I have a 5 year old Tempstar furnace and it's short cycling.

Customer Question
I have a 5 year...
I have a 5 year old Tempstar furnace and it's short cycling. Meaning the furnace fires, runs for a period of time with heat coming out, however shuts off before getting to the desired temperature. as soon as it cools downs and shuts off, the heat cycle begins again. does this until desired temp is reached.Checked obstructions in duct work- none
replaced hi heat limit switch- still operating same
checked to see if the flame rollout sensors tripped.. no they did not trip.Green light blinks 4 times when burners shut off. indicating limit circuit fault
Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
11/25/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,274
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
thanks!
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

The resetable thermal rollout is tripping out this one....CLICK HERE do you see that one?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
ok.. i'm not sure where to locate that one..i see the limit switch.. 2 flame rollouts.
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

OK the unit is tripping on an AUTO RESET limit. The ones with push button switches are not auto resetting it is the one with out a button.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Sending a couple of pics. Not sure where that one is on this unit
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

This one...CLICK HERE that is the one that is likely tripping off. Check the filters on the furnace as a restriction in the filter or blower issue could cause it to overheat.

All I ask is please select the 5 STAR rating at the top of your page before leaving otherwise I receive ZERO credit for assisting you. BONUSES are always appreciated...Thanks and you can come back anytime for free followup questions & Happy Holidays!

Ask Your Own HVAC Question
Customer reply replied 4 months ago
that is the one i replaced..
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

OK bypass it and see if it continues to run fine...if so the unit is likely overheating...do you have a HEPA filter installed? If so remove that and put a regular one in and try it.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
bypass.. just disconnect it then and let it run? i have the least expensive filter meaning the least restrictive and also i have tried without the filter..
Customer reply replied 4 months ago
could it be the blower not blowing hard enough or not pulling enough cool air in?
Customer reply replied 4 months ago
the blower sounds ok. meaning doesn't sound like the bearings are going bad
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Just bypass it and see if it stays running if so the heat exchanger could be blocked or the blower may not be running on the fastest speed.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
Was this answer helpful?
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,274
18,274 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
How to clean heat exchanger coils, filters have been clean
filters have been clean recently and I am getting an airflow alarm on the thermostat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,676 satisfied customers
I'm curious... I have a Tempstar furnace and it is short
I'm curious... I have a Tempstar furnace and it is short cycling. Can you answer questions? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
277 satisfied customers
I have a 5 year old Tempstar furnace and it's short cycling.
I have a 5 year old Tempstar furnace and it's short cycling. Meaning the furnace fires, runs for a period of time with heat coming out, however shuts off before getting to the desired temperature. as … read more
HVAC Guru
HVAC Guru
HVAC TECH
18,274 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a tempstar furnace that wont close pressure switch.
Have a tempstar furnace that wont close pressure switch … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick
Rick
Supervisor
23,596 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick
Rick
Supervisor
23,596 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
We have a tempstar furnace with a ecm motor that is hooked
we have a tempstar furnace with a ecm motor that is hooked to the air conditioner that when it starts on air the motor pulses fast then slow and then stops for a bit and restarts .Checked bearings on … read more
Charles Bodenheimer
Charles Bodenheimer
Owner
Associate Degree
78 satisfied customers
I have a tempstar furnace a few yrs old and this morning no
I have a tempstar furnace a few yrs old and this morning no heat get an error code of three the pressure switch appears to be working … read more
Rick
Rick
Supervisor
23,596 satisfied customers
Have a tempstar furnace two years old and the light is
Have a tempstar furnace two years old and the green light is blinking 7 times and stopping no heat in the house… read more
Rick
Rick
Supervisor
23,596 satisfied customers
I have a Tempstar Furnace Model number NUGK125DK08. I need
I have a Tempstar Furnace Model number NUGK125DK08. I need and schematic diagram and to know what fan control I need to buy for it.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Tempstar furnace won't come up to temperature with filter
tempstar furnace won't come up to temperature with filter in … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a tempstar furnace, the blower and inducer motors
I have a tempstar furnace, the blower and inducer motors continue to run even if I take the wires off the thermostat. I have checked the low voltage fuse and it is fine. Additionally when it was calli… read more
Rick
Rick
Supervisor
23,596 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x