I have a hvac system that the fan will work when turned to…

Customer Question
I have a hvac...

I have a hvac system that the fan will work when turned to air conditioning , but the fan will not kick on when turned to heat.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes and even tried a different thermostat.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Nordyne model number e2eb-015ha

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 25 minutes by:
11/28/2017
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,703
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello. the printed circuit board with the fan relay on it is bad, OR if its an older unit the Fan limit switch is bad, or much less likely the los speed winding in the blower motor is bad.

.

Takea close up, exceedingly well focused photo of the wiring diagram glued inside the furnace/air handler door, and I will mark it up with trouble shooting instructions. Use the 'add files' link next to your send button to get the photo(s) to me.

Wecan go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed , after yourate this answer:

Selectthe 'finishand rate your expert link' near the top of your page and click on it.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,703
9,703 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,703 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Model E2EB-015HA fan runs all the time, after heat is off,
model E2EB-015HA fan runs all the time, after heat is off, must shut off power to stop. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Nordyne E2EB-015HA. I have replaced the capacitor,
I have a Nordyne E2EB-015HA. I have replaced the capacitor, fan relay switch, and the sequencer. The system will not come on. No heat, no fan and no cold.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Nordyne e2eb-015ha. Here are the details of my
I have a Nordyne e2eb-015ha. Here are the details of my original problem. I previously submitted this problem to JustAnswer: "Issue is with the heat. I can see elements get orange, but fan never kicks… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
I have a Nordyne e2eb-015ha. Issue is with the heat. I can
I have a Nordyne e2eb-015ha. Issue is with the heat. I can see elements get orange, but fan never kicks on. Elements get hot, then I hear a click and elements cool down. If I put fan on AUTO on thermo… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I trying to install a Trane thermostat I have a Nordyne E2EB
I trying to install a Trane thermostat I have a Nordyne E2EB 015HA. It said determine if your system has a 24 VAC common wire which is require to power the tstat. it said to connect the wire to the 24… read more
Appliance Guru
Appliance Guru
18,162 satisfied customers
Ok had a unit with a bad sequencer so changed it was a 24v-1-110
Ok had a unit with a bad sequencer so changed it was a 24v-1-110 double stack ... They gave me a part 24v-1-24 Also thermostat will not engage blower in auto selection INterTherm E2… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Why the heat and fan will not turn off after you turn the
why the heat and fan will not turn off after you turn the thermostat off or it reaches temperature setting?you can hear the thermostat click off,but the fan and heat still running for a long time unti… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a nordyne model e2eb-015ha a/c and it keeps blowing
I have a nordyne model e2eb-015ha a/c and it keeps blowing the 3a fuse. we have a recent tropical storm (isaac) and not sure if power sureges have caused this or not. help me… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
My nordyne E2EB-015HA won't blow cold air. I have a Nordyne
My nordyne E2EB-015HA won't blow cold air. I have a Nordyne E2EB-015HA system in it. The heat works fine. Two days ago, the A/C worked as well. Today the A/C was turned on but it won't blow cold air. … read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a Nordyne model E2EB-015HA electric furnace.
I have a Nordyne model E2EB-015HA electric furnace. Sometimes we use just the fan to circulate air. Today it stopped working and apparently made a loud "whoosh" noise as it quit. Its controlled by a H… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
intertherm model E2EB-015HA, once or twice a week, heater
intertherm model E2EB-015HA, once or twice a week, heater wont come on, cycled thermostat a few times and it would work.. replaced thermostat, last night didn't come on again, could feel heat at furna… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,703 satisfied customers
I have a Nordyne Heating unit #E2EB-015HA in a mobile home.
I have a Nordyne Heating unit #E2EB-015HA in a mobile home. First the blower will only come on if I place the thermostat in the ON position instead of auto. Also it seems that only one of the elements… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Nordyne Model#E2EB-012HA all electic. heat will not work at
Nordyne Model#E2EB-012HA all electic. heat will not work at all does not even attempt to kick on but air conditioning works fine could this be thermosthat or something else.… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Have a nordyne 903021f. Fan turns on only when switched from
Have a nordyne 903021f. Fan turns on only when switched from auto to on. Switch thermostat to heat or cool and nothing happens with system and no change on the stat. Changed the stat and exact same is… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
We have a Nordyne E1E8-015HA forced air system. The fan is
We have a Nordyne E1E8-015HA forced air system. The fan is not turning on when the furnace heats. We tried replacing the thermostat already but this did not solve the problem. We can manually turn on … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
nordyne blower model e2eb-015ha workeed well with a three and
nordyne blower model e2eb-015ha workeed well with a three and half ton vexar heat pump. is it compatibe to a new bryant three and a half unit for the purpose of handling the proper air flow.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
my heater is set on and it is blowing air but is not hot
my heater is set on and it is blowing air but is not hot the element is good and i replaced the thermostat . what should i check now… read more
Josh
Josh
Service Technician
High School or GED
30 satisfied customers
have a nordyne e2eb-o15ha electric furnace changed sequencer
have a nordyne e2eb-o15ha electric furnace changed sequencer and it still dont get very hot any help would be appreciated.… read more
Al
Al
Master Service Technician
Votec, College, Master Electrical S
24 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x