We have a Westinghouse/Nordyne FS4BI-036K 23 SEER system and…

Customer Question
We have a Westinghouse/Nordyne...

We have a Westinghouse/Nordyne FS4BI-036K 23 SEER system and lately at night when it gets colder outside (we are in central Florida) we get the "RSOD" (red screen of death) on the thermostat and low pressure switch fault on the display. Our tech came out a couple of weeks ago and said it was definitely low on freon, injected the sealant/dye into it and it worked for about 10 days or so, but, now the problem is happening again. It will run just fine during the day

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Just reporting what I saw on the thermostat, definitely a problem elsewhere.

Contractor's Assistant: Do you plan on doing the work yourself?

Nope.

Contractor's Assistant: Anything else we should know to help you best?

The unit works during the day when it is warmer outside so in my mind that tells me it isn't a simple low pressure switch failure (because it wouldn't "chose" to only fail at night) and the fact the tech already had to top off freon.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
11/30/2017
HVAC Technician: airheatman, HVAC Technician replied 6 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,074
Experience: Furnace, A/C and heat pump specialist.
Verified

If tech did not find and repair leak it is probably low again.Just recharging does nothing but buy time until leak can be found and repaired.

The reason for it only doing it late in the evening or overnight is that the system holds about 10.5 lbs of refrigerant.It is probably only leaking a lb or so when this happens.

During the day with a load on the structure the suction pressure might be borderline but just high enough to prevent lockout, but in the evening when it gets cooler, the load is reduced, thus dropping pressures and allowing low pressure lockout.

This should be a warranty issue and I suggest you demand they locate and repair leak, nt just keep topping it off.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
We have the same unit over at our offices and about 18 months ago it, too, had the same problem. A single visit with the dye/sealant fixed that one and as he said at the time, "Putting in the sealant and the dye will either fix the problem or help me diagnose where the leak is, if it doesn't fix it." That one still works fine.But, this one clearly still has a problem so he is scheduled to come back tomorrow.Over the phone he said it is obviously still leaking, could be a range of things and wouldn't know until he came back.He also surmised that since the house was built in 2002 and originally had an R22 system in it before we upgraded to the Westinghouse in 2008 or so, that if the installers just reused the copper that was there originally that copper could have develope leaks along the lines.I was hoping for some more specific stuff to be armed with when he comes back.(BTW, I do trust him and he has done well by us but I figured it would be nice to have extra info.)
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

I understand. Let me address a couple of the issues.

1. Using the same tubing is fine as long as they flushed it with R11 to remove any mineral oil residue.Not impossible but unlikely for older copper to develope a leak unless rubbing against something.

2.The copper used in these newer units however is almost all imported from China a stress cracks are way to common due to the quality of the material and high operating pressures of the R410A.

3.The dye on rare occassions will seal a leak but not designed to This is one of the drawbacks of the dye is that it can seal small leaks and therefore can also clog up the tiny oriifices in the metering devices.

4.Since he has already added dye, it is also possible that you may no longer have a leak but now are getting a low pressure cut out due to the dye clogging a metering device.However that is not as likely since it only does it when load is reduced at night.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
About 3 feet of the copper tubing is run underground outside (from the compressor to the wall of the house then through the concrete block and up the inside wall of the garage into the attic and about ten more feet to the air handler).The stuff he used (and I read the package stuff while he was using it but can't for the life of me remember the brand) was definitely sealant and dye, not just dye.He said once his dad started using this stuff several years ago their replacement of coils and other stuff went down drastically but they were fine with that since customers loved the lower repair cost (and that was our experience at our offices as I mentioned).Since (relatively speaking) AC systems are pretty simple (compressor outside, tubing running to coil inside and then the coil itself) the leak is "somewhere" (duh!) and the task now will be lighting it up and watching for the glow.I guess I was hoping for something more reassuring like, "Well, most of the time with these sorts of low pressure switch issues, the problem turns out to be... or..."
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

I understand. Just being honest most of the time with these sorts of low pressure issues, the cheap imported crap we are getting dumped on from China is the culprit.

Now it is not out of question that the actual pressure switch could be out of calibration as if you look on these parts you will also see an imported from Mexico or China on them.

To accurately diagnose of course I would have to be onsite with gauges and test equipment and catch the unit in this troublesome mode.

