I have a Lennox concervator G8E that has worked tirelessly for forever. Currently it is constantly cycling off a few seconds after starting up. The top of the furnace gets super hot. If I turn the furnace off until it completely feels cold to the touch It will start and complete one cycle, then goes back to cycling on and off until I turn it off and let it get cold again.

Contractor's Assistant: Did you check the furnace's filters?

I have checked the filter and cleaned it, I have checked and cleaned the flame sensor with steele wool.

Contractor's Assistant: Do you plan on doing the work yourself?

Only to a point... ha ha !

Contractor's Assistant: Anything else we should know to help you best?

I have had a look at the roof vent from a distance and the cap is securely in place so I don't think anything has gone in it.

Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 38 days by:
1/7/2018
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,873
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello again,

Click here please for the manual

so far it sounds like a bad printed circuit board.... its mounted on the blower section of the furnace, bottom panel.

Let the furnace cool for an hour.. Then use a hair drier to warm the board up to 130F slowly and gently.... if the furnace will not fire or shows any changes at all in behavior or the furnace goes off after just a minute or so, the printed circuit board is bad.

.

We can go from here without a time limit.

You can order a new board at http://www.cozyparts.com

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,873
9,873 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,873 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Goodman GKS90703BXAD furnace with Emerson PCBBF112S
I have a Goodman GKS90703BXAD furnace with Emerson PCBBF112S control board.Upon applying power, inducer motor comes on for ~ 10 seconds, then ignitor begins glowing, then gas valve opens and flame ign… read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
My ducane gas furnace stopped working. When I turn it on at
Hi Pearl, my ducane gas furnace stopped working. When I turn it on at the thermostat, I can hear kick in and a few seconds later the burners start up only to last a few seconds then it shuts off. It d… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane XL80 furnace that is about 20 yrs old that is
I have a Trane XL80 furnace that is about 20 yrs old that is used very little.Sometimes when I turn up the thermostat it works normally, heat & shut down correctly. Other times the little fan comes on… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
792 satisfied customers
i have a 80uhg lennox furnace which has been working fine until
i have a 80uhg lennox furnace which has been working fine until it fires up for 2 secs then no gas comes out and then flame dies is this a gas valve problem or control board problem… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My forced air gas fired furnace does not start sometimes. Why?
My forced air gas fired furnace will not start sometimes (not all the time). The thermostat is asking for heat. When this happens, if I turn the power switch OFF to the furnace, then turn it back on, … read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
792 satisfied customers
My thermostat is staying at 60 degrees. My furnace is going
My thermostat is staying at 60 degrees. My furnace is going through the cycles but the yellow light calls for heat for 5-10 seconds then turns off. Cold air is blowing through the registers. The conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
lennox elite... set thermostat the furnace cycles on
lennox elite... set thermostat the furnace cycles on , burner runs 5 seconds stops... minute later burner shuts off, a couple of times this happens then the unit shuts down.... Red and Green lights bl… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a model G23Q3/4-125-4 Lennox gas furnace. When starting,
I have a model G23Q3/4-125-4 Lennox gas furnace. When starting, the furnace always shuts the burner flame off on the first (strike) try and a second (strike) try immediately follows and there is never… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox G24M Series Gas Furnace. I turned it off at
I have a Lennox G24M Series Gas Furnace. I turned it off at the thermostat yesterday and now it won't turn back on. It tries to light through five or six cycles. I hear what sounds like a blower then … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Lennox G60UH has been intermittently not starting for the
My Lennox G60UH has been intermittently not starting for the last 2 weeks. It is getting worse. The error code says "Lost flame sense 5 times in one cycle". Is there anything I can do to get the furna… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
Have Lennox Diplomat Furnace with Ignition Control Board EGC-1.
Have Lennox Diplomat Furnace (80MGF4/5-100A-1) with Ignition Control Board EGC-1. Issue: Both Diagnostics LEDs are blinking together and fairly fast (indicating a "Heat" demand / Normal Operation). Th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i noticed that my lennox furnace was not running. i went to
i noticed that my lennox furnace was not running. i went to look at it and the green led lights on the bottom section were not blinking simultaniously they were alternating. when i flipped the breaker… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Trane XR80 that does not appear to be working tonight.
I have a Trane XR80 that does not appear to be working tonight. The fan turns on, the pilot is lit, the burner ignites for about 3 to 5 seconds and then shuts off. The temperature in the house is now … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a TRANE XE 78 in a rental house. The tenants are telling
I have a TRANE XE 78 in a rental house. The tenants are telling me that they lower the thermostat to 65 at night. They claim that when they get up the next morning that the furnace will be blowing col… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a lennox model c23-41fc-1 with an electric ignition.
I have a lennox model c23-41fc-1 with an electric ignition. The burners start but then cut off after a few seconds. It works at random times. it is cold here...please help :)… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Gas furnace lights, runs gas, blower starts, gas blows for
My Gas furnace lights, runs gas, blower starts, gas blows for 2 minutes, blower continues for 3 more minutes, turns off and then starts over again a minute later. Air is only slightly warm at vents, i… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
Lately when it has been real cold outside at night, I am woken
Lately when it has been real cold outside at night, I am woken up with cold air blowing from the vents and the room temperature much lower than the thermostat setting. I can usually get the furnace to… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
i have a lennox g61v furnace. the product label is in a place
i have a lennox g61v furnace. the product label is in a place where i can't see it or reach it so i can't get the serial number or even the btu's off it. the diagnostic lights are alternately flashing… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x