Customer Question
My good man gks90904cxag...

My good man gks90904cxag is not producing heat

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Just changed filter and checked thermostat

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Im at the unit with the panel off and it kicks on fan runs but it's not igniting

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
11/24/2017
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,378
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

What is the flash code on the control board LED?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Would that be the ds1 led?
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

I never noticed any LED designation. Do you have an LED that's flashing a sequence?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
It's staying solid
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Steady on is normal operation. If the furnace isn't doing anything try this; jump the R & W terminals on the thermostat terminal strip on the control board. Then power it back up. Does the draft fan run?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The fan runs
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

The draft fan runs and you have no heat and a steady on LED? If so cycle the power off wait a minute then turn it back on. Tell me what happens.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The igniter lights up for around 11 seconds then shuts off, and there is no flame
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

Ok, you should be getting a failed igniton flash sequence. You need to test for 24 volts AC at the gas valve when the igniter is glowing.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Blower shuts off and on when it should just stay on when
Blower shuts off and on when it should just stay on when heating. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Trying to fix my thermostat to kick on the heat correctly. I
trying to fix my thermostat to kick on the heat correctly … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
My Heat Does Not Work In Auto Mode. It will work with fan
My Heat Does Not Work In Auto Mode. It will work with fan swirch to On. AC side is all good. … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
The portion of my unit in the attic won't kick on...fan
the portion of my unit in the attic won't kick on...fan outside is running but it isn't pulling out hot air like it normally does...thermostat has new batteries and cool on isn't blinking...temp is se… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
I have a Honeywell HZ322 Truezone panel and a Lennox CBX27UH
Pearl, I have a Honeywell HZ322 Truezone panel and a Lennox CBX27UH HVAC. We need AC today bc we are in Florida. The system is running and air is flowing through the system, but the AC unit is not spi… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have a Trane XR90 furnace about 12 years old. It's blowing
Hi, I have a Trane XR90 furnace about 12 years old. It's blowing cold air not warm. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Bryant Zone Perfect Plus thermostat won't pump heat
I recently bought a house with a Bryant zone perfect plus thermostat. This is the first time I needed to use it and it won't pump heat. There are 2 zones. Both are programmed identically. The Therm is… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have an American standard freedom 80 furnace. I changed the
I have an American standard freedom 80 furnace. I changed the filter and when I put the doors back on, it sounds like it wants to run, but will not kick on. It has a fast blinking red light, which say… read more
R G
R G
44 satisfied customers
I have a Comfortmaker rpj II and it will not ignite. When the
I have a Comfortmaker rpj II and it will not ignite. When the thermostat kicks it on, the blowers start but there is no flame, not even an attempt at a flame. We called the local repair man and he has… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Trane electric home furnace blowing only cold air. Why?
My Trane electric home furnace is now only blowing cold air and no heat. Thermostat works to turn it off/on. Apparently the fan works.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a RUUD model no. UBHC-17J11NFD air unit.the vent inside
i have a RUUD model no. UBHC-17J11NFD air unit.the vent inside the house has no suction. it does not seem to be pulling any air in. when i look at the thermostat i see that it is on AUX heat. is there… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
hello, my furnace is not producing warm air and the fan does
hello, my furnace is not producing warm air and the fan does not turn on..........the unit clicks on......then off in about a 30 second effort and repeats this cycle about once per minute.......please… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
changed thermostat over to a RTH6350d now the ac doesnt run
changed thermostat over to a RTH6350d now the ac doesnt run at all C= blue not used y= yellow r= red with jumper to rc aux= white with jumper to E o/b= orange g= green the power has been turned back o… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
i have a older trane unit on my roof and ive been having consistent
i have a older trane unit on my roof and ive been having consistent problems with the heater and ac turning on for about 30 seconds then shutting off. any ideas?… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
My heat pump is blowing cool air. The furnace wont kick on
My heat pump is blowing cool air. The furnace wont kick on so the heat pump is continally running. When i would reset everything it would kick on, but once the house has heated it will no longer run a… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
my bryant Mav355 is not blowing enough heat and its running
my bryant Mav355 is not blowing enough heat and its running under the code low heat what is wrong… read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
I have a coleman-evcon furnance. just recently when the house
I have a coleman-evcon furnance. just recently when the house reaches the desired temp, the furnance kicks off like is is supposed to. But it will not automatically re-ignite when it drops below the t… read more
BARRY
BARRY
owner
Associate Degree
56 satisfied customers
I cleaned the filters - electrostatic and passive - on my @
I cleaned the filters - electrostatic and passive - on my @ 5 year old Trane furnace. Before removing I turned off the breakers in the household panel, then turned off and I unplugged the electrostati… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x