As for the dye/ sealant, I am not knocking your tech as it appears you have a lot of trust in him, but personally only use spectroline bye on which has no sealing properties. The reason is, as stated earlier, if it can seal a leak it can clog a tiny orifice in metering device and cause us to lose a compressor.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It seems to me that the pressure switch most likely isn't the problem (since I would presume if it was out of calibration it wouldn't have worked after the unit was filled with freon to the proper pressures and worked for 10 days or so and just like prior to "topping off"/"refilling" only have the problems at night now that the problem has come back).I was just in the attic (pull down ladder on this side of the house where the air handler is located) and pulled the "front" off of the air handler.I do have a "party" black light (yeah, I am that old...) and turned off the lights in the attic with that light in one of those protective cages and though with the lights on I did see rust where the galvanized sheet metal met all of the copper tubing of the coil with the lights off and just the black light on I didn't see anything "glowing".I didn't pull the cover off of the "back" side (that is far less accessible and I'll let the HVAC tech do that tomorrow) so, of course, that side could look like a crime scene sprayed with luminol and I just didn't see it since I wasn't looking back there.The fact, also, that the unit still cools during the day is a good sign to me (it was 74 in here before I went into the attic, I cranked it down to 68 and it is now registering 72(At night we keep it at 66 since we are from the midwest and not being able to sleep with the covers on is just not right (that, and my wife is going through "that" phase and meat locker temperatures at night are in order))So, I'll go outside tonight with the black light and nose around the compressor in the dark and see if I see anything.Other than the little bit of black light investigating in the attic I guess I am still no farther along.
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

No without hooking the gauges up we are doing a lot of assuming,but most likely still a small leak somewhere.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,074
9,074 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What is the nitrogen leak testing pressure for 410A system
what is the nitrogen leak testing pressure for 410A system on new installation… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
what are flashing codes on an york heat pump model e4ts036s06a
what are flashing codes on an york heat pump model e4ts036s06a with white control board part number 031 008 32. code five list of the codes… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hi, I have a 5 ton a/c unit cooling just shy of 2,000 sq ft.
Hi, I have a 5 ton a/c unit cooling just shy of 2,000 sq ft. My air return is built into a sealed box positioned between 2 walls at the bottom of the second floor. The box pulls air from downstairs th… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a 113 condenser and the suction pressure is only 15
I have a bryant 113 condenser and the suction pressure is only 15 psi and the liquid line is 198 #. is there a problem with the txv? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
What is the suction side pressure to be on a MR24C3F it's
What is the suction side pressure to be on a MR24C3F it's the only port and after a leak was repaired and everything vac down to 500M and new charge weighed in. It runs cool but not cold … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
1.5 ton system brand new, lineset length is 60feet,
1.5 ton coleman system brand new, lineset length is 60feet, subcooling is 3 superheat is 72, suction pressure 40 head pressure 220 factory charge is 5 ibs 11 oz, added 1 ib 6 oz for lineset length, ev… read more
hvacdave84
hvacdave84
53 satisfied customers
I have a Trane XL13xi outdoor unit that has been not keeping
I have a Trane XL13xi outdoor unit that has been not keeping up with the thermostat for the past 3-4 days. It's been unusually hot but I'm unsure if I need a charge or the compressor is going out. The… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Carrier, 9 yr old 3 ton residential heat pump (R410a)....not
Carrier, 9 yr old 3 ton residential heat pump (R410a)....not cooling. Suction pressure drops rapidly to about 10 psig when I turned it on. High side pressure only reached about 300 #. Compressor was v… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
My outside HVAC compressor is making a vibrating noise that
My outside HVAC compressor is making a vibrating noise that I need help diagnosing. Has been going on for a couple of weeks now. Unit works but the noise is concerning. I have a video recording of the… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
This question is for Phil only please *** It's getting ready
This question is for Phil only please ***It's getting ready to warm up here in Virginia. It is supposed to be hitting 80 degrees today. You said previously you wanted the temperature in the house to b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a goodman AVPTC3137 air handler and would like to know
I have a goodman AVPTC3137 air handler and would like to know the recommended dimensions for the plenum/trunk supply and return.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Whats normal pressure for r22 walk in cooler, all day today
whats normal pressure for r22 walk in cooler JA: I'll do all I can to help. How long have you been dealing with this? Customer: all day today i want satisfiy JA: Do you plan on doing the work yourself… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I HAVE A 3 TON COLEMAN HEAT PUMP AND HIGH SIDE PRESSURE READING
I HAVE A 3 TON COLEMAN HEAT PUMP AND HIGH SIDE PRESSURE READING IS 238 AND LOW SIDE PRESSURE READING IS 236.5 OUTSIDE TEMP AT TIME WAS 39 F. WHAT DO YOU THINK IS THE CAUSE REVERSING VALVE OR WHAT. THE… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
what is the procedure to replace a chilled water sensor on
what is the procedure to replace a chilled water sensor on RTHD screw chiller… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Lennox Heat Pump HP25-311-1P, s/n 5894C65407 matched
I have a Lennox Heat Pump HP25-311-1P, s/n 5894C65407 matched with indoor unit model CB19-31-1P, s/n 5894D38883. We are having a problem in the cooling mode. We can get it to cool consistently. Curren… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Goodman HDC24-1AB Split ductless outside unit not coming on.
Goodman HDC24-1AB Split ductless outside unit not coming on. Yesterday the indicators flashed and it quit. But it ran OK again an hour later for 18 hrs. Quit again during the night. Now dead. I've che… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x