't see anything "glowing".I didn't pull the cover off of the "back" side (that is far less accessible and I'll let the HVAC tech do that tomorrow) so, of course, that side could look like a crime scene sprayed with luminol and I just didn't see it since I wasn't looking back there.The fact, also, that the unit still cools during the day is a good sign to me (it was 74 in here before I went into the attic, I cranked it down to 68 and it is now registering 72(At night we keep it at 66 since we are from the midwest and not being able to sleep with the covers on is just not right (that, and my wife is going through "that" phase and meat locker temperatures at night are in order))So, I'll go outside tonight with the black light and nose around the compressor in the dark and see if I see anything.Other than the little bit of black light investigating in the attic I guess I am still no farther along.
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

No without hooking the gauges up we are doing a lot of assuming,but most likely still a small leak somewhere.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,371
9,371 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What couldcause my daughters Trane AC to heat or cool for an
What couldcause my daughters Trane AC to heat or cool for an hour or so, then only blow normal air butthen heat or cool again? … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I've got a lennox elite xp13-030-230-01. just had to have
hi, I've got a lennox elite xp13-030-230-01. just had to have freon added and a leak fixed and two days later the fan motor seized. had been expecting that as it had been screaming (bearing, i think) … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a nordyne iq-drive hvac split system, horizontal install
I have a nordyne iq-drive hvac split system, horizontal install in attic w/ flow to left 4 ton, 23.5 seer, 95.1... variable speed, high efficiency attic C6BH E48C C c6 indoor coil attic FG7TC 100D-VC … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I asked a question before regarding this matter but have more
I asked a question before regarding this matter but have more information now. Here are the facts. I could not get unit below 78F when it was 83F outside after 3 hours. The units were installed in 200… read more
airheatman
airheatman
HVAC Technician
6 years college
9,371 satisfied customers
Hey tim I have a problem with my daughters ac heat pump model
Hey tim I have a problem with my daughters ac heat pump model T3A-024K, it stopped working and I found that the coil was bad I replaced it and it started working when it got hot out but at night when … read more
gmac2905
gmac2905
hvac tech
Vocational, Technical or Trade Scho
18 satisfied customers
I have a Heil pgf024k060a combo ac/gas heat unit. The evaporator
I have a Heil pgf024k060a combo ac/gas heat unit. The evaporator coil froze about a third of the way up from the bottom, and the large line coming from the compressor also froze. I let the unit thaw a… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
We have a LG Multi V - Sync II system that needs to have the
We have a LG Multi V - Sync II system that needs to have the main power turned off and then back on every morning. No exceptions , every day! What could be the reason?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
what causes heat pump to keep continuously turning on and run
what causes heat pump to keep continuously turning on and run for about 15 minutes, then cut off for about 5 minutes, then turning back on and off at about the same intervals... this is a friends heat… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Hello a couple of questions here for a couple of weeks now
Hello a couple of questions here for a couple of weeks now the air blower system in the condo was starting to give meaning the blower would come on for an hour then go off for days and I would turn th… read more
Charles
Charles
Owner
FCC Communication License
738 satisfied customers
Hi Folks I have a Lennox 10ACB 30-11P condesing unit on
Hi Folks: I have a Lennox 10ACB 30-11P condesing unit on a rooftop of an Apartment condo. At the end of last summer, upon return from a vacation, i noticed the unit inside the apartment make clicking … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Ive had three different AC companies come out to service and
Ive had three different AC companies come out to service and check my AC. All have told me everything is working "perfectly". The problem I'm having is that the AC stops cooling around 9-10pm every ni… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
We had a 15 seer goodman/amana installed about 2 months ago.
We had a 15 seer goodman/amana installed about 2 months ago. It seems to be fine when it's not real hot, but around 12:00 to 7:00 it runs constantly and won't cool down to 78, it will go to 79 or 80. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
HVAC high pressure switch keeps tripping. What should I do?
My high pressure button keeps on tripping outside on the condenser unit. What causes this?… read more
Curt Kinder
Curt Kinder
Bachelor's Degree
1 satisfied customers
just had condensing unit installed,11/2 ton unit everything
just had condensing unit installed,11/2 ton unit everything was fine, until a few days after tech came back and said getting some head press. but no suction press. what ever that means… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
our 12 seer heat pump unit is not engaging the heat cycle,
our 12 seer heat pump unit is not engaging the heat cycle, the thermostat is flashing aux heat. what can we do, it is very cold here in cocoa florida… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a trane home heat pump which was originally installed
I have a trane home heat pump which was originally installed in 1988. At that time I had oil furnace as back-up heat instead of electric. In 2007 I converted and had a Trane Air Handler Model TEC3F36A… read more
tom goellner
tom goellner
owner
Vocational, Technical or Trade Scho
1,115 satisfied customers
I have had problems with my AC unit in my condo for a couple
I have had problems with my AC unit in my condo for a couple of years. Each Summer I have to have FREON added because a small undectectable leak. This usally lasts for the summer. Several weeks ago a … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have since a 1 1/2 year an Frigidaire IQ drive A/C seer
We have since a 1 1/2 year an Frigidaire IQ drive A/C seer 23, when ik works it is fantastic, but every time it turns off it says "low gas pressure" and does not start up until I hit the thermostat. O… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x