I have a carrier 9200. The limit switch is popping. There…

Customer Question
I have a carrier...

I have a carrier 9200. The limit switch is popping. There was a very dirty filter in, but that it not in now. I have checked the air inlet for both the flame unit and the fan blower are working fine. I reset it earlier today, and it popped again. I have reset again and I am waiting to see what happens. Any idea on areas to check

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

The thermostat is fine and I actually removed the filter for testing. Have a new one coming. It is working currently, but I am suspicious the limit switch will blow again

Contractor's Assistant: Do you plan on doing the work yourself?

I have so far. I am pretty good with electrical and mechanical, so I would like to try

Contractor's Assistant: Anything else we should know to help you best?

It flashes error code 33 when out, so it is leading in the direction that the system is not getting enough air to keep cool. So far, it has been working for about 30 minutes since reset with no issue. I feel air coming in the return vents as well as the air intake for combustion unit.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
11/27/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy. Is it a flame rollout switch near burner you are resetting?

Or the credit card sized flat plate behind gas valve (no reset on this)

Ask Your Own HVAC Question
Customer reply replied 8 months ago
It is the little flame roll out switch above window to see the flame. The unit appears to be installed upside down, so this switch may normally be on the bottom.
It is definitely manually resetting when I hit the button
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

The bad thing about the flame roll out (manual reset) is it is not really tied to exchanger temp but the fact the heat is going the wrong way....99% of the time this is a crack in the heat exchanger. When the main blower kicks on it blows air into the crack and stifles the flame backward.

One reset a year or 2 is an inconvenience....repeated reset is bad exchanger.

Unfortunately this particular unit is prone to exchanger failure starting around 10 years + old.

The flame roll out is there for when flame actually rolls backwards....this is the most important safety on the furnace to prevent carbon monoxide/fire.

Any other swith I would talk you through...this one - I would have the exchanger looked at

Billy

Ask Your Own HVAC Question
Customer reply replied 8 months ago
OK, thanks for your help
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

I am very sorry....we can work on this unit top to bottom as I had years experience with this model....but I must be upfront also when it comes to safety. Please do not keep resetting..or bypassing....this is a dangerous one to mess with

Billy

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 months ago

If all set please rate service ( not the bad news) to close question.

If you need more info use reply

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
23,151 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Carrier furnace WeatherMaker 9200 and Ac. This fall
I have a Carrier furnace WeatherMaker 9200 and Ac. This fall when the tenant turns on the furnace, first the blower motor will run for a few minutes and then shut off. Then the induced motor will come… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I get a code 33 on a Bryanr MAV 350MAV. I reset the temp
I get a code 33 on a Bryanr MAV 350MAV. I reset the temp reset button. It runs for 5 minutes and shuts off again. The intake pipe pups out. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
What causes the condensate water to leak from inside the
What causes the condensate water to leak from inside the furnace? I cleaned the condensate trap.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
I have a Carrier 58STA10116 with a code 33. I bypass the
I have a Carrier 58STA10116 with a code 33. I bypass the main limit switch and the furnace runs fine. I reaplaced the main limit switch today and still get the code 33. I go back into bypassing the ma… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
. I gave the same problem-code 33. Only after following your
. I gave the same problem-code 33. Only after following your first steps, I get the 12 code seconds, then operation. Ignition and blower few minutes. Then it all shits off again...… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
My BRYANT 310AAV/JAV Is not giving out heat fan is continuously
My BRYANT 310AAV/JAV Is not giving out heat fan is continuously running just changed filters code changed from 13 to 33 after i took panel off and pushed the manual reset buttons but still no heat. Is… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My CARRIER Wheathermaker 9200 furnace cycles to rapidly. It
My CARRIER Wheathermaker 9200 furnace cycles to rapidly. It does not reach temp set on thermostat. Shuts off on Code #33. How do I run tests to diagnose the problem?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 58MVP. It was cold this week and furnace didnt light.
I have a 58MVP. It was cold this week and furnace didn't light. The technician pushed a reset button on the side of the combustion chamber and the unit lit up. He said the furnace needed replacement b… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
I Have a carrier 58MSA060 14112 SERIES 140 that is blowing
I Have a carrier 58MSA060 14112 SERIES 140 that is blowing warm but not hot air. I've changed the filter, washed the internal filter and checked the intakes and vents and everything looks open. 60-62 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a model 58ta hot air furnace. The vent motor will not
I have a model 58ta hot air furnace. The vent motor will not start, the blower motor is running, thermostat call for heat. The led code seems to to be 3 long 3 short blinks… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a carrier home heater model 58ZAV096-16 that will ignite
I have a carrier home heater model 58ZAV096-16 that will ignite but the flame will go out and the fan remains on. The flame will cycle on and off every ten minutes or until the temperature inside my h… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I Carrier weathermaker 9200 and its only blowing cold air,
I Carrier weathermaker 9200 and its only blowing cold air, and the led is blinking 33. I replaced the filter. Still nothing. Pulled out the thermocouple and cleaned it. still no go. I bypassed the hig… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
I am getting an error 33 indacting a flame rollout switch problem
I am getting an error 33 indacting a flame rollout switch problem on a Carrier 9200. Fan runs even with fan set to auto and heat to off. Where is this switch and what does it look like so i can try th… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
Carrier WeatherMaker 9200 - error code 33. Blower motor and
Carrier WeatherMaker 9200 - error code 33. Blower motor and capacitor are new and working. When I switch the power ON to the furnace, I hear a click, the blower motor kicks on and the error code 33 in… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a carrier model # 58pav070-12. The led light is flashing
I have a carrier model # XXXXX The led light is flashing code 33. I have tried turning the switch off and restarting it, nothing happened. The blower fan just runs constantly, the furnace doesnt even … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My Carrier Weathermaker 8000 is 7 years old. Just a few days
My Carrier Weathermaker 8000 is 7 years old. Just a few days ago the air is blowing cold air and the burners are not igniting. I am getting Code 33. Any quick fix suggestions? Anything to reset? I did… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
I have a Payne PG 8MAA048110 furnace which flashes an LED code
I have a Payne PG 8MAA048110 furnace which flashes an LED code of 33. I purchased a spare limit and flame roll out switch for backup a few years ago. I replaced the flame roll out switch and still had… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
We have a Carrier Weathermaker 9200. Were currently having
We have a Carrier Weathermaker 9200. We're currently having a blizzard and our air intake valve got clogged. We cleaned it out, but the furnace smelled hot and had water underneath it. We turned it on… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